Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
ASHP fault for DHW only with high set point – P1 error on 6kW Grant Aerona 3
Hi, has anyone seen an issue where an air source heat pump warms radiators fine, and warms Domestic Hot Water fine when the setpoint is set lower to 40c, but gives an error when the DHW set point is set higher to 45C?
For context it's a 6 year old 6kw Grant Aerona 3, and it's been working fine until recently where we started seeing a P1 error.
Resetting it gets it running again but we've noticed that it's always heating DHW when it trips, and that lowering the DHW set point seems to fix the issue permanently.
Still, doesn't seem right that it can't deal with a 45C DHW setpoint.
System pressure is 1.5 bar, all valves are fully open, the mag filter is clean and the 2 port motorised valve for the DHW tank appears to be working fine so I don't believe there is any water flow restriction into the tank that would account for the P1 high pressure error.
Hi
Im not a Grant expert but the Grant R32 manual says the following - it this the error?
I wonder how it detects this error. One would think it was the flow meter but it could be temperature sensors. You seem to have checked the obvious, the other things I can think of are: Is there a fine mesh filter somewhere (I have one on my Vaillant system that wasnt obvious until the installer pointed it out), is there a real time readout of flow rate which could confirm. Are there any other real time diagnostics that might tell you whats going on?
I suppose its possible that its a compressor fault - has it been serviced recently?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks for the reply. Yeah there isn't a mesh filter or strainer anywhere in the system, just the mag filter which is clean.
It probably is due a service alright. Just curious that it only happens when DHW setpoint is increased. I'll try find the flow diagnostics too, to confirm it's a flow rate issue.
@2019ashp I’ll ask Grant for their thoughts tomorrow… strange that it only happens in DHW.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @2019ashpThanks for the reply. Yeah there isn't a mesh filter or strainer anywhere in the system, just the mag filter which is clean.
It probably is due a service alright. Just curious that it only happens when DHW setpoint is increased. I'll try find the flow diagnostics too, to confirm it's a flow rate issue.
I don't know the Grant system but this is common when there is air trapped in the tank circuit which causes the water to have reduced flow and reduced heat exchange causing this fault. If there are thumb valves or AAV's on that section of line you should check they are open or open and bleed them, its effectively the same result as having air in the top of a rad, seems like it gets hot on the pipes but not doing much on the emitter.
I would find the code that give you the flow rate on the water circuits and check it in heating and hot water and compare them.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Cheers, yeah there's no AAVs or thumbvalves approaching the outdoor unit.
One of the first things I done was check the AAV on the outdoor but itself and purge some water through.
The p1 error is often caused by an airlock but system is well bled in this case.
Posted by: @2019ashpCheers, yeah there's no AAVs or thumbvalves approaching the outdoor unit.
One of the first things I done was check the AAV on the outdoor but itself and purge some water through.
The p1 error is often caused by an airlock but system is well bled in this case.
I think @ashp-bobba was referring to a possible airlock in the DHW circuit, near the DHW tank itself. As this is usually a high point in the DHW circuit there should be a bleed valve (automatic or manual) near the tank.
Given your symptoms that does seem very plausible to me; @ashp-bobba does this for a living so should know!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @2019ashpCheers, yeah there's no AAVs or thumbvalves approaching the outdoor unit.
One of the first things I done was check the AAV on the outdoor but itself and purge some water through.
The p1 error is often caused by an airlock but system is well bled in this case.
I think @ashp-bobba was referring to a possible airlock in the DHW circuit, near the DHW tank itself. As this is usually a high point in the DHW circuit there should be a bleed valve (automatic or manual) near the tank.
Given your symptoms that does seem very plausible to me; @ashp-bobba does this for a living so should know!
Yes, I have seen "many times" where the indirect coil connections raise up but no air bleed, it only takes a small amount of air in the line to effect the flow rate.
Perhaps we can get a picture of the set up to see how it is?
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@jamespa Of course that's what he meant, I was half asleep 🙂
I had look for a way of bleeding this last week but there doesn't seem to be a bleed valve on the grant monowave tank, nor an aav\thumbvalve on the plumbing circuit near the tank. Poorly designed IMO.
But yes it does seem very, very plausible indeed with the symptoms.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobbaYes, I have seen "many times" where the indirect coil connections raise up but no air bleed, it only takes a small amount of air in the line to effect the flow rate.
Thats worrying, its like an obvious place for air to collect; why would you not put a bleed there (no need to answer that!)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,645 Topics
- 61.8 K Posts
- 478 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Anyone concerned about GivEnergy?
So it seems subscription day has finally arrived for Gi...
By TechnoGeek , 42 minutes ago
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
No, I agree entirely. There shouldn't be a need for an ...
By Majordennisbloodnok , 2 hours ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 3 hours ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 3 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 3 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 16 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 1 day ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago