Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
ASHP and PV diverter working together
- it pumps hot water into the cylinder through the coil. that only takes the temperature inside the tank to between 45 and 50C.
- there's 2 wires from the pump to a box next to the cylinder (one for power and one for data). the box contains a circuit breaker and a contactor that decides whether energy is sent to the immersion heater to top up the temperature.
- is this set up even possible? if so, do you have any details setting it up that you can share? what i understand is that when paired with the heat pump, the immersion heater would only work if lg sends the signal and there's excess energy being produced. this doesn't seem very practical to me, but maybe i'm not understanding how it really works. the electricians tell me that i can also press the boost button on the iboost, but it wouldn't really work unless lg decides it has to be on anyway. actually, the way they've tried to set it up (iboost between the contactor and the tank) means that the iboost will not even be on until lg tries to start the heater. it has not direct feed most of the time.
- if this is possible, do you reckon it's worth doing? my dhw is usually set between 48 and 50 depending on the time of the year. it's enough even when 2 people have a shower at the same time. i have a night tariff that i use to charge batteries overnight already in winter and i can schedule the pump to heat the water so that it's ready when we get up. i have no idea about the financials about both options, but again, i'm looking for a practical solution unless using iboost is much cheaper than the current set up.
Posted by: @ewan-costarHi,ÂI've got both a solar pv and an ashp system.ÂThe solar system also has 2 batteries and it's configured to fill the batteries first and then export to the grid when they are full.ÂI don't think it matters, but the pump is an LG Therma V R32 monobloc.From what I understand (I'm not an electrician or have any kind of technical background), the heat pump is connected to the cylinder in the attic in 2 different ways:Â
- it pumps hot water into the cylinder through the coil. that only takes the temperature inside the tank to between 45 and 50C.
- there's 2 wires from the pump to a box next to the cylinder (one for power and one for data). the box contains a circuit breaker and a contactor that decides whether energy is sent to the immersion heater to top up the temperature.
ÂIt's all working fine, except that I've still got an iboost+ (or similar) pending to be fitted. We've been back and forth with the installer for almost a year now.The installers have tried the solic200 and the solar iboost+ so far without success. They designed the system with this (without specifying the model) and i didn't even know this existed before they mentioned it to me.ÂThey've sent me a few electricians. Every new guy tells me a different thing about compatibility with the heat pump and even some times they manage to break things that were already working when trying to make it work. i've lost trust on them.We have a bad relationship at the moment and I'd rather get this installed and working if possible rather than having to battle for a refund that may take a long long time.Âthe original design said that the diverter would be wired into the lg box and use energy that would go into the grid to heat the water.however, now that i've looked into it, it doesn't make a lot of sense to me.Âdespite all the conversations with engineers and my own research, I'm not really an expert by any stretch of the imagination, so I would then like to ask you for your experience with similar setups. I've got 2 main questions:Â
- is this set up even possible? if so, do you have any details setting it up that you can share? what i understand is that when paired with the heat pump, the immersion heater would only work if lg sends the signal and there's excess energy being produced. this doesn't seem very practical to me, but maybe i'm not understanding how it really works. the electricians tell me that i can also press the boost button on the iboost, but it wouldn't really work unless lg decides it has to be on anyway. actually, the way they've tried to set it up (iboost between the contactor and the tank) means that the iboost will not even be on until lg tries to start the heater. it has not direct feed most of the time.
- if this is possible, do you reckon it's worth doing? my dhw is usually set between 48 and 50 depending on the time of the year. it's enough even when 2 people have a shower at the same time. i have a night tariff that i use to charge batteries overnight already in winter and i can schedule the pump to heat the water so that it's ready when we get up. i have no idea about the financials about both options, but again, i'm looking for a practical solution unless using iboost is much cheaper than the current set up.
ÂI called iboost and solic manufacturers, and also LG. they all have told me that they have clients using the 2 things together, but wouldn't give me any hints/help/recommendation on how to set them up. they just don't want to offer any help with something they don't make themselves.Âany help would be greatly appreciated.
