Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Buffer tank bypass on EDF Ideal heat pump installation
I have an Ideal Logic Air installed through EDF heat pumps. They insisted on having a buffer tank and CH pump. I argued against and we came to a compromise - by installing a bypass on the buffer (on the flow and return sides). The pump does not have a bypass. Does anyone have recommendations on how best to set this up? I could bypass it completely, have the hot water bypass it, have the return bypass it. Also can I keep the pump running or unplug it (easy to do)?
incidentally the efficiency as stated on the control box is awful SCOP 1.7. But it doesn’t seem particularly expensive and the house is warm. When I called Ideal support they told me not to trust it!
I would bypass the buffer tank in one of flow or return only, it will then act a bit like a volumiser.
The problem you have relatively to a tank that was deliberately plumbed as a volumiser will be stratification. Really you want input and output at different levels so that it gets stirred up. Normally the recommendation is to put a volumiser in the flow, but with stratification messing it up a bit Im not so sure. Try and see. The symptom of stratification will be additional cycling. Either way its got to be better to leave it in than to take it out altogether.
As to the pump you really want to bypass it. I fear that if you turn it off it will impede flow (try it and find out!). If you leave it on the two pumps may fight each other but probably not.
Maybe someone else has actually tried this experiment and worked out the best way!
To get value out of bypassing the buffer you will need to adjust your WC curve down to compensate for the loss of temperature across the buffer which will no longer be occurring.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks James.
I know that the 5kW unit has the same circulation pump as the bigger units but its flow is capped to 70% by default but it can up changed in the settings. If I turn the second pump off at least there is some extra capacity that I can use to try to push through the other pump. If it works I could look at removing it later on. I will try and give an update.
@kevb, before you re-plumb, I'd speak to EDF as it may invalidate your warranty if something goes wrong.
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
Well I can try the valving which can be undone so I don’t see that’s an issue. But yes removing the pump would be different matter.
@kevb, many of these companies look for the smallest of excuses to not honour warranties.
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,064 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 3 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 17 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago