Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hi Sam,
It would appear, that as I feared, your ASHP is poorly sited and is creating as batalto stated a 'cold well'.
Because the cold air coming out of your ASHP is more dense (heavier) than the warmer air above, it cannot escape and is pulled back into your ASHP and cooled even further. Hence the 12C difference in temperature around your ASHP with the ambient air temperature.
As a quick way to check the effect on your ASHP of having warm air going in rather than cold air, it may be possible to make a simple duct from strong cardboard, or similar, to funnel warm air from above your ASHP into the intake. Basically, you need to put cardboard on each side of your ASHP, from the ground to about 2 metres high. Tape it to the wall and the sides of your ASHP and tape over any leaks. Then put a third piece of cardboard above your ASHP up to the same height as the side pieces and tape the joints. Then put an old blanket or similar to stop air being sucked underneath your ASHP. If you are not certain what to do I can provide a sketch.
Obviously switch off your ASHP whilst you put the cardboard etc. in place.
If you now run your ASHP you should find that it is not working as hard as previously and the air temperature around your ASHP does not fall as low.
The optimum solution would be to re-site your ASHP to a more appropriate location.
I have recently installed an Air to Air ASHP at my home, and extended the pipework and electrics to position the outdoor unit at the desired location. Whether it is refrigerant pipework or water pipework it should be quite easy to extend within the maximum limit, which I believe is approximately 20 metres. You could even consider moving your ASHP some distance down your garden, though obviously this would require more work and hence be more expensive.
An alternative would be to mount your ASHP on a wall bracket so that it is above the fence height, though this would probably infringe on planning permission requirements.
I hope that this helps.
Regards,
Derek.
Thanks Derek,
Once we have sorted the sizing issue, I think the best thing to do would be to move it around the corner (did you see the images I uploaded?). This would only need a few metres of extension to the pipes.
Kindest regards,
Sam.
Hi Sam - I don’t think “moving it round the corner” is a simple task. Because of the power cables (the easy bit) but mainly the insulated water pipes (the difficult bit) that allow the heat water to flow into your home with directly to radiators/UFH or via a hydro box or buffer tank. You’d need to get a competent ASHP engineer in to discuss.
the chap who will be fitting my ASHP said south facing units can overheat in the summer and cut out. They need a north sited thermometer connected to know the real temperature.
lovely property by the way
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Volvo EX30 Ultra Twin Performance electric vehicles with Myenergi Zappi mk1 & Ohme chargers
Hi JulianC/Sam,
I did not mean a DIY move around the corner, it would have to be carried out by a competent Engineer.
Since the installation of Sam's ASHP does not meet the specified requirements of at least 1 metre from the boundary fence, then it should be the builders responsibility to have it re-sited to an appropriate location.
Regards,
Derek.
@derek-m, the rules for permitted development say that the ASHP needs to be 1m from the boundary. If Sam's house is a new build it would have had full planning permission, which could have included the ASHP being nearer the boundary. The builder definitely has a case to answer for the poor siting but it might not be a planning one. Is distance from boundary also specified as part of buildings regulations or MCS?
Hi Kev,
If I am understanding you correctly, to use permitted development to avoid the need for planning permission, you cannot install the ASHP closer than 1 metre from the boundary, but if you get planning permission you can stick it wherever you like!!!
I suppose that sounds about right for the modern world in which we now live.
@derek-m, planning departments, processes and decisions make my head ache.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@derek-m, theoretically yes, but I don't know if planning permission for an ASHP closer than 1m would be given or if there is anything else (building regs, MCS guidance) that might influence ASHP placement.
Hi all,
I just checked my current boiler (Ideal Vogue Max 32kW) and I checked the efficiency level which is an option in the menu. Its down at 58%! which is a real kicker considering its quite new. However this has totally changed my ASHP calculations as currently I am wasting 42% of my gas costs.
My gas use for the last 12 months was 34,600kW but with the efficiency calculations I actually only needed to use 20,000kW if the boiler was being efficient. I imagine it wasn't set up well when it was installed and I didn't really play with the settings. If I can get a COP of 2.7-3.0 in the winter I should reduce my current gas bill even without changing my electricity tariff.
I'd advise anyone looking at an ASHP to first consider how efficient their current boiler actually is!!!
@batalto, that's super interesting. I didn't realise that gas boilers were able to monitor this.
58% is crazy, which certainly paints a far more favourable picture for things like heat pumps.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
I totally forgot the boiler had the feature. I was told when it was put in that it should be 90% efficient. But I can just tap a button to see. To be honest it makes sense as the figure after efficiency matches up with the heat pump calculation I was given when they went room by room to work out my heating and loss demands.
Clearly the boiler is configured wrong or just isn't as good as stated. I imagine it's the former. I'm keeping it anyway as a backup heating system in case something ever goes wrong. But worth considering when your ASHP calculations
-
How Accurate Is My DIY Heat Loss Calculation?
1 day ago
-
Surface mount or bury primaries for heat pump installation?
1 day ago
-
Issue with Samsung Cascade System
1 month ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
2 months ago
-
Design Of Cascade System Replacing Undersized ASHP
2 months ago
Currently viewing this topic 2 guests.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 321 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 3 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 8 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 13 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago