Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@bornagain Thanks for the comments and comparison with your own system. My understanding is that the flow rate should automatically adjust to provide a DT of 5. Like you, my system is running ok and perfectly warm. The reaction I got from the technical advisor suggested all is not well with my system. I have no comparisons (other than yours) on which to draw a conclusion. At least, pumping faster than required will consume more power and presumably reduce the COP.
Posted by: @davidbleast, pumping faster than required will consume more power and presumably reduce the COP.
Posted by: @davidbAs I get to know my 3.5kW Aerotherm instal I have had a number of calls with Vaillant tech support. A recent call turned up info that the flow and return DT was about 2C.
It will consume more power in the water pump but it is more likely to increase COP than decrease it, because it means that you need a slightly lower flow temperature for any given emitter output. Thus there is a tradeoff. The folks on openergymonitor reckoned that the optimum for the 3.5kW scenario they modelled was about 2C DT as it happens, but the effect is small as long as you dont go too far above DT5. DT5 is not sacrosanct, its just a design assumption used to size things at design time, actual operation will always differ! Significantly higher DT is certainly bad news, lower DT (provided you are getting sufficient output) not. Max flow rate is also not a problem unless there is excessive noise.
With radiators (which I dont think you have), there is an argument for not modulating the pump speed as the resulting output curve combined with the non linear response of the radiators to DT (rad to room) more closely follows the 'ideal'.
Even though I have a Vaillant I have been unable to determine for certain whether it does bother modulating the water pump or not.
In summary unless any of this is actually causing a problem I wouldn't worry about it! The Vaillant heat pump is pretty good at sorting itself out so long as there is sufficient flow rate.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 611 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 2 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 16 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago