Battery with existing PV - regulations
Im now looking again at batteries because recent changes in tarifs (which are no surprise and I suspect are the direction of travel) have altered the equation. I have grid tied solar and I am looking at grid tied AC coupled batteries. Ideally I would want islanding to be possible to cover power cuts and 3.6kW output maybe a bit more
At this stage I am trying to get my mind around the regs. As I understand it
a) even if the battery inverter is set so that it does not discharge when this would lead to export, I still need G99, which will need to specify both inverters, because the DNO assumes it might export. This might limit the max output of the battery inverter even though its not intended to export
b) If the inverter does support islanding, there must be a suitable cut out device |(presbetween the supply and any part of the internal wiring that will be energised during a power cut, to ensure that nothing is fed back to the grid in this circumstance
Have I got this correct? Im not trying to 'design' the system, just understand so I am an informed customer!
Also, has anyone looked seriously at sodium ion batteries. They seem to be obtainable and are, at least prima facie (but who knows what happens under the hood), more ethical in production and lower fire risk.
Sorry to ask simple questions, Im starting on a new learning curve here!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaa) even if the battery inverter is set so that it does not discharge when this would lead to export, I still need G99, which will need to specify both inverters, because the DNO assumes it might export. This might limit the max output of the battery inverter even though its not intended to export
I have just been through this. I had an electrician connect a battery to an inverter to my consumer unit (and I had previously had the CU replaced to improve safety).
I am not familiar with combined battery+inverter, my preference was to have a set that works, I chose low voltage lifepo4 as I understood it was the best value. I made the mistake to get a battery kit, there are now ready made 16kwh batteries starting at £1000.
I chose a solis hybrid inverter that provides 4ms switch from power failure, essentially it is fast enough that no device notices it. I did some tests. I switched the consumer unit off, all ok, the inverter made a few clicks and all continued as normal. I then switched it back to grid, again no issues, no flicking, as the inverter kept handling the load with the battery. It took some time to defer to use grid power. I think these timings are mandatory for approval.
I was not planning to export, but when I contacted my DNO (UK Power Networks) to let them know I had an inverter, they said they did not need to know unless I would be exporting. They "offered" 5kw export and said "just fill in the details in the initial G99 form as if G98". In short, right now I have an export MPAN.. for 8kw.. All without any MCS overhead.
As I underspent, we are now considering investing the spare funds and getting PV a bit earlier than we thought.
The regs may be a bit more restrictive than what UKPN allows.. So it may depend on what your DNO says and it may depend on your local grid as well.
Posted by: @jamespab) If the inverter does support islanding, there must be a suitable cut out device |(presbetween the supply and any part of the internal wiring that will be energised during a power cut, to ensure that nothing is fed back to the grid in this circumstance
Have I got this correct? Im not trying to 'design' the system, just understand so I am an informed customer!
Officially you may, and there is apparently only one brand of inverter in the list that does not require a separate device.
@transparent kindly provided an explanation of the oscillators the inverters have to support islanding, etc.
Still, my experience was that UKPN was happy to accept the Solis G100 capability. I contacted them after the system was up and running (I always made sure it was set to not export). When filling in the G99 commissioning form, provided the inverter is type approved, much of it does not need to be tested on your installation. it is "out of the box". Very little work involved, it seemed. They were very helpful.
Posted by: @jamespaAlso, has anyone looked seriously at sodium ion batteries. They seem to be obtainable and are, at least prima facie (but who knows what happens under the hood), more ethical in production and lower fire risk.
That may be a longer route.. If you search for sodium, some suggestions were made, but I think nobody ordered it, or if they did, I do not recall a report of the experience.
16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
G99 needed for ac coupled battery. DNO will assume it can export unless it is type tested G100 and installed how the DNO likes to be export proof. Limiting export via software settings is not considered inherently safe or reliable.
PV inverter + battery inverter together count as combined generation capacity.
If you want it to power the house during a grid outage, it must have a certified anti-islanding mechanism. Must comply with Engineering Recommendation G98/G99 and ENA anti-islanding requirements.
Sodium ion batteries are heavy, LFP cells are now so cheap the shipping is the majority of the price. So sodium has to "compete" against that. Sodium is dirt cheap, but you'll never avoid the weight. The temp tolerance is moot in domestic storage application where its being constantly cycled. They have lower power density and a wider, annoying, voltage range, which means inverters will need to change for them.
To make clear, my Solis inverter has anti islanding. But because it has a couple of separate ports that it can serve independently from the grid, those can continue to work based on PV or battery. So only the grid port looses power to prevent islanding.
16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Hi It well worth getting the G99 as it opens up "options"
I have the give energy AIO and "gateway" and yes i to had to get a G99 giving me 9.64kw export.
the AIO can discharge at 6kw which works for us.
the Gateway will go into "island Mode" if the grid is down all Automatically.
also when the AIO is support the home any solar will continue to charge or run the house, without the need for the grid.
A 2 box solution, just works ! and is tidy !
I see the Powerwall 3 can do a higher discharge and they do an equivalent to a "gateway"
Regarding Sodium I think in a year that be more options but your need more space for the same capacity.
I to will expand my storage with sodium when it more of a option..
Posted by: @swwils@batpred The EPS output can be tricky to do to current regs. The old "rcd socket for type 2 only!" doesn't really cut it anymore.
I have the export MPAN, what are you talking about?
This is how it is working, before exporting..
16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @rob-heatpump-bobRegarding Sodium I think in a year that be more options but your need more space for the same capacity.
I to will expand my storage with sodium when it more of a option..
I am curious... which inverter would you go with for sodium batteries?
16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @rob-heatpump-bobI have the give energy AIO and "gateway" and yes i to had to get a G99 giving me 9.64kw export.
We submitted our papers for SEG, so hopefully we will soon unleash our inverter with export. Keen to see what Solis AI can do with that.
@rob-heatpump-bob I am curious if your DNO accept 9.64kW on a single phase circuit?
16kWh Seplos Fogstar battery; 8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 283 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
No need to create a new thread, @sheriff-fatman. You do...
By Majordennisbloodnok , 2 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Well done to Scottish Power for doing a good job. Well ...
By Majordennisbloodnok , 2 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Fair point. The highest frequency of defrosts I'd seen...
By Sheriff Fatman , 3 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 3 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick interesting update - thanks.I've been thr...
By Tim441 , 4 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I remember reading in some inverters. They mandate a se...
By Batpred , 5 hours ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 6 hours ago
-
RE: Running from backup generaor in powercut?
@majordennisbloodnok Back in the 80’ or 90’ we had a te...
By Toodles , 6 hours ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 7 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 8 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Great to hear! I just figured this out a day or tw...
By anotherdaveuk , 9 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 14 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 1 day ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago