Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Trying to choose between 2 towel rads - which one should I go for?
trying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamktrying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
both are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
Posted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
im thinking of going for the taller one and letting the heat from the plant room plus the flow/return 28mm and the primary 28mm's that are in the ceiling all do there bit, as ive had a rad in a bathroom before and they tend to rust quickly. also the room is insulated on all sides including the floor and ceiling.
- 27 Forums
- 2,814 Topics
- 66.6 K Posts
- 4,953 Online
- 7,223 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Should Households Who Can Afford It Pay More for Energy to Help Those Who Can't?
@batpred I mentioned earlier that targeting the payment...
By Toodles , 28 minutes ago
-
RE: DIY powerflushing tutorial
You could perhaps start by putting a sample in a small ...
By cathodeRay , 40 minutes ago
-
Buffer tank on a 2 x 14kw Ecodan system
We have a setup where there are 2 x 14kW Ecodan units (...
By fosterl2 , 2 hours ago
-
RE: Why don't people choose heat pumps?
@rob-of-york The Panasonic units also have a microscopi...
By Toodles , 2 hours ago
-
RE: Adventures in heat loss calculations
@toodles thanks! So as suspected, around a doubling of ...
By SusannaSaunders , 3 hours ago
-
Six books in three years and I think I’ve now covered j...
By Mars , 3 hours ago
-
RE: Grant Aerona3 13kw - Buffer Tank - Heating Journey
@heymikey Well done in achieving as nearer a match acro...
By Toodles , 10 hours ago
-
Grant Aerona - Weather Compensation and Schedules
Im trying to set up a friends Grant Aerona. The WC curv...
By bontwoody , 1 day ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
@jamespa I agree, the efficiency of Cosy Cooler ought...
By Rob of York , 1 day ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
I think you're right! 🤨
By Transparent , 2 days ago
-
RE: Renewables & Heat Pumps in the News
ECO4 muddies the water somewhat, and then some. I thi...
By cathodeRay , 2 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
If there is a drain nearby that's exactly what I would ...
By JamesPa , 2 days ago
-
I think that CCGT plant in Lingen is more likely to suc...
By Transparent , 3 days ago
-
RE: Heat Geek installations: share your experiences
@l8again fwiw my experience (Valiant but not with heat ...
By JamesPa , 3 days ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
@etchedpixels thank you for the advice paid cash all...
By Chilli304 , 4 days ago