Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan new build install - zoning question
Hi apologies, if this is a duplicate post. We have newly purchased a new build that has a Ecodan R32 ASHP.
FTC is in the cupboard with all the tanks and has 1 wireless controller downstairs and 1 wireless controller upstairs.
The system has been configured as 2 "zones" and a wireless controller assigned to each. Am I correct in thinking that the way Ecodans work in this situation is that zone 1 sets the whole house temp and zone 2 allows you turn off the rads in that zone if you are too hot but not call for heat ie set a temperature higher than the zone 1 temp if you are too cold?
Thanks in advance
@darlomrh, not quite, it is normal to set the unit up so that each wireless stat can energise the Ecodan and run any single zone, usually there would be an S-plan valve actuated, this will be in place to prevent migration when zone is not needed.
This is a classic setup but the designer needs to be sure each zone can reach the minimum flow and output of the ASHP lowest output to prevent unwanted cycling and allow minimum volume for defrost. The minimum water volume may be satisfied by a volumiser in this case but it will not prevent the short cycling if the circuit cannot dissipate the minimum output of the ASHP when a small amount of heating is required.
Hopefully they designed your ASHP somewhere near 20-30W/m2 so its not over sized and can cope with the zoning assuming your new build is built to the latest energy standards.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Thanks for the reply. I hope this the case. I think it's a case of just finding the sweet spot for the house.
It's been a confusing start, when we first had the house, no matter how high we had the setpoint on the downstairs RC, no heat in the rads. Turned out that the RC downstairs was controlling the upstairs zone so it was 24c upstairs by the time we went to bed. We had the installers out to fix that.
Currently
RC1 is set for Zone 1 temp and Zone 1 Programme
RC2 is set for Zone 2 temp and Zone 2 Programme
The thing that is confusing me and it's probably a perception thing. RC1 is upstairs and RC2 is downstairs.
Picture from Melcloud home (I had no choice when I registered my equipment, Melcloud couldn't find the big white unit so I had to use MCHome ) I don't think this helps the perception.
- 26 Forums
- 2,634 Topics
- 61.5 K Posts
- 626 Online
- 7,030 Members
Join Us!
Latest Posts
-
RE: Setback savings - fact or fiction?
I too agree with what you say, and am grateful to you f...
By cathodeRay , 10 minutes ago
-
RE: Vaillant Sensocomfort Time
Thank youy for the pointer. I think I have managed to ...
By ispookie666 , 1 hour ago
-
RE: Forum updates, announcements & issues
I have been doing a lot of work on the site lately and ...
By Mars , 1 hour ago
-
@majordennisbloodnok good advice, thanks for that.
By David999 , 5 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
I am following this thread with great interest and than...
By TaffontheTaff , 8 hours ago
-
RE: Sizing an ASHP; Heat loss and kW
You can't measure heat loss with a website. But you ca...
By JamesPa , 23 hours ago
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a — I have a sort of residual interest in this pr...
By cathodeRay , 1 day ago
-
Hi, Thank you. So its a Daikin Altherma 3M...
By Lbart68 , 1 day ago
-
I have a Contactum CU. Would the below RCBO (descriptio...
By Batpred , 1 day ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
@chainreaction Agree with @broadsman , it seems many ...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
@transparent Thank you and appreciate your timely reply...
By SUNNYSKIES , 1 day ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
The hot water heating looks normal. The heat transfer ...
By GrahamF , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 2 days ago