Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Is it mad to think there should be a minimum SCOP for UK heat pump installs?
Is it crazy to think that every UK heat pump installation should have to meet a minimum SCOP value?
We’ve now got tens of thousands of heat pumps going in, and yet there’s no performance benchmark for what’s actually considered “good”. MCS and installers can say a system is “working”, but what does that mean if it’s running with a SCOP of 2.2 and the house still struggles to hit 21C?
Heat pumps are incredibly easy to monitor and we can see exactly how they’re performing. So why not draw a clear line in the sand?
For example: anything below a SCOP of 3 (at 21C) is sub-par. Anything above is acceptable.
No more guesswork. No more arguments about “every home is different”. Just a clear, fair, measurable standard that protects homeowners and gives everyone clarity.
What do you think? Fair idea or unrealistic?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
BUS requires minimum SCOP of 2.8, see https://www.legislation.gov.uk/uksi/2022/565/regulation/9
Building regulations require
Reasonable provision shall be made for the conservation of fuel and power in buildings by—
(a) limiting heat gains and losses— (i) through thermal elements and other parts of the building fabric; and (ii) from pipes, ducts and vessels used for space heating, space cooling and hot water services;
(b) providing fixed building services which— (i) are energy efficient to a reasonable standard; (ii) have effective controls; and (iii) are commissioned by testing and adjusting as necessary to ensure they use no more fuel and power than is reasonable in the circumstances.
The requirements, at least arguably, already exist, the problem is enforcement.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa, I don’t think that’s quite right. The regulation you’re referring to doesn’t require the installed system to achieve a SCOP of 2.8… it says the heat pump unit itself must have a seasonal coefficient of performance of at least 2.8, based on the Secretary of State’s approved test method (whatever that’s supposed to mean).
That figure comes from laboratory testing of the unit (including some dodgy Chinese labs), not from how the full system performs once it’s installed in someone’s home.
So in practice, we still don’t have a benchmark for real-world system performance. Until we start measuring and setting minimum in-situ performance values, poor installs will continue to slip through the net IMO.
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
Posted by: @editor@jamespa, I don’t think that’s quite right. The regulation you’re referring to doesn’t require the installed system to achieve a SCOP of 2.8… it says the heat pump unit itself must have a seasonal coefficient of performance of at least 2.8, based on the Secretary of State’s approved test method (whatever that’s supposed to mean).
That figure comes from laboratory testing of the unit (including some dodgy Chinese labs), not from how the full system performs once it’s installed in someone’s home.
Fair enough, I stand corrected, my apologies.
In that case its currently down to the protection (if any) provided by Building Regs. The requirement is quite general however the guidance is more specific and says that, "in the opinion of the Secretary of State" (the phrase used in the guidance) the requirement is met if the heat pump has a SCOP of 3 for space heating and 2 for DHW (which is interesting - you can get the BUS grant for a heat pump that does not meet the guidance in the building regs). A test method is specified and it is, I believe, the one applying to heat pump units not systems, so same problem.
Since your question asks - is it mad?, lets examine this specific question, or to turn it around, is it practical?. To be practical as a piece of law you need to be able to define a test method which is sufficiently cheap and robust and enforceable. You will need to specify reference points and a test method.
I could imagine defining a test method where the reference points for output are the pipes which directly feed the emitters (ie beyond any system separation which I think you would agree is essential), and the reference point for input is the electricity feed to the ODU. I cant see how you could define a test method for the house as a whole and practically speaking it would be difficult to define a measurement point that is guaranteed to include controls and any secondary pumps. The ODU reference point would still allow energy to be lost in the length of pipe between the test point and the emitters, but that is probably a secondary consideration, as is electricity consumed by control equipment. Secondary pumps can be a significant draw in a low loss house, but perhaps an allowance could be made for these which would be adequately accurate.
We would need to define a climate curve against which to test the SCOP. That's possible and might vary according to location, or may just be representative of the UK.
Then we would need to collect measurements. This would require a flow meter and temperature measurement at the output reference points, an electricity meter at the input reference points and a data logger. The former is the issue here, they aren't particularly accurate and arent particularly cheap. The openenergymonitor heat pump monitoring bundle is essentially these components and retails at £461. We would need to log over a sufficient range of OATs to be able to extrapolate, say a month or two between mid October and end February in the South of England. The data would then need to be processed.
I would say this would be challenging to argue that this should be added to every installation from day 1 but quite possible if only installed on the occasions where there was a dispute. If (compulsory) provision were made for the plumbing access points to be included when the heat pump was installed then it might well be cost effective, although would probably still add £200 to every installation. At a first guess you would need 2 lockable valves, a piece of flexible pipe and a couple of couplings. You would also need a nearby source of power but perhaps that could be presumed.
If we go down the route of install only if there is a dispute the question arises - who would pay (if we instal on every system from day 1 then we know the answer - its the homeowner). I would say that the only answer likely to be acceptable to the industry is the homeowner, on the understanding that they would get the money back if they are proved to be correct. It could be covered by insurance, but that just means everyone pays. So the way it might work is, if there is a dispute, the homeowner has to fork out perhaps £500 to have the monitoring kit installed, wait a few months and then gets a determination and either a fix and their £500 back if there is a problem, or nothing if there is not. That sounds plausible, but wont help those who for example have had minimum cost installs under an ECO4 scheme because they qualify for a means tested benefit.
Obviously the above is just a first thought, but perhaps shows some of the challenges that need to be faced.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @editor@jamespa, I don’t think that’s quite right. The regulation you’re referring to doesn’t require the installed system to achieve a SCOP of 2.8… it says the heat pump unit itself must have a seasonal coefficient of performance of at least 2.8, based on the Secretary of State’s approved test method (whatever that’s supposed to mean).
That figure comes from laboratory testing of the unit (including some dodgy Chinese labs), not from how the full system performs once it’s installed in someone’s home.
So in practice, we still don’t have a benchmark for real-world system performance. Until we start measuring and setting minimum in-situ performance values, poor installs will continue to slip through the net IMO.
Or a minimum standard for data collection. The Daikin MMI gives unusable graphs on the tiny MMI interface. There are sums for input and output on different menus but you have to do any calcs for the COP/SCOP.
The Onecta app only recently started to show consumption graphs/totals, again no COP/SCOP calculation.
Posted by: @radwhispererOr a minimum standard for data collection. The Daikin MMI gives unusable graphs on the tiny MMI interface. There are sums for input and output on different menus but you have to do any calcs for the COP/SCOP.
The Onecta app only recently started to show consumption graphs/totals, again no COP/SCOP calculation.
This wouldn't solve the problem @mars is trying to solve, which is system COP not heat pump COP. To measure system COP you need to measure output at the emitters or at worst after any system separation (which is one of the main reasons for poor system COP!). its no good measuring it at the heat pump.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Sadly I think it is mad. If the BUS is not granted for too low a system SCOP (I forget the exact system interface definitions and numbers) then who pays the gap?
Is there a year delay before the BUS grant? then the installer has a cash flow problem if the customer doesn’t pay first. Or the customer ends up with no BUS and a poor install.
It’s great in principle but in practice it’s too difficult to enforce a minimum.
BUT recording the SCOP against each installer, on a “name and shame” basis would be good if Joe Blogs Install Ltd gets only 2.5 to 3.2 then who would choose them when comparing installers? It all revolves around would it be enough to use the heat pump’s value, or would compulsory heat pump measurements be necessary? The RHI scheme had a heat meter option and that showed an average of just 2.7, pretty damming.really.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
- 27 Forums
- 2,745 Topics
- 64.5 K Posts
- 766 Online
- 7,148 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
@editor Thanks for your response and recommendations. ...
By DavidB , 3 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
I think I saw a diagram for an exhaust air dhw tank wit...
By JamesPa , 16 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu Of course, in the way of such things, there a...
By Toodles , 23 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks, however that's an answer to a subtly different ...
By JamesPa , 3 days ago
-
RE: Flushing system, cleaning and inhibitor
Yes, my 50L volumiser uses the two lower ports, so ther...
By Old_Scientist , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Such elegant symmetry. look at my lumpy bag of...
By Papahuhu , 4 days ago
-
RE: PV and battery long payback - sense check query
Quite probably not, but you can get a 32A relay and a S...
By JamesPa , 4 days ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s Look forward to making contact soon! Regards, To...
By Toodles , 4 days ago
-
I don't notice mine defrosting, and most of the time Im...
By JamesPa , 5 days ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 5 days ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 6 days ago
-
I meant to say I cannot register my kit at Energyplus… ...
By Batpred , 6 days ago
Members Online
No online members at the moment