Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Dialling in
So I am currently at the point where the heating is now coming on solidly at night - I know this because my wife is complaining its cold. So I am trying to dial in the system to make things work as best they can.
Yesterday I went for 21 across the whole house, both zones for 24 hours. It means we've had some pretty serious power demand. Already just today (from midnight) we've used 16.5kw; including base load and hot water, breakfast, washing machine and now my wife has the tumble drier on. At 7am we had used 10kw and that must only be base load and heating. I know our base load is 320w so in that 7 hours, 2.2kw was base load and 7.8kw was heating.
I had to increase the flow temperature minimum manually last night up to 37 degrees, from 27. At 27 it simply could not heat the house and upstairs was around 19. I now need to play around to get this as best I can. I might need to tweak the weather compensation curves or something.
With my plan to move to Octopus Go next week, I should be preloading my heating at 0-4am and filling my battery with lovely cheap power as well. This should make a big difference. However it will also tell me if I need more storage. Given I can add around 14kw for around £2000 (maybe even less) I think in the winter this might be a no brainer. If I spend £500-£800 in the winter for heating it would easily pay for itself.
Also something I have read is that wet and windy weather impacts your heating due to wind chill. This is clearly true, however I can see nothing that takes this into account on any unit. The only ways to accommodate this seem to be custom software to run your ASHP. I am going to investigate this further on a few specialised forums.
Interesting stuff. Increasing your flow rate to 37C from 27C will definitely help. I've set ours manually to 40C and the house is feeling cosy. More than acceptable. Your battery strategy is sound and you will save a packet doing that given the crazy tariffs.
We've never found cold windy weather to have an impact on the performance of the pump. It probably contributes to greater heat losses from the house. The worst weather for us is the -2 to 4C mark when it's really humid outside because the unit frosts over very regularly leading to an increased amount of defrost cycles which makes the pump work harder.
But please keep sharing your experiences. Very interesting.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor the question is, how will that affect the COP. But given we dont want to live in an ice cold house, its something of a null point
@batalto Hi Batalto,
Increasing the water flow temperature minimum setting from 27C to 37C will limit the operating range of the weather compensation.
Your Midea ASHP is better than many others, in that you can create your own weather compensation curve to match your home, rather than select one of the available curves from a list. The reason that installers prefer to provide 'fit and forget' thermostats, rather than controllers that utilise the weather compensation capability, is that it can take days or even weeks to correctly optimise the system or correct operation with weather compensation.
Rather than increasing the minimum water flow temperature setting, you should probably have increased the temperature offset by one or two degrees.
Did you record the operating parameters as I suggested?
@derek-m I've not been collecting those, I just haven't had the time at home - we were out all yesterday until 7pm. I will try to find a day or two to collect them.
I have a range of options I can play with. What I chose to change was the minimum flow temperature. At the moment I have it set at 37 degrees when its 17+ outside down to 55 degrees at -2. Are you suggesting lowering the max outside temperature before compensation occurs?
As a note, the heating has only just come on over the last few days. Frankly the biggest factor in our house is solar gain in the day. On a sunny day we can easily get to 23 or 24 even at this time of year. I think the biggest factor in the heating will be the "wife factor". When she is happy its not cold, those are the right settings!!
Posted by: @batalto@derek-m I've not been collecting those, I just haven't had the time at home - we were out all yesterday until 7pm. I will try to find a day or two to collect them.
I have a range of options I can play with. What I chose to change was the minimum flow temperature. At the moment I have it set at 37 degrees when its 17+ outside down to 55 degrees at -2. Are you suggesting lowering the max outside temperature before compensation occurs?
As a note, the heating has only just come on over the last few days. Frankly the biggest factor in our house is solar gain in the day. On a sunny day we can easily get to 23 or 24 even at this time of year. I think the biggest factor in the heating will be the "wife factor". When she is happy its not cold, those are the right settings!!
Hi Batalto,
There are various problems in optimising an ASHP based heating system, the primary one being the slow reaction time compared to an oil or gas fired heating system.
Another problem is matching the weather compensation curve to the heat demand, which can take some time to achieve. Increasing the minimum water flow temperature from 27C to 37C, means that the water flow temperature cannot go bellow 37C even when it should do so.
It could be that to meet the heat demand at an ambient air temperature of 17C requires a water flow temperature of 30C or 33C, this is what you need to discover by monitoring your system. At the other end of the scale it could be that at -2C outside air temperature, you require a water flow temperature of 50C rather than 55C.
The offset value is designed to move the weather compensation up or down by a number of degrees. If your initial curve is set at 27C to 55C, then increasing the offset by 2C would change the curve to 29C to 57C.
Changes in heat demand due to chill caused by wind and rain should be accommodated by the control system, though it may take a little time to respond.
@derek-m I can actually move both the top and bottom
it has a max ambient, max flow temp and min ambient, min flow temp. At the moment these are;
Max Ambient: 17
Flow Temp: 37
Min Ambient: -2
Flow temp: 55
I can edit any of those up or down as I see fit
Posted by: @batalto@derek-m I can actually move both the top and bottom
it has a max ambient, max flow temp and min ambient, min flow temp. At the moment these are;
Max Ambient: 17
Flow Temp: 37
Min Ambient: -2
Flow temp: 55
I can edit any of those up or down as I see fit
Hi Btatlto,
The objective, for optimum operation, is to match the water flow temperature to the heat demand. To do so you would need to monitor the actual indoor temperature in relation to the desired temperature, along with the outdoor air temperature and the actual water flow temperature.
Based on your present settings, a 1C fall in outdoor air temperature, should produce an approximately 1C increase in the water flow temperature.
If the required water flow temperature to meet the present heat demand is below 37C, then of course there will be no change in the water flow temperature, and you should find that your heat pump switches on and off. Because I cannot see your system and how it is responding I am having to make assumptions.
What I suggest, if you have the time, is that you monitor your system with the above settings and see how it responds, remembering that changes in actual indoor temperatures will be very slow, unless they are caused by solar gain.
If, over a range of outdoor air temperatures, you find that the actual indoor temperature is deviating from the desired temperature, then you need to adjust the slope of the weather compensation curve. If the indoor temperature increases above the desired value with falling outdoor air temperature then reduce the maximum water flow temperature setting.
One thing of which I am not certain about, is if the minimum and maximum water flow temperature values are actually limits, in that the produced water flow temperature cannot go below or above these values.
- 26 Forums
- 2,675 Topics
- 62.6 K Posts
- 257 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
...and as if by magic... Here was me asking for a bit...
By Majordennisbloodnok , 16 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
I didn't know about those, they look like good pieces o...
By JamesPa , 3 hours ago
-
@mkz, that's very helpful. Even if Urban Plumber are no...
By Majordennisbloodnok , 3 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 4 hours ago
-
My first question is why bother with the auto balancin...
By JamesPa , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 4 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 5 hours ago
-
I share the same experience as @majordennisbloodnok hav...
By Old_Scientist , 5 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 8 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@jamespa many thanks, definitely i will give the pre...
By ragtime27 , 20 hours ago
-
RE: Heat pump installation quotations
@jamespa I noticed that in the Heat Geek design consult...
By Batpred , 21 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@bash, something we haven't touched on already relates ...
By Majordennisbloodnok , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Vaillant arotherm plus 12kW. Installed March 2025. Ex...
By Harebell , 2 days ago