Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
help sizing rads based on room by room heat loss
scratching my head a bit as to what size rad i need for a given room based on its heat loss. the system is designed to 40c flow @-3.1c outside. lots of sites list rad outputs based on delta t50, is this the flow temp? so if i can find out the output at dt40 for instance is that the output i need to match to this chart?
With a flow of 40C the dT for a 20C room temp is 20 it’s the difference in temp between flow and room. The output of a rad at dT 20 is 0.3 of its output at dT50
so why dont sites list the output based on flow temp? cause most seem to use dt.
Posted by: @adamkso why dont sites list the output based on flow temp? cause most seem to use dt.
Because they don't know your room temperature and it's only (average) DT that matters
Posted by: @adamkso does that mean at a dt of 50 the actual flow is 70c for a 20c room temp?
Not strictly I think. It's 20 plus half the DT between flow and return so that the average dt rad to room is 50
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @garyYep exactly that
jees ive got 2 hopes of heating my bathroom then. someone suggested an standard design aluminium rad, instead of a towel rad, but im worried in a copper and steel setup ill get galvanic corrosion.
I just left the old towel rail which is now way underpowered. I am relying on heat transfer from the adjacent hallway, which has excess capacity, together with steam when you run a bath/shower. It works just fine - the level of thermal separation between rooms is quite modest in practice.
Obviously this is house dependent but more than one prospective installer remarked to me that they frequently do not install a 'fully compliant' radiator in a bathroom (because of the low output of and desire for towel rails).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
can i ask then if i have a heat loss for a room of 1079w and a flow of 40c@-3.1c what wattage rad do i need to hit? cause at the moment im struggling to find one big enough that would fit in the space.
The output of a rad is proportional to DT to the power 1.3, where DT is the average temperature difference between rad and room.
At a flow temperature of 40, and assuming a room temperature of 20 and a temp drop across the radiator of 5, DT is 37.5-20=17.5
Radiators are usually specified for a DT of 50. So you will need a rad with an output at DT 50 of (50/17.5) to the power 1.3 x 1079W = 3.9x1079W=4.2kW.
That's a mighty big radiator. What room is this in? Consider more than one radiator or a fan radiator if the loss really is that high.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Posted by: @adamk@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Have you got the loss calculations, if so perhaps you could post?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 1,601 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
@cathoderay I started to record oil usage per month on ...
By ian33a , 31 minutes ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 4 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 9 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago