Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Trying to choose between 2 towel rads - which one should I go for?
trying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamktrying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
both are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
Posted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
im thinking of going for the taller one and letting the heat from the plant room plus the flow/return 28mm and the primary 28mm's that are in the ceiling all do there bit, as ive had a rad in a bathroom before and they tend to rust quickly. also the room is insulated on all sides including the floor and ceiling.
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 380 Online
- 7,028 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a — a measured heat loss always trumps a calculat...
By cathodeRay , 5 minutes ago
-
RE: Setback savings - fact or fiction?
@cathoderay Thanks for your detailed response.Just two ...
By PeterWurmsdobler , 13 minutes ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
The hot water heating looks normal. The heat transfer ...
By GrahamF , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 4 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 13 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 15 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 20 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 22 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 1 day ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 1 day ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 1 day ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 2 days ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 2 days ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 2 days ago