Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@bornagain Thanks for the comments and comparison with your own system. Â My understanding is that the flow rate should automatically adjust to provide a DT of 5. Â Like you, my system is running ok and perfectly warm. Â The reaction I got from the technical advisor suggested all is not well with my system. Â I have no comparisons (other than yours) on which to draw a conclusion. Â At least, pumping faster than required will consume more power and presumably reduce the COP.
Posted by: @davidbleast, pumping faster than required will consume more power and presumably reduce the COP.
Posted by: @davidbAs I get to know my 3.5kW Aerotherm instal I have had a number of calls with Vaillant tech support. Â A recent call turned up info that the flow and return DT was about 2C.
It will consume more power in the water pump but it is more likely to increase COP than decrease it, because it means that you need a slightly lower flow temperature for any given emitter output. Thus there is a tradeoff. The folks on openergymonitor reckoned that the optimum for the 3.5kW scenario they modelled was about 2C DT as it happens, but the effect is small as long as you dont go too far above DT5.  DT5 is not sacrosanct, its just a design assumption used to size things at design time, actual operation will always differ! Significantly higher DT is certainly bad news, lower DT (provided you are getting sufficient output) not. Max flow rate is also not a problem unless there is excessive noise.
With radiators (which I dont think you have), there is an argument for not modulating the pump speed as the resulting output curve combined with the non linear response of the radiators to DT (rad to room) more closely follows the 'ideal'.
Even though I have a Vaillant I have been unable to determine for certain whether it does bother modulating the water pump or not.Â
In summary unless any of this is actually causing a problem I wouldn't worry about it! The Vaillant heat pump is pretty good at sorting itself out so long as there is sufficient flow rate.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,738 Topics
- 64.3 K Posts
- 1,348 Online
- 7,143 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
As I recall, 3kW is the maximum available from the main...
By Transparent , 17 minutes ago
-
RE: Electricity price predictions
Nationally-based Demand Flexibility makes little sense....
By Transparent , 1 hour ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Oh dear. Glad it was replaced. I have been mighty imp...
By JamesPa , 8 hours ago
-
RE: Can I start an argument about buffer tanks please? 🙂
Dont, just adjust the LSVs to get different temperature...
By JamesPa , 18 hours ago
-
RE: Heat pump running costs – what has actually worked for you?
I installed the air source heat pump in January 2026, i...
By bobflux , 21 hours ago
-
RE: Grant Aerona Air to Water R290 6.5 kW - Quiet Mark and Silent Running
Thats all interesting. DHW on my Vailant seems to respe...
By JamesPa , 1 day ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
One of the other mods has just reminded me that @ashp-b...
By Majordennisbloodnok , 1 day ago
-
RE: PV and battery long payback - sense check query
@old_scientist I have now drafted 2 replies - both have...
By DavidB , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: adrian Manufacturer: Appliandirect.co....
By Adrian , 3 days ago
-
RE: Acond heat pump failed after four years - diagnostic quote £940 plus VAT
@downfield Thank you Downfield. This sounds potenti...
By Mia , 4 days ago
-
RE: Digest of UK Energy Statistics
@jeff Yes my brother in Oz told me of that charge year...
By Jancold , 4 days ago