Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Solis inverters S6-EH1P: pros and cons and battery options
As my battery packs were heavily used yesterday and had discharged to 20%, the charge window would mean they'd hit capacity around 6.30am so I decided to take a look at my packs this morning.
The conclusion.
As Andy and I have said, the Seplos BMS will ramp down the charge rate when nearing capacity (about 98.5-99%).
The issue is how quickly the charge rate ramps down to keep up with the cells now starting to race away (around 3.430V).
My full capacity target is 3.450V.
This is very very close to 100% fully charged. I am not chasing a tiny bit extra.
With aiming to be fully charged at 3.450V (55.20V total capacity )and the JK Balancer set to start balancing at 3.450V there is a small window to start balancing and the Seplos BMS to ramp down it's charge rate. If your cells aren't as well balanced as mine you may have even less time).
I observed about 5-10 minutes.
At this point the total pack voltage hit 55.20V, the BMS resets to 100% and shuts down the charge request.
Am I happy with this.
Yes and no.
My packs were top balanced at 3.600V and are still well balanced (15mV at 55.20V pack voltage), so they don't require much balancing.
However 5-10 minutes isn't a lot of time (plus a bit extra as they taper down when the charge current is stopped).
With this in mind I have set my balance start voltage to 3.410V which will give me about 30 minutes of balance time and should ensure they stay balanced at 3.450V (55.2V total pack), my target 100% full capacity.
As a side note I observed the the charge/discharge time window is 10 minutes out of sync.
My Inverter is set to charge between 12.10am and 6.50am to ensure I don't use any peak electricity during charging.
My packs started discharging at exactly 6.40am.
With this mind I have adjusted the heavy draw items (garage heater, EV charger etc) to stop at 6.40am to ensure they aren't discharging from the battery packs and reducing their capacity unnecessarily.
Posted by: @bashAs my battery packs were heavily used yesterday and had discharged to 20%, the charge window would mean they'd hit capacity around 6.30am so I decided to take a look at my packs this morning.
The conclusion.
As Andy and I have said, the Seplos BMS will ramp down the charge rate when nearing capacity (about 98.5-99%).
Thanks for checking and sharing!
It is odd that Fogstar advised differently, so either:
- they do not know how the Seplos BMS works
- they know, but prefer to close a query about how the Seplos BMS works by stating it does not do this, as they do not care enough
Some of their current battery kits use BMS from other manufacturers.
I am still planning to get my JK balancer to work.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
Which is why ,I assume,Fogstar fit the JK balancer to their 16Kw Pace BMS batteries?
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
Posted by: @bashI'd change your JK balance start voltage a little lower to give a it a chance to actually balance your cells.
Yes, but I need to reopen the battery box.. I just noticed that the binary_sensor.503010d0243_problem "sensor" (on the JK HA integration) reports a problem. No details provided, so the first thing will be to recheck the cabling.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 712 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 49 minutes ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 6 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 12 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago