Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
ASHP fault for DHW only with high set point – P1 error on 6kW Grant Aerona 3
Hi, has anyone seen an issue where an air source heat pump warms radiators fine, and warms Domestic Hot Water fine when the setpoint is set lower to 40c, but gives an error when the DHW set point is set higher to 45C?
For context it's a 6 year old 6kw Grant Aerona 3, and it's been working fine until recently where we started seeing a P1 error.
Resetting it gets it running again but we've noticed that it's always heating DHW when it trips, and that lowering the DHW set point seems to fix the issue permanently.
Still, doesn't seem right that it can't deal with a 45C DHW setpoint.
System pressure is 1.5 bar, all valves are fully open, the mag filter is clean and the 2 port motorised valve for the DHW tank appears to be working fine so I don't believe there is any water flow restriction into the tank that would account for the P1 high pressure error.
Hi
Im not a Grant expert but the Grant R32 manual says the following - it this the error?
I wonder how it detects this error. One would think it was the flow meter but it could be temperature sensors. You seem to have checked the obvious, the other things I can think of are: Is there a fine mesh filter somewhere (I have one on my Vaillant system that wasnt obvious until the installer pointed it out), is there a real time readout of flow rate which could confirm. Are there any other real time diagnostics that might tell you whats going on?
I suppose its possible that its a compressor fault - has it been serviced recently?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks for the reply. Yeah there isn't a mesh filter or strainer anywhere in the system, just the mag filter which is clean.
It probably is due a service alright. Just curious that it only happens when DHW setpoint is increased. I'll try find the flow diagnostics too, to confirm it's a flow rate issue.
@2019ashp I’ll ask Grant for their thoughts tomorrow… strange that it only happens in DHW.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Posted by: @2019ashpThanks for the reply. Yeah there isn't a mesh filter or strainer anywhere in the system, just the mag filter which is clean.
It probably is due a service alright. Just curious that it only happens when DHW setpoint is increased. I'll try find the flow diagnostics too, to confirm it's a flow rate issue.
I don't know the Grant system but this is common when there is air trapped in the tank circuit which causes the water to have reduced flow and reduced heat exchange causing this fault. If there are thumb valves or AAV's on that section of line you should check they are open or open and bleed them, its effectively the same result as having air in the top of a rad, seems like it gets hot on the pipes but not doing much on the emitter.
I would find the code that give you the flow rate on the water circuits and check it in heating and hot water and compare them.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Cheers, yeah there's no AAVs or thumbvalves approaching the outdoor unit.
One of the first things I done was check the AAV on the outdoor but itself and purge some water through.
The p1 error is often caused by an airlock but system is well bled in this case.
Posted by: @2019ashpCheers, yeah there's no AAVs or thumbvalves approaching the outdoor unit.
One of the first things I done was check the AAV on the outdoor but itself and purge some water through.
The p1 error is often caused by an airlock but system is well bled in this case.
I think @ashp-bobba was referring to a possible airlock in the DHW circuit, near the DHW tank itself. As this is usually a high point in the DHW circuit there should be a bleed valve (automatic or manual) near the tank.
Given your symptoms that does seem very plausible to me; @ashp-bobba does this for a living so should know!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @2019ashpCheers, yeah there's no AAVs or thumbvalves approaching the outdoor unit.
One of the first things I done was check the AAV on the outdoor but itself and purge some water through.
The p1 error is often caused by an airlock but system is well bled in this case.
I think @ashp-bobba was referring to a possible airlock in the DHW circuit, near the DHW tank itself. As this is usually a high point in the DHW circuit there should be a bleed valve (automatic or manual) near the tank.
Given your symptoms that does seem very plausible to me; @ashp-bobba does this for a living so should know!
Yes, I have seen "many times" where the indirect coil connections raise up but no air bleed, it only takes a small amount of air in the line to effect the flow rate.
Perhaps we can get a picture of the set up to see how it is?
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
@jamespa Of course that's what he meant, I was half asleep 🙂
I had look for a way of bleeding this last week but there doesn't seem to be a bleed valve on the grant monowave tank, nor an aav\thumbvalve on the plumbing circuit near the tank. Poorly designed IMO.
But yes it does seem very, very plausible indeed with the symptoms.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @ashp-bobbaYes, I have seen "many times" where the indirect coil connections raise up but no air bleed, it only takes a small amount of air in the line to effect the flow rate.
Thats worrying, its like an obvious place for air to collect; why would you not put a bleed there (no need to answer that!)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 592 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 25 minutes ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 6 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 11 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago