Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@bornagain Thanks for the comments and comparison with your own system. Â My understanding is that the flow rate should automatically adjust to provide a DT of 5. Â Like you, my system is running ok and perfectly warm. Â The reaction I got from the technical advisor suggested all is not well with my system. Â I have no comparisons (other than yours) on which to draw a conclusion. Â At least, pumping faster than required will consume more power and presumably reduce the COP.
Posted by: @davidbleast, pumping faster than required will consume more power and presumably reduce the COP.
Posted by: @davidbAs I get to know my 3.5kW Aerotherm instal I have had a number of calls with Vaillant tech support. Â A recent call turned up info that the flow and return DT was about 2C.
It will consume more power in the water pump but it is more likely to increase COP than decrease it, because it means that you need a slightly lower flow temperature for any given emitter output. Thus there is a tradeoff. The folks on openergymonitor reckoned that the optimum for the 3.5kW scenario they modelled was about 2C DT as it happens, but the effect is small as long as you dont go too far above DT5.  DT5 is not sacrosanct, its just a design assumption used to size things at design time, actual operation will always differ! Significantly higher DT is certainly bad news, lower DT (provided you are getting sufficient output) not. Max flow rate is also not a problem unless there is excessive noise.
With radiators (which I dont think you have), there is an argument for not modulating the pump speed as the resulting output curve combined with the non linear response of the radiators to DT (rad to room) more closely follows the 'ideal'.
Even though I have a Vaillant I have been unable to determine for certain whether it does bother modulating the water pump or not.Â
In summary unless any of this is actually causing a problem I wouldn't worry about it! The Vaillant heat pump is pretty good at sorting itself out so long as there is sufficient flow rate.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 1,360 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
@cathoderay I started to record oil usage per month on ...
By ian33a , 2 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 5 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 10 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago