Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow

14 Posts
5 Users
3 Reactions
3,553 Views
(@davidb)
Estimable Member Member
Joined: 10 months ago
Posts: 79
Your energy: 0 kWh
Topic starter   [#2806]

I have a concurrent thread running re improving COP.  This is a spin off question which I hope is more appropriate as a new topic.

i am slowly getting to know my system, installed Sept. last year.  During a call to Vaillant today, the tech support indicated that something odd appears to be happening in that the flow and return DT is mostly <5C.  My hand on the UFH flow and return suggest the flow is as expected but the return is ambient - cold to touch.  The circuit has its own pump, which has a green light so seems to be running.  The pic below shows the flow meters - with which I am unfamiliar.  My first impression was that the flow is actually zero - which would explain the cold return.  Have I interpreted the picture correctly??  Apologies for the poor lighting and hope it is enough.  Both meters have the red disk in the same upper position.  Any advice would be appreciated.

IMG 2269

This topic was modified 10 months ago by Mars

   
Like
1
Quote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5043
Your energy: 57 kWh
 

Yeah, absolutely, those look closed or open very, very little. You can see it says 0 at the top and 5 at the bottom, which are litres per minute. I'd open it to 1 litre per minute to see what happens. 

If you have rads connected to the same heating circuit it might affect them, which is why I suggest opening to 1 litre per minute for now.


This post was modified 10 months ago by Mars

Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
Steelbadger
(@steelbadger)
Trusted Member Member
Joined: 1 year ago
Posts: 31
Your energy: 0 kWh
 

Yes, your interpretation is correct, and those flow meters are indicating a zero or close to zero flow.

Assuming you have a buffer or low-loss header, this would mean that your heat pump will essentially just be circulating water through the buffer and back to itself, with a minimal heat loss (and so a low dT).

If you don't have a buffer or low-loss header, you may instead have a bypass valve, or some other component which is able to act as a kind of short-circuit for the heating fluid (this includes another manifold, or radiators etc).

You may be seeing zero flow here because the flow-regulating valves are closed right off, because the circulation pump feeding the manifold is not pumping (for whatever reason), or because the zone-control thermostats (if you have them) have closed those circuits.

From checking your other post, it seems as if you're running open loop, so there shouldn't be any thermostat-controller actuators on the heating circuits. Then again, you also didn't flag any concerns with your heating not actually working, so I'm a bit suspicious.

Was this photo taken while the heat pump was on, and actively heating?


This post was modified 10 months ago by Steelbadger

   
Like
1
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5043
Your energy: 57 kWh
 

@davidb, turn the red bit (see photo) anti-clockwise. 2-3 finger turns should drop it to around 1l/min.

left

Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote

(@davidb)
Estimable Member Member
Joined: 10 months ago
Posts: 79
Your energy: 0 kWh
Topic starter  

@editor so simple, thanks.  Reevaluating what I was seeing, the valve was only just cracked open. It meant the flow pipe was warm a meter away from the manifold.  I have set both to your suggested 1l/m but curious to know why that figure.  Is that a simple industry rule of thumb?



   
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5043
Your energy: 57 kWh
 

@davidb there isn’t really a universal 'rule of thumb' number for UFH flow rates, which is why I was careful not to present 1 l/min as the answer. In your case it was more of a safe, visible starting point than anything else.

UFH flow rates are ultimately a function of heat output, pipe spacing, loop length and design temperature difference, so in a perfect world you’d calculate them loop by loop. But when you’re troubleshooting a system that’s clearly doing almost nothing, the immediate goal isn’t optimisation, it’s simply to get meaningful circulation and see how the system reacts. Going from effectively zero flow to 1 l/min is a big enough step that you’ll feel it quickly in pipe temperatures and see it reflected in system behaviour, without suddenly dumping a load of flow into the circuit and destabilising everything else.

As you’ve already seen, with the valves barely cracked open the flow pipe warming a short distance from the manifold makes total sense... there just wasn’t enough movement to carry heat back. At 1 l/min you’re now firmly into 'this should actually do something' territory, which gives you useful feedback.

There’s also a practical reason for not jumping straight to higher numbers. If your UFH is on the same primary circuit as radiators, or shares a buffer/LLH, opening the manifold too far can absolutely throw balancing out elsewhere. UFH likes low and slow by nature, so sneaking up on the flow rather than swinging it wide open is usually the least disruptive way to go.

On @steelbadger’s point, he’s right to flag the bigger picture. Near-zero flow at the manifold will lead to low system dT because the heat pump is effectively circulating against itself via whatever path offers the least resistance, whether that’s a buffer, bypass or another open circuit. That doesn’t automatically mean anything exotic is broken, but it does mean the UFH loop wasn’t participating in heat delivery at all.

Given you’re running open loop, no actuators closing things down and the pump appears to be running, the simplest explanation was also the right one here: the flow limiters were basically shut. The key now is to see how the system behaves with some actual circulation... how the UFH responds, whether the return starts to lift and what happens to overall dT and COP once the heat has somewhere useful to go.

I’d live with 1 l/min for a bit, observe, then adjust incrementally. 


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
(@davidb)
Estimable Member Member
Joined: 10 months ago
Posts: 79
Your energy: 0 kWh
Topic starter  

@steelbadger yes, HP running “normally” and, if you have seen some of my other thread, I have no stove burning.  I have the system in active mode - so control via WC curve only.  With only a trickle through the UFH pipes, I am not surprised I haven’t been reaching set temperature.



   
ReplyQuote
(@davidb)
Estimable Member Member
Joined: 10 months ago
Posts: 79
Your energy: 0 kWh
Topic starter  

Update - I have been checking the UFH return manifold, waiting on a rise in temperature.  Response was fairly slow so I figured the heat was being absorbed by the slab.  However I then realised the flow had returned to nearly closed.  Strange, I had it set clearly at just over 1.  I readjusted the flow control only to find it wasn’t operating, regardless of how much I rotate the adjuster.  It looks like I have a hardware failure.  I have no idea what that will take to fix as I am on a Scottish island and my installer on the mainland.  Add to that we have had no ferry service for 2 days due to an easterly gale!  If there are any tricks I can perform to get the flow going, please take to your keyboard.  Thanks to all for their comments.  BW. 



   
ReplyQuote

Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5043
Your energy: 57 kWh
 

@davidb, if the flow has drifted back to near-closed and the adjuster now isn’t doing anything (bearing in mind that I'm not a plumber or heating engineer) that, for me, points to a failed or stuck flow regulator on the manifold rather than anything the heat pump or controls are doing. With UFH, a trickle like that will happily fool you into thinking things are running normally, while in reality the slab is being starved of energy. Under those conditions, not hitting set temperature is exactly what you’d expect.

I think that the slow return temperature rise you saw also fits. Some absorption into the slab is normal on start-up, but if the flow control is intermittently or permanently closed, you’ll never get sustained heat transfer... you’re effectively trying to heat a concrete mass with a dribble of water.

Before you resign yourself to waiting for ferries and installers, there are a couple of low-tech things worth trying. Gently tapping the flow meter body and valve stem can sometimes free a stuck regulator.

Fully winding the adjuster open and closed a few times can also help if it’s jammed with debris or scale. That solved a similar issue for us a couple of years ago.


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
(@davidb)
Estimable Member Member
Joined: 10 months ago
Posts: 79
Your energy: 0 kWh
Topic starter  

@editor thanks for the tips which I will try before calling my installer on Monday. Again much appreciated.



   
Like
1
ReplyQuote
(@davidb)
Estimable Member Member
Joined: 10 months ago
Posts: 79
Your energy: 0 kWh
Topic starter  

Hi everyone,  As I get to know my 3.5kW Aerotherm instal I have had a number of calls with Vaillant tech support.  A recent call turned up info that the flow and return DT was about 2C.  On the back of that I discovered the manifold valves for the UFH were not opening.  I now have a temporary fix on that (thanks Mars) and called Tech support to check if, with the UFH pipes connected, the DT had changed.  Apparently DT is just under 2.  However the tech individual said the flow rate is sitting at 859l/hr - apparently pretty much the maximum.  I have called my installer and hope to get a call back soon but recognise we are in the middle of the heat season so I am not holding my breath.

Can anyone suggest what may be going astray, the impact on system performance at such rates and any suggestion as to anything I can do about it?  

I joined this community a week ago - thanks to everyone for their comments.  My understanding is going up a steep learning curve and I am finding out things which are almost certainly having a negative impact on system efficiency.  This is a great community and really appreciate the assistance.  David 



   
ReplyQuote
(@bornagain)
Active Member Member
Joined: 2 years ago
Posts: 12
Your energy: 0 kWh
 

We have a 5kw Aerotherm feeding an existing UFH manifold plus one radiator.

Our flow rate is also 860 lph and the system is performing beautifully with no cycling during the seven hours a day that it runs.

As an aside, with this flow rate, the heat output in kw is the same number as the dT, so a dT of 2c happens to be 2kw.