Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Buffer tank in primary circuit?
Hi all,
New member to this very informative forum.
I've recently moved into our new build which has a Samsung Gen6 12kW ASHP. We have UFH throughout seperated into 8 zones controlled by separate room thermostats with manifold valves. My DHW is a 300L Kodiak/Joule pre-plumbed cylinder.
I noticed that at the last minute they installed a 50L buffer tank in line with the hot pipe of the ASHP i.e. on the primary side. This suprised me, as to me it seems rather wasteful. My thinking is, that when heating DHW in summer time, I have to heat up an extra 50L in the buffer tank, which is totally wasted.
When I questioned this, the plumber said that they have had two heatpumps failing in other properties supposedly not doing a defrost cycle. The second reason was to avoid short cycling.
Now I can imagine that if in winter the house is warm and all manifold valves are closed, there's no volume available to do a defrost cycle. That's where a buffer tank may be useful. I can also see that in cases where only one (small) circuit is asking for heat, a buffer tank can avoid short cycling. In both cases the heating is in use, so why not have the buffer tank in the heating circuit rather than the primary?
However, I wonder is the unit not capable of using some heat from the DHW tank for a defrost cycle? Does this require a setting that may be wrong?
The plumber also claimed the buffer tank was necessary to prevent short cycling when heating DHW. He claimed it was something to do with a thermostat switching on/off. I cannot see that a difference between heating 350L instead of 300L would make any difference for short cycling. The HP does not seem to cycle hwne heating hot water.
Needles to say, we need to find out the real cause of these other heatpumps failing. If I understood correctly, this buffer tank 'solution' was proposed by Joule and all previous properties were refitted to avoid any more failures. The plumber is scheduled to come in again and discuss the matter and he already said he was more than happy for me to talk to Joule directly. We need them to be involved as not to void any warranty.
Some observations probably unrelated to the above:
- I noticed the legionaires cycle seems to be done using the immersion heater only heating the water up to 60C. The HP does not seem to be used here. I need to go through the settings, but I'm thinking about disabling it altogether anyway. (Unvented tank, Chlorine in water etc.)
- With the cold spell this summer, we have had the heating on a little, and I noticed the LWT went up to about 45C while the water law should have limited this to 35C for Ta>15C. I noticed that FSV 2091 is set to 'use signal on/off', probably to prevent short cycling at all cost. Am I right in assuming it would be better set to some Waterlaw control for better efficiency? I'm just not sure which one.
Just like to hear any opinions of others ...
Posted by: @roelplumber also claimed the buffer tank was necessary to prevent short cycling when heating DHW.
No it isn't. Make sure he has installed a DHW cylinder with a 3m2 coil. If they haven't ask why not.
Posted by: @roelWe have UFH throughout seperated into 8 zones controlled by separate room thermostats with manifold valves
That's why you need a buffer, get rid of the thermostats and manifold actuators you will not need a buffer.
Posted by: @roelSamsung Gen6 12kW ASHP
Sounds big for a new build, unless it's a massive house?
@johnmo
Agree. It's a 180m2 bungalow with modern 150mm cavity insulation.
When questioned the developer, he said 'well, just to be sure it will handle it'...
The reason the other heat pumps failed may be that the houses have zones, NOT good with heat pumps, and as the pumps is big then it needs a minimum water volume. Quite frankly you ( and the others on your site) may have got bigger problems than heating an extra 50ml of water.
if you club together with other owners get a Heatgeek elite guy in to survey what needs changing. Then your builders plumber can do the changes needed.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
I agree we need the buffer tank when using thermostats (not ideal), but my main question is, should it be placed in the primary circuit i.e. in series with the HP? Would it not be better placed on the other side of the controller i.e. in the UFH circuit before the manifolds? At least we're not heating it then in summer.
And if so, should it be 'in series' with the pump or in parallel as if it was a extra radiator?
Posted by: @roel50L buffer tank in line with the hot pipe of the ASHP i.e. on the primary side.
So I take you mean not a buffer but a volumiser. So hot in, hot out, and installed upstream of the diverter valve. It really needs to on the CH side of the diverter only. Other wise you are heating an additional 50L of water for no reason.
With all those zones the heat pump will have no place to pump all the water around 2m³ an hour. If it is volumiser and not a buffer it's not going to help much unless you also have min flow valve. System is just chasing its own tail flow rate wise.
@johnmo
Posted by: @AnonymousSo I take you mean not a buffer but a volumiser. So hot in, hot out, and installed upstream of the diverter valve. It really needs to on the CH side of the diverter only. Other wise you are heating an additional 50L of water for no reason.
Ah, didn't know it's called a volumiser when placed upstream of the diverter, anyway extacly my point heating 50L for no reason.
Posted by: @AnonymousWith all those zones the heat pump will have no place to pump all the water around 2m³ an hour. If it is volumiser and not a buffer it's not going to help much unless you also have min flow valve. System is just chasing its own tail flow rate wise.
I don't know this detail. I'll speak to the plumber soon and see what he says.
Thanks so far.
@roel welcome to the forums. Please post a photo of your system.
Historically, buffer tanks played a crucial role in heating systems, designed to address the limitations of on-off fossil fuel boilers that operated at high temperatures to prevent corrosion. These boilers required a low flow rate, and buffer tanks helped manage the differing demands of connected circuits by blending down high temperatures efficiently. However, this approach is outdated when it comes to heat pumps, but inexperienced installers still use them, as was the case in your system (and ours).
