Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Buffer tank bypass on EDF Ideal heat pump installation
I have an Ideal Logic Air installed through EDF heat pumps. They insisted on having a buffer tank and CH pump. I argued against and we came to a compromise - by installing a bypass on the buffer (on the flow and return sides). The pump does not have a bypass. Does anyone have recommendations on how best to set this up? I could bypass it completely, have the hot water bypass it, have the return bypass it. Also can I keep the pump running or unplug it (easy to do)?
incidentally the efficiency as stated on the control box is awful SCOP 1.7. But it doesn’t seem particularly expensive and the house is warm. When I called Ideal support they told me not to trust it!
I would bypass the buffer tank in one of flow or return only, it will then act a bit like a volumiser.
The problem you have relatively to a tank that was deliberately plumbed as a volumiser will be stratification. Really you want input and output at different levels so that it gets stirred up. Normally the recommendation is to put a volumiser in the flow, but with stratification messing it up a bit Im not so sure. Try and see. The symptom of stratification will be additional cycling. Either way its got to be better to leave it in than to take it out altogether.
As to the pump you really want to bypass it. I fear that if you turn it off it will impede flow (try it and find out!). If you leave it on the two pumps may fight each other but probably not.
Maybe someone else has actually tried this experiment and worked out the best way!
To get value out of bypassing the buffer you will need to adjust your WC curve down to compensate for the loss of temperature across the buffer which will no longer be occurring.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks James.
I know that the 5kW unit has the same circulation pump as the bigger units but its flow is capped to 70% by default but it can up changed in the settings. If I turn the second pump off at least there is some extra capacity that I can use to try to push through the other pump. If it works I could look at removing it later on. I will try and give an update.
@kevb, before you re-plumb, I'd speak to EDF as it may invalidate your warranty if something goes wrong.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Well I can try the valving which can be undone so I don’t see that’s an issue. But yes removing the pump would be different matter.
@kevb, many of these companies look for the smallest of excuses to not honour warranties.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 26 Forums
- 2,697 Topics
- 63.3 K Posts
- 892 Online
- 7,106 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Electricity price predictions
Chinese manufacturing has the ability to be very good q...
By Majordennisbloodnok , 2 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: GotGordon Manufacturer: Samsun...
By Gotgordon , 13 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
@ian33a I am not easy with sleep either unfortunately…....
By MK4 , 14 hours ago
-
RE: Renewables uptake near you
In a village of under 40 houses...Conservation Area. I'...
By Tim441 , 1 day ago
-
RE: Home Alone with Home Assistant (previously A Beginner's Guide to ASHP Monitoring)
Great news, @bontwoody.
By Majordennisbloodnok , 1 day ago
-
Haier R290 Super Aqua Monobloc. Output capacity tables.
As I mentioned in my introduction post, I've been consi...
By Singlespeed , 1 day ago
-
RE: Air to air bus grant installer anywhere
I am consistently told by aircon folks (ie air/air) tha...
By EtchedPixels , 2 days ago
-
RE: What is possible with FIT, SEG, Hate Pumps and Batteries?
Thank you, everyone, for your replies. Our FIT provid...
By ian33a , 2 days ago
-
@mk4 And of course, the panels are less productive due ...
By Toodles , 2 days ago
-
RE: GivEnergy inverter tripping due to over-voltage?
I'm trying to get clarity on exactly when the inverter ...
By Tim441 , 2 days ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Autocorrupt seems to be working overtime.
By Majordennisbloodnok , 2 days ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
I looked into that wallbox a bit more off the back of t...
By Majordennisbloodnok , 3 days ago
-
RE: Say hello and introduce yourself
@jandp awesome system I hope it works out well.
By Judith , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@bobflux That's the stuff. The installer recommended tw...
By tomasmcguinness , 5 days ago