Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Bathroom Radiator replacement

5 Posts
3 Users
0 Reactions
2,553 Views
(@alfapat)
Estimable Member Member
Joined: 4 years ago
Posts: 187
Your energy: 0 kWh
Topic starter   [#2265]

I need to replace a 600 x 1200 double panel radiator as it leeks a little with a vertical towel and heat radiator . How do I compare an old radiator to this , is it by the amount of BTU'S they emit ?



   
Quote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5719
Your energy: 22 kWh
 

Posted by: @alfapat
↑

I need to replace a 600 x 1200 double panel radiator as it leeks a little with a vertical towel and heat radiator . How do I compare an old radiator to this , is it by the amount of BTU'S they emit ?

Thats the main consideration.   You need to calculate btu or kW at your design flow temperature and compare with the room heat loss.  Towel rails emit very little heat so you are unlikely to match the output of a panel radiator.

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@alfapat)
Estimable Member Member
Joined: 4 years ago
Posts: 187
Your energy: 0 kWh
Topic starter  

OK , Thanks James, can the btu's be calculated from the existing Radiator as it was measured to size for that room initially.

By the way I have a plumber / heat engineer the create a volumizer out of buffer and remove excess pumps and sort the pipework , at last!



   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5719
Your energy: 22 kWh
 

Posted by: @alfapat
↑

OK , Thanks James, can the btu's be calculated from the existing Radiator as it was measured to size for that room initially.

By the way I have a plumber / heat engineer the create a volumizer out of buffer and remove excess pumps and sort the pipework , at last!

Yes.  Just find any radiator catalogue eg myson or stelrad and look it up.  This will give you W at a DT of 50C between flow temp and room.  To convert to W at whatever your design ft is, use output proportional to DT raised to the power 1.3. 

Alternatively you can just look for another rad with the same output at DT50, but you are unlikely to find a towel rail that does this.

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5028
Your energy: 27 kWh
 

@rob-nezard can you please offer your professional advice on this subject?


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow