Advice on potential HW Cylinder size
Firstly its not the coil volume that is normally the issue it's the area, the typical 'requirement' being 3sq m. In principle system volume of the dhw loop could be an issue during defrost, but because the dhw coil is immersed in warm water in practice not and neither is it something UK installers bother about (and we get lots of defrosts).
So I'm not really clear what your installer is worried about. If he is only worried about system volume then a volumiser will fix it, but it's almost certainly unnecessary. If he is worried about coil area then why is he talking about volume?
The truth is it will very probably work as is if you are happy to heat it at ft70, but whether you can persuade your installer that is another matter given that he seems to be concerned about the wrong thing!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The installer has simply dismissed the idea as non-standard. The volume issue was practically raised by me but he refuses to leave his comfort zone…. Midea ASHP requires a minimum of 40lt in the circuit and I seriously doubt the existing cylinder circuit+coils have this water volume.
I think once we feel comfortable with our new ASHP , we will tackle the cylinder issue and try a volumizer. And I will sign another disclaimer taking responsibility that it will work (much as I did for not installing a buffer with the ASHP)
Posted by: @mk4The installer has simply dismissed the idea as non-standard. The volume issue was practically raised by me but he refuses to leave his comfort zone…. Midea ASHP requires a minimum of 40lt in the circuit and I seriously doubt the existing cylinder circuit+coils have this water volume.
They wont have that volume, neither will most others, and the installers interpretation of what Midea say is unconventional to say the least (ie I have never heard this interpretation for any heat pump and it makes no logical sense so far as I can see. It does make logical sense to worry about coil area though).
The problem with the volumiser is that it means that you heat 50l (or whatever the size) of water unnecessarily to a high temp each time you heat DHW. This is pure waste and thus undesirable. This is why people dont put a volumiser in the DHW loop.
The possible problems with a small coil are defrost and cycling. You are right that, by increasing the flow temperature to 70C you are heating the tank exactly the same as with a boiler. Its very likely indeed to work particularly if you are only targeting a tank water temp of say 50C. If you are targetting a very high tank water temp then you may get to the point where the heat loss from coil to tank is less than the minimum output of the heat pump, at which point its may cycle. This is of course also true of a boiler, which is one reason I think its unlikely. Of course this could simply be tested and a change made only if its a problem (suck it and see)
Defrost is potentially another story however. When a defrost occurs the heat pump is reliant on sucking heat from the system to melt the water. This is the primary reason for specifying a minimum system volume. If it occurs during a DHW cycle then all of the stored water in the hot water tank itself is effectively engaged, as its thermally connected to the system via the heat exchanger (coil), hence why system volume of the DHW loop isnt generally an issue. Its in principle possible, if you have only a small coil at the bottom of the tank, that defrost cools the bottom of the tank before the water melts, ie effectively only part of the tank is engaged not the whole tank. Is this likely? I would guess not at all, but its in principle possible and its not really practical to do a test. This then is the argument for changing the tank. Of course if it only frosts for a few days a year you could disable dhw heating via the heat pump and use the immersion instead, if there is one.
An alternative to changing the tank is to add a circulator pump plus an external PHE so that the heat exchange occurs in the external PHE instead of (or in addition to) the coil. Some advocate this anyway and there are some DHW tanks that are built this way. Its quite a cost effective route.
In summary, and having thought some more about this, I wouldn't add a volumiser. You options practically are
1. Leave as is, test to check it heats, take a risk on defrost which can be mitigated by engaging the immersion during frosty conditions, albeit thats a bit of a pain.
2. Add a circulator pump plus plate heat exchanger to 'plate load' the cylinder
3. Replace the cylinder
Hope that helps.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I think the comment about heating from cold is quicker than adding to warm is analogous to a battery system or EV - it is far quicker to charge an EV from 10 to 80% than then forcing it from 80 to 100%. The same logically applies to a thermal battery - although it may not to a Sunamp due to the way the phase change material is organised around the heating elements.
The other point I'd make is around solar export. With the export tariff levels dropping, it is expected that self-consumption will become far more important than maximum export. Therefore any means of storing energy, whether that be as electricity or heat, and again for both wet central heating or DHW, is going to save more money than the export unit price.
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 565 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
*** I now see @jamespa has already posted but will stil...
By cathodeRay , 27 minutes ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 35 minutes ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 2 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 6 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 13 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 13 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 16 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 17 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 20 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 23 hours ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago
-
RE: Homely setup on daikin heat pump
@craigh I refer to our somewhat elevated temperature of...
By Toodles , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
My turn, this describes the future installation, only t...
By bobflux , 4 days ago