Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Trying to choose between 2 towel rads - which one should I go for?
trying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamktrying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
both are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
Posted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
im thinking of going for the taller one and letting the heat from the plant room plus the flow/return 28mm and the primary 28mm's that are in the ceiling all do there bit, as ive had a rad in a bathroom before and they tend to rust quickly. also the room is insulated on all sides including the floor and ceiling.
- 27 Forums
- 2,778 Topics
- 65.5 K Posts
- 1,877 Online
- 7,185 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Say hello and introduce yourself
@olivierm welcome to the forums and finding the right i...
By Mars , 12 minutes ago
-
RE: Estimating true heat loss from twelve months of consumption data
Finally, after what seems like an eternity, we paid a d...
By ian33a , 4 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
@paul1098 — as we are getting down to the nitty gritty,...
By cathodeRay , 16 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
I’ve had two calibration cycles in the last three month...
By Davesoa , 21 hours ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@editor That's a pity, but thank you for checking. I'l...
By ltron2 , 1 day ago
-
My fifth heat pump book, Heat Pumps Explained, is out n...
By Mars , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Just furkled Into the parameter menu. Found the master ...
By AgentGeorge , 2 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
It's interesting that Norway with a much colder climate...
By Rob of York , 2 days ago
-
RE: Review your electricity provider
Happy to add Scottish Power and the review 'dont touch ...
By JamesPa , 2 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
Yes, and I would suggest likely to get worse with more ...
By Batpred , 4 days ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 4 days ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 4 days ago
-
RE: Panasonic Free Multi Z and Etherea Internal units.
@dgclimatecontrol Thank you for that information and re...
By Toodles , 4 days ago
-
RE: My Kronoterm Adapt 0312 ASHP is finally installed!
@editor It was serendipitous really. Both my wife and I...
By tomasmcguinness , 4 days ago