The notion that buffer tanks help heat pumps "smooth out load" is a misconception. In reality, a 100-litre buffer tank holds only 1.17kW of energy at a 10°C higher temperature than required, providing just 7 minutes of buffer time for a system with a 10kW load. Achieving this extra temperature can also increase energy bills by up to 25%.
Modern heating systems with modulating boilers and heat pumps are designed for efficiency and precise control, making buffer tanks unnecessary and even detrimental by blending down temperatures. Bizarelly, most manufacturers still recommend buffers due to design limitations in their heat pumps, but this is a workaround rather than a true solution, often masking underlying design flaws.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @roel- I noticed the legionaires cycle seems to be done using the immersion heater only heating the water up to 60C. The HP does not seem to be used here. I need to go through the settings, but I'm thinking about disabling it altogether anyway. (Unvented tank, Chlorine in water etc.
Hi @roel. Welcome 🙂
The Samsung Gen6 12kW ASHP can heat water up to 65degC, which would charge your DHW tank to 60degC within a reasonably short time, especially using a 12kW unit! If you were happy to have DHW at 60degC then it's more cost effective to use the ASHP to do this, and provide for Legionella sterilisation, rather than using a 3kW direct electric immersion. You'll probably find the cylinder contents heating is more uniform and effective with the ASHP than with the immersion anyway. System volume isn't an issue with DHW generation as the cylinder contents absorb heat quickly, and also provide a source of heat into the hydronic circuit for defrost should this be required mid-charge of the DHW cycle.
For the m2 size of the bungalow and UFH I'm at a loss as to why the developers thought it necessary to use 8 zones all with room thermostats. They usually do this through ignorance and a lack of understanding about hydronic heating, minimum circuit volume scenarios, and how to maximise efficiency.
You've got a scenario [if I'm correct] where one zone may call for heating, and energise a 12kW heat source. The heat source is way too big for the zone heating load, even on minimum turn down, which will be around 3 - 3.5kW. The ASHP will cycle on and off and it will be impossible to have a stable weather compensated leaving water temperature. That's inefficient. You'll probably find this problem persists even when multiple zones are calling for heat, as the combined thermal load demand may still be lower than the ASHP minimum turn-down output.
12kW sounds oversized, probably getting on for 100% oversized, if a 180m2 new build is well insulated and compliant to current Part L building regs. That fundamentally compromises the efficiency of the ASHP as it will spend a lot of time cycling on and off at minimum turn down when the dwelling heating demand is low. Buffers and volumisers add volume on the primary side, and they have their uses, but in your case they are a sticking plaster over what appears to be a fundamental problem caused by a poor hydronic system design with 8 thermostat controlled zones mis-matched to an oversized ASHP. When just one or two zones are calling for heat there will be inadequate system volume in circuit to meet the ASHP's minimum volume requirements, hence to buffer/volumiser, hence likely also the issue the developer has cited about problematic defrost.
@judith has an excellent idea. Talk to other owners in your development with identical systems, club together and ask a Heat Geek or an independent expert renewable heating consultant to review the design and fitness for purpose. The recommendation they will likely come up with is to get rid of a far-too-complicated multi-zone control, open zone the system control, to bring all system volume into play all the time, and thereby give the ASHP a chance to achieve a stable weather compensated control with constant volume flow on primary and secondary side. Manual balancing can adjust for preferences to have some areas warmer than others.
They would also be able to review or perform a new heat loss calculation to check if the 12kW ASHP is grossly oversized. NHBC guide to heat pump design and specification has some good stuff, but is very top level. It uses data borrowed from CIBSE et al for infiltration/exfiltration AC/h and zone design temperatures. AC/h values are probably over-estimated however. It doesn't cover the detail of the hydronic circuit design, and this is where things usually go wrong.
Posted by: @allyfishThe Samsung Gen6 12kW ASHP can heat water up to 65degC, which would charge your DHW tank to 60degC within a reasonably short time, especially using a 12kW unit!
The maximum DHW temperature on the 12 kW Gen 6 Samsung is 55C. The Gen 7 may be higher.
Posted by: @mike-hPosted by: @allyfishThe Samsung Gen6 12kW ASHP can heat water up to 65degC, which would charge your DHW tank to 60degC within a reasonably short time, especially using a 12kW unit!
The maximum DHW temperature on the 12 kW Gen 6 Samsung is 55C. The Gen 7 may be higher.
Hi @Mike, says 65degC on the Samsung Data sheet
Other data sources support this:
https://www.elementshop.co.uk/samsung-12kw-air-source-heat-pump-170l-cylinder
Aaaaaah, that’s gas boiler thinking! and the recipe for problems with ashp.Posted by: @roel@johnmo
Agree. It's a 180m2 bungalow with modern 150mm cavity insulation.
When questioned the developer, he said 'well, just to be sure it will handle it'...
As several people are explaining better then I can, an over-sized pump will be switching off a lot and will generate errors (and it seems then fail for your neighbours) in the low flow, low volume conditions of your zone valves closing down when the rooms are warm enough.
This site (a distributor) says the minimum volume is 50L so that is where the value comes from. I suspect it has to go in the primary because there needs to be system volume when neither dhw nor heating is active. https://midsummerwholesale.co.uk/buy/samsung-heat-pumps/samsung-stealth-12-heat-pump. I don’t know if this is gen 6 or 7 however.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 816 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 12 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 12 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 15 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago