Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Buffer tank bypass on EDF Ideal heat pump installation
I have an Ideal Logic Air installed through EDF heat pumps. They insisted on having a buffer tank and CH pump. I argued against and we came to a compromise - by installing a bypass on the buffer (on the flow and return sides). The pump does not have a bypass. Does anyone have recommendations on how best to set this up? I could bypass it completely, have the hot water bypass it, have the return bypass it. Also can I keep the pump running or unplug it (easy to do)?
incidentally the efficiency as stated on the control box is awful SCOP 1.7. But it doesn’t seem particularly expensive and the house is warm. When I called Ideal support they told me not to trust it!
I would bypass the buffer tank in one of flow or return only, it will then act a bit like a volumiser.
The problem you have relatively to a tank that was deliberately plumbed as a volumiser will be stratification. Really you want input and output at different levels so that it gets stirred up. Normally the recommendation is to put a volumiser in the flow, but with stratification messing it up a bit Im not so sure. Try and see. The symptom of stratification will be additional cycling. Either way its got to be better to leave it in than to take it out altogether.
As to the pump you really want to bypass it. I fear that if you turn it off it will impede flow (try it and find out!). If you leave it on the two pumps may fight each other but probably not.
Maybe someone else has actually tried this experiment and worked out the best way!
To get value out of bypassing the buffer you will need to adjust your WC curve down to compensate for the loss of temperature across the buffer which will no longer be occurring.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks James.
I know that the 5kW unit has the same circulation pump as the bigger units but its flow is capped to 70% by default but it can up changed in the settings. If I turn the second pump off at least there is some extra capacity that I can use to try to push through the other pump. If it works I could look at removing it later on. I will try and give an update.
@kevb, before you re-plumb, I'd speak to EDF as it may invalidate your warranty if something goes wrong.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Well I can try the valving which can be undone so I don’t see that’s an issue. But yes removing the pump would be different matter.
@kevb, many of these companies look for the smallest of excuses to not honour warranties.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 26 Forums
- 2,677 Topics
- 62.6 K Posts
- 210 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Floor standing brackets for K3 rads
My neighbour is a plumber and said I would need to fit ...
By Singlespeed , 6 minutes ago
-
After an intense recode, I’m pleased to announce that w...
By Mars , 15 minutes ago
-
RE: Heat pump installation quotations
@batpred, @sttpd1917 I agree with what @batpred says...
By JamesPa , 15 minutes ago
-
RE: Harvest Thermal - ASHP with a smart thermal battery
As its using ToU tarrifs then its totally believable so...
By JamesPa , 2 hours ago
-
Why do you want to maintain a specific deltaT? The out...
By JamesPa , 2 hours ago
-
Hopefully this will answer your question. To...
By ASHP-BOBBA , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I would be interested to find out if others do this and...
By ASHP-BOBBA , 3 hours ago
-
Don't you dare. You just carry on as you are; as @batpr...
By Majordennisbloodnok , 4 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@ragtime27 some rooms in our house only have one place ...
By Judith , 4 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 8 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 9 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 9 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 13 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago