Mixture of copper and plastic CH pipework. Will it be ok, or need changing?
We are getting closer to our heat pump install and I have been reading (and reading!) in the hope I can catch any potential pitfalls before the installation begins.
One slightly concerning area is the existing central heating pipework.
We had an extension fitted to our 1950's semi 20 yrs ago. The boiler was fitted in our new utility room connecting to the old radiator circuit somewhere in the middle of the house where the old back boiler was housed.
I can see that our primary 22mm copper CH pipework tees off into what looks like 22mm plastic pipe using a right angled push fit connector in the ceiling above the boiler (there is a small void left by the gas fitter in the new boiler cupboard). It also appears we only have one central heating circuit for the whole house, certainly from the boiler and I'm assuming connected to the old CH circuit.
From the plentiful reading I have done, this copper to plastic connection and pipe run will have a limiting impact on the flow rate.
I'm hoping it will probably be ok, although not perfect and that I can still get decent efficiency from the HP and possibly still run at DT5.
We are due to be installed a Daikin EDLA08EV3. Heat loss calculation (which we feel is pretty accurate) was 6.2KW. Radiators are all 15mm copper connections and are all being replaced. Design 42.5c @ -2
What are your thoughts?
Thanks.
According to the Heat Geek cheat pipe sizing sheet (which seems to have disappeared form the heat geek site but is reproduced here 22mm copper is good for 6kW @DT5. That means that 22mm plastic, and its a single pipe (you describe it as teeing off via a right angle connector which I dont exactly understand), then is a bit marginal, but the HC calcs are based on 0.9m/s and many would say you can go a bit faster. Of course the run before it splits to the first rads is fairly short, its also less likely to be a problem, and if you have to run at DT6 the performance penalty is only 1.5% or thereabouts.
If it were my house I would very definitely 'suck it and see'. Very likely it will work at DT5, if not a tweak will almost certainly get it to work. It might be worth replacing that plastic elbow (if that is what it is) with a swept bend or copper elbow though whilst its drained down.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaAccording to the Heat Geek cheat pipe sizing sheet (which seems to have disappeared form the heat geek site but is reproduced here 22mm copper is good for 6kW @DT5. That means that 22mm plastic, and its a single pipe (you describe it as teeing off via a right angle connector which I dont exactly understand), then is a bit marginal, but the HC calcs are based on 0.9m/s and many would say you can go a bit faster. Of course the run before it splits to the first rads is fairly short, its also less likely to be a problem, and if you have to run at DT6 the performance penalty is only 1.5% or thereabouts.
If it were my house I would very definitely 'suck it and see'. Very likely it will work at DT5, if not a tweak will almost certainly get it to work. It might be worth replacing that plastic elbow (if that is what it is) with a swept bend or copper elbow though whilst its drained down.
Yes, an elbow is what I should have said.
The 22mm copper pipe from the boiler curves slightly into the ceiling and then the push fit elbow connects to the horizontal run of plastic pipe under the 1st floor floorboards.
The copper pipe is about 1.5m into the ceiling which is directly below the first radiator, so I'd expect the first tee from the plastic pipe to be no more than 2m.
The HP will be fitted on the same wall as the boiler and the run of 28mm primaries will be around 2m, so about 4m or so to the ceiling where the 22mm copper and plastic pipes are joined.
If I need to run at dt6, would that only be required in the colder months?
Posted by: @bashIf I need to run at dt6, would that only be required in the colder months?
In principle yes. Some heat pumps (I think including Daikin) appear to modulate the water pump to achieve a quasi fixed DT. So if you set it at 6 for the cold months it may stay at 6 even in the warmer months. There are probably some installer settings to control the water pump behaviour which you may well be able to tweak if it comes to that.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 255 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Interesting. I don't have that problem, although the f...
By AndrewJ , 18 minutes ago
-
A while back I had a Y strainer fitted on the external ...
By jeegnesh , 32 minutes ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
So to clarify (and rephrase the problem into my own ter...
By Majordennisbloodnok , 2 hours ago
-
RE: Free Ecoheat Heat Pump Install
This is an interesting way of looking at it, and I can ...
By Mars , 2 hours ago
-
RE: Configuring third party dongle for Ecodan local control
That's a good spot and a valuable insight, @sheriff-fat...
By Majordennisbloodnok , 2 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@majordennisbloodnok And did ‘Honey’ order it for you? ...
By Toodles , 3 hours ago
-
RE: Setback savings - fact or fiction?
@robs — thanks again for your detailed comments. Some r...
By cathodeRay , 16 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 20 hours ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 21 hours ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 22 hours ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 22 hours ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 1 day ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 1 day ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 1 day ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 2 days ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 2 days ago
-
@majordennisbloodnok I have decided to take the plunge....
By TechnoGeek , 2 days ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 3 days ago