Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
help sizing rads based on room by room heat loss
scratching my head a bit as to what size rad i need for a given room based on its heat loss. the system is designed to 40c flow @-3.1c outside. lots of sites list rad outputs based on delta t50, is this the flow temp? so if i can find out the output at dt40 for instance is that the output i need to match to this chart?
With a flow of 40C the dT for a 20C room temp is 20 it’s the difference in temp between flow and room. The output of a rad at dT 20 is 0.3 of its output at dT50
so why dont sites list the output based on flow temp? cause most seem to use dt.
Posted by: @adamkso why dont sites list the output based on flow temp? cause most seem to use dt.
Because they don't know your room temperature and it's only (average) DT that matters
Posted by: @adamkso does that mean at a dt of 50 the actual flow is 70c for a 20c room temp?
Not strictly I think. It's 20 plus half the DT between flow and return so that the average dt rad to room is 50
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @garyYep exactly that
jees ive got 2 hopes of heating my bathroom then. someone suggested an standard design aluminium rad, instead of a towel rad, but im worried in a copper and steel setup ill get galvanic corrosion.
I just left the old towel rail which is now way underpowered. I am relying on heat transfer from the adjacent hallway, which has excess capacity, together with steam when you run a bath/shower. It works just fine - the level of thermal separation between rooms is quite modest in practice.
Obviously this is house dependent but more than one prospective installer remarked to me that they frequently do not install a 'fully compliant' radiator in a bathroom (because of the low output of and desire for towel rails).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
can i ask then if i have a heat loss for a room of 1079w and a flow of 40c@-3.1c what wattage rad do i need to hit? cause at the moment im struggling to find one big enough that would fit in the space.
The output of a rad is proportional to DT to the power 1.3, where DT is the average temperature difference between rad and room.
At a flow temperature of 40, and assuming a room temperature of 20 and a temp drop across the radiator of 5, DT is 37.5-20=17.5
Radiators are usually specified for a DT of 50. So you will need a rad with an output at DT 50 of (50/17.5) to the power 1.3 x 1079W = 3.9x1079W=4.2kW.
That's a mighty big radiator. What room is this in? Consider more than one radiator or a fan radiator if the loss really is that high.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Posted by: @adamk@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Have you got the loss calculations, if so perhaps you could post?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,690 Topics
- 63.1 K Posts
- 1,219 Online
- 7,099 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How do I set up Tesla Powerwall export for saving sessions since AI Takeover?
@toodles You might have gotten away with a 50L hot wate...
By Papahuhu , 16 minutes ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Yesterday i had a single overvoltage event. But that mu...
By Tim441 , 5 hours ago
-
RE: Design Of Cascade System Replacing Undersized ASHP
I don't know the full details of your house or installa...
By Temperature_Gradient , 5 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
Some pics of my heat solutions… Bought the shut...
By Watcher , 5 hours ago
-
RE: Moving growatt axe batteries
@etchedpixels just been informed that you can’t have ba...
By David999 , 18 hours ago
-
RE: Anyone have experience with Daikin Multi+ for air to air & hot water?
Maybe, just maybe, if you are prepared to leave the doo...
By JamesPa , 18 hours ago
-
RE: How to heat a bathroom when using an air to air heat pump?
You can air/air a bathroom with a suitable ceiling or o...
By EtchedPixels , 18 hours ago
-
RE: Plug and play solar. Thoughts?
They've been extensively tested by folks like the Germa...
By EtchedPixels , 18 hours ago
-
RE: Electricity price predictions
@majordennisbloodnok Similar, although no heat pump h...
By IanMK13 , 1 day ago
-
RE: vaillant arotherm plus - Failure - DHW
As expected it failed to run late yesterday with the sa...
By trebor12345 , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
Personally, I don't always rate the "payback on install...
By HeatNoob , 2 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thanks. Will be sure to keep a record of s...
By bontwoody , 2 days ago
-
@jamespa Well, something along the lines of "three buse...
By ian33a , 2 days ago