Electrical power diverters are excellent devices, we have had one connected to our system for quite a number of years.
Because they use electronic components to regulate the amount of power being diverted, I don't think that they would take too kindly to being reverse fed, that is having a 240v ac supply connected to the output terminals.
This prevents an immersion heater from being supplied from two different sources at the same time, one being the power diverter and the other being a separate 240v ac supply.
What is the size of your solar PV system?
If you have sufficient solar generation and don't use vast amounts of hot water, you may find that your solar system can provide the majority, if not all, of the hot water you use from Spring through to Autumn. To do this using the power diverter it would need to be connected directly to your electricity consumer unit, with the output from the power diverter wired directly to the immersion heater. By setting the immersion heater thermostat at 65C, it would periodically perform cylinder sanitization when there is sufficient solar generation. If there is an extended period when there is insufficient solar generation to perform legionella control, you would need to use the boost function. It may be possible to schedule the boost function either within the iboost itself, or if it can accept an external signal, from the heat pump controller. By heating the water using solar PV it should reduce the amount of water heating that your heat pump would need to perform.
I assume that for the heat pump controller to perform the legionella cycle, it will be energising the contactor that you mention, since a 3kW immersion heater will draw approximately 12.5 amps from the 240v ac supply.
Can you provide a closeup photo of your contactor and circuit breaker, so that they can be identified.
If the contactor has both Normally Open (NO) and Normally Closed (NC) contacts, and they are break before make, it may be possible to wire both the power diverter, and the alternative power supply, to the immersion heater via the contactor. It could operate in the following manner.
The electrical supply would be connected to the immersion heater via the NC connections during the majority of the time, and would provide solar energy to the immersion heater when it is available. It would also be possible to use the boost function if necessary.
If the heat pump controller is scheduled to perform the legionella cycle, it will energise the contactor. This will disconnect the immersion heater from the power diverter supply and connect the immersion heater to the alternative power supply. Simples. 😎Â
Â
Bit of an old thread but this is the way i am planning to use my iboost in case it helps anyone.
I have a Daikin Mono and third party cylinder.
I have three options
1) let the ASHP control the immersion for the boost periods such as the legionella cycle.
2) let the iboost control the immersion
3) Do some fancy stuff with additional relays/contactors so both are connected but only one live at a time.
WARNING! The iboost powers the immersion via a DC output and not AC240v. Therefore you CANNOT connect both the ASHP and Iboost at the SAME time without an interlock.
I'm going to keep it really simple based on wanting to use the spare solar energy I have as close to 100% of the time as i dont have a battery to take the excess.
I will wire only the iboost to the immersion so that the sun heats my water through the summer and assists through part autumn and spring.  I know when the once per week legionella cycle will run.  I do that at 1300hrs when my solar is generating max energy and i also do this on a Saturday as the hot 60c water is more likely to be used up earlier for going for an evening out.  As i know its Saturday at 1300hrs, i simply set the iboost "boost" schedule to come on at about 13:15 for 45 minutes.
Â
I will choose 45 minutes as I will assume a starting water temp of 50c at the point the iboost schedule starts. It takes 35 mins to heat 150 litres (my tank size) from 50c to 60c and i want it maintained for 5-10 mins at 60c. I will monitor this to get an accurate amount of time needed to heat the delta 50c to 60c (Delta 10) and adjust to make it the most effective.
The iboost mains boost will only come on if there is something to do, which in the summer wont be much as the solar heats it to max most days anyway.
Â
Â
Â
Â
Â
Â
Â
Â
-
Hot water tank lose heat rapidly on random days
3 weeks ago
-
Heat pump done right first time? Installation in Kent.
3 weeks ago
-
Why Buffer Tanks & Low-Loss Headers Can Sabotage Your Heat Pump's Efficiency
2 months ago
-
British Gas Heat Pump Installation Complaint
5 months ago
-
Heating Turned Off but Radiators Still Warm
6 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 523 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago