Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @bashI don't recognise that screenshot you have posted.
I spent many nights working out why the unit's weren't balancing as well as I'd hoped using the Seplos desktop app.
Once the batteries reached around 97-98% capacity the BMS would ask the Solis inverter to ramp down the charge rate, dropping to around 10A, possibly 5A, from the requested 100A charge rate I set
The screenshot is via home assistant, as it is currently working..
I would be interested to know if there's any configuration required to get it to ramp the charging down as it gets close to 100 soc.
I assume you are using pylontech protocol on both the BMS and the Solis sides? I think that does not allow control of the voltage range etc, or did I miss anything?
I also assume you are using the default config that Fogstar shipped the kit with?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
The easiest way to analyze what's going on is to post screenshots of the BMS configuration parameters and the inverter settings.
My blog where I write about all the systems in place and decisions made for my off-grid house at 63 degrees north in Finland.
There is no configuration required to the Seplos BMS settings. The BMS automatically does this for you.
I know that it does it as I spent many late nights staring at a computer screen trying to get my head around why the cell balance was off!
In the end I upgraded to the JK Active balancer, which confirmed conclusively that my cells had got out of balance, significantly.
The cells need to be reasonably balanced for the balancer to have an opportunity to top balance properly.
I had 4 cells that were way out. The cells ran away too quickly and never allowed the balancer time to do it's work.
In the end I made a lighting rig out of car headlight bulbs and discharged the over shooting cells to bring them back in line with the others.
Now that the cells were roughly the same I observed the BMS ramp down its charge rate once the cells got to about 3.450V, at which point the Active Balancer kicked in and moved the energy around the cells to get them properly balanced.
Once the total pack reached 57.6V the BMS shut down the charge rate to 0A.
The Active balancer still works when the cells are not charging until they drop back below 3.450V.
It is important to check your balance start voltage on the JK Active balancer.
The default is 3.450V and will keep going until the difference is less than 10mV.
You can change these, but I wouldn't. Do check though.
You need to really observe this through the Seplos app and JK bluetooth app as the batteries reach near capacity. This will mean staying up late one night (or more if they are out of balance, although I suspect you'll find they are probably balanced anyway).
Posted by: @upnorthandpersonalThe easiest way to analyze what's going on is to post screenshots of the BMS configuration parameters and the inverter settings.
On my Solis, there are only a handful of parameters in the timed charge periods (they are actually exactly the same for discharge periods). This is all that can be set:
- start and stop times of the period
- the amp level
- the soc level
For charging, I just split the last charging slot. So I now have a few slots before that, with a soc of 94-98. The last one now has 10A charging to soc 100.
The Seplos 16kwh battery was configured as below:
- battery type: Lithium Battery
- battery model: PYLON_LV
- Max charge current: 100A
- Max discharge current: 190A
- battery saving: Disable
- Max charge SOC: 100
Attaching screenshots reduces the resolution, making it unreadable.
So I made the screenshots with the Seplos BMS configuration accessible via this link:
https://drive.google.com/drive/folders/1YVChebpuYF5KqYWYK72GXrRq4C5Qi2TQ?usp=sharing
Perhaps @bash configs are different, and that would trigger the BMS to slow the charging down automatically.
Below I am including a graph including the charge current. That does not show any smoothing effect (as was the case with the power). Note: the charging periods shown are yesterday's, slightly different from the ones described above.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
As I said you are looking at the wrong thing.
You need to be connected to your BMS direct.
I am using the default settings of the BMS, so should be the same as yours unless you have fiddled with your BMS settings.
Posted by: @bashAs I said you are looking at the wrong thing.
You need to be connected to your BMS direct.
I am using the default settings of the BMS, so should be the same as yours unless you have fiddled with your BMS settings.
I don't think so. 🙂 My post crossed with yours, thanks for that. I will look at the cell balancing later.
All I am looking for now is to understand the "magic" that worked for you, enabling the Seplos BMS to slow the charging as the battery charge increases.
I assume you did not check the gdrive where I placed the screenshots with all the configs that I directly grabbed from the Seplos BMS?
Anyway, hopefully some fiddling with the Seplos BMS parameters worked in those overnight sessions.
As @upnorthandpersonal said, sharing your config is the simplest way. I can do the detailed comparison. 😆
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Interestingly having had a very quick look at your BMS settings, they look totally different to mine, not the values themselves, but the layout.
Are you definitely on Seplos V3?
How did you log onto the BMS?
I connect using the USB - RS485 cable supplied by Fogstar connected to my laptop using the Seplos Dev software application.
Posted by: @bashYou need to set your alarm for 3am and do some observations 😆
At the moment, my HA is doing the monitoring job. I thought I would do the tedious job to compare all those parameters. 😆 Anyway, when you get a chance..
I did have a few late evenings to get Solis on a straight and narrow. What I rather forget is the DIY pack building "customer experience"..
Posted by: @bashInterestingly having had a very quick look at your BMS settings, they look totally different to mine, not the values themselves, but the layout.
Yes, this is the layout on the Seplos bluetooth app, called Octopus. It is a V3 and I upgraded the firmware to 1.5.
For some reason I cannot access the JK LB via their app, but HA still plots some basic data. I suspect it is not doing anything..
As for the values for the Seplos BMS, the old Fogstar just advised me to change one or two values.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@batpred - Two observations:
1: Since a USB to RS485 adapter is cheap and readily available, I recommend getting one so you're seeing the same data format as @bash
2: I don't like the idea of using HA to scrutinise parameters held by a BMS.
It will only collect the data which the Modbus command is constructed to give you.
Ramping down of the charge current may not be detectable by HA is its present configuration.
Save energy... recycle electrons!
Posted by: @transparent@batpred - Two observations:
1: Since a USB to RS485 adapter is cheap and readily available, I recommend getting one so you're seeing the same data format as @bash
2: I don't like the idea of using HA to scrutinise parameters held by a BMS.
It will only collect the data which the Modbus command is constructed to give you.Ramping down of the charge current may not be detectable by HA is its present configuration.
Thanks. It is not clear how @bash concluded the charging is being smoothed by the Seplos BMS. Also, I would need a config before I can check mine.
I agree with 1, when @bash is able to share
Regarding 2, plotting data that comes direct from the Seplos BMS on HA has been very reliable.
What I could see is that charging power data that is retrieved from the Solis is smoothed artificially. That itself lead me to need confirmation the Seplos could be slowing the charging.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 317 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 4 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 4 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 4 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 5 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 6 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 7 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 9 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 9 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 11 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 14 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 17 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago