Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Solis inverters S6-EH1P: pros and cons and battery options
As my battery packs were heavily used yesterday and had discharged to 20%, the charge window would mean they'd hit capacity around 6.30am so I decided to take a look at my packs this morning.
The conclusion.
As Andy and I have said, the Seplos BMS will ramp down the charge rate when nearing capacity (about 98.5-99%).
The issue is how quickly the charge rate ramps down to keep up with the cells now starting to race away (around 3.430V).
My full capacity target is 3.450V.
This is very very close to 100% fully charged. I am not chasing a tiny bit extra.
With aiming to be fully charged at 3.450V (55.20V total capacity )and the JK Balancer set to start balancing at 3.450V there is a small window to start balancing and the Seplos BMS to ramp down it's charge rate. If your cells aren't as well balanced as mine you may have even less time).
I observed about 5-10 minutes.
At this point the total pack voltage hit 55.20V, the BMS resets to 100% and shuts down the charge request.
Am I happy with this.
Yes and no.
My packs were top balanced at 3.600V and are still well balanced (15mV at 55.20V pack voltage), so they don't require much balancing.
However 5-10 minutes isn't a lot of time (plus a bit extra as they taper down when the charge current is stopped).
With this in mind I have set my balance start voltage to 3.410V which will give me about 30 minutes of balance time and should ensure they stay balanced at 3.450V (55.2V total pack), my target 100% full capacity.
As a side note I observed the the charge/discharge time window is 10 minutes out of sync.
My Inverter is set to charge between 12.10am and 6.50am to ensure I don't use any peak electricity during charging.
My packs started discharging at exactly 6.40am.
With this mind I have adjusted the heavy draw items (garage heater, EV charger etc) to stop at 6.40am to ensure they aren't discharging from the battery packs and reducing their capacity unnecessarily.
Posted by: @bashAs my battery packs were heavily used yesterday and had discharged to 20%, the charge window would mean they'd hit capacity around 6.30am so I decided to take a look at my packs this morning.
The conclusion.
As Andy and I have said, the Seplos BMS will ramp down the charge rate when nearing capacity (about 98.5-99%).
Thanks for checking and sharing!
It is odd that Fogstar advised differently, so either:
- they do not know how the Seplos BMS works
- they know, but prefer to close a query about how the Seplos BMS works by stating it does not do this, as they do not care enough
Some of their current battery kits use BMS from other manufacturers.
I am still planning to get my JK balancer to work.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Which is why ,I assume,Fogstar fit the JK balancer to their 16Kw Pace BMS batteries?
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
Posted by: @bashI'd change your JK balance start voltage a little lower to give a it a chance to actually balance your cells.
Yes, but I need to reopen the battery box.. I just noticed that the binary_sensor.503010d0243_problem "sensor" (on the JK HA integration) reports a problem. No details provided, so the first thing will be to recheck the cabling.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 846 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
Hi @ian33a you could do your own heat loss calculation ...
By Judith , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@djh ah, I have never seen this before, interesting ide...
By ASHP-BOBBA , 7 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 8 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa — this version may be marginally better: &nb...
By cathodeRay , 10 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 10 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 15 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 17 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 19 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 22 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 22 hours ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
That would be abnormal but I cant see from your charts ...
By JamesPa , 22 hours ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago