Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Antifreeze top up for my heat pump - is this a rip off?
The company that installed my ASHP went bust and was clearly a bit dodgy! I was left no information about the antifreeze used originally.
The ASHP had been working fine for a couple of years. Had it serviced by a company yesterday. The guy, who seemed genuine, said the antifreeze was low so needed topping up, but unless he knew what type it was he would have to drain the whole system, because there might be a chemical reaction. He said we would send a quote.
Does this sound right or am I potentially being ripped off?
Welcome to the forums Sally. To answer your query, it’s important to know that there are two different types of system additives that might be in your heat pump circuit and we need to know which one he’s talking about:
- Inhibitor: this is a corrosion inhibitor used to protect the metal components inside your system (pipes, rads, heat exchangers, etc.). It doesn’t provide any protection against freezing… it’s purely there to reduce the risk of rust, scale and sludge build-up.
- Glycol (antifreeze): this is used to lower the freezing point of the water in your system if any pipework is outside or in unheated spaces. Most glycols also contain inhibitor as part of the mix, so you often get both in one product.
There are two main types of glycol:
- Ethylene glycol: slightly more efficient thermally, but toxic, so more commonly used in sealed systems.
- Propylene glycol: less efficient but non-toxic, and often preferred for domestic settings.
Now, on to testing and answering your question.
If your engineer said the antifreeze level was low, the correct way to confirm that would have been with a refractometer which is a small handheld tool that reads the glycol concentration by placing a drop of fluid on the lens and checking the reading. It tells you roughly what the freeze protection level is (e.g., down to -10C or -20C). It’s a quick and reliable way to check whether you actually have glycol in the system and if it needs topping up.
Did you see him use one? If not, it’s worth asking what he based his assessment on. To my knowledge this is the only way to verify glycol concentration. If you didn’t observe him doing this, he didn’t check for it.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Thank you for your detailed response.
So if I don’t know what type it is, is it necessary to drain the system before topping up?
Posted by: @editorEthylene glycol: slightly more efficient thermally, but toxic, so more commonly used in sealed systems.
Sorry that isn't correct, it may be used in vehicles, but has zero place in a domestic heating system. An issue with a cylinder heating coil you can end poisoning the house in a worst case.
Bigger question is do you need antifreeze? My answer is no. You don't even need antifreeze valves.
I really wouldn't worry to much.
I changed to VDI 2035, which is very clean water, no additional additives. No anti freeze valves or antifreeze in water. We get -9 outside temperature in winter. No issues to date.
Posted by: @sallylbut unless he knew what type it was he would have to drain the whole system, because there might be a chemical reaction.
Pretty unlikely. Just top up you wish with heating system antifreeze from Screwfix. To test drain a little (half cup) from heating system into a cup, add same amount of Screwfix antifreeze mix and leave overnight. If its looking the same it's ok, if it's changed colour, gone thick or any other change maybe not compatible.
Posted by: @AnonymousSorry that isn't correct, it may be used in vehicles, but has zero place in a domestic heating system. An issue with a cylinder heating coil you can end poisoning the house in a worst case.
It may have no place in domestic heating, but it has been used.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
This is what is used in nearly all ASHP system that have glycol.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
If they have used the wrong antifreeze you would want it taken out, if they used one of the 3 most popular monopropylene glycol's they can likely be mixed but there is no way to test which one you have without lab analyses and all of the manufacturers state do not mix them as this is a cover all for mixing chemicals and how the responsibility carries.
Its simply not worth the risk as the chem reaction could be caused over months and may do long term damage to your system.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@editor @sallyl As Mars said, there are 2 different types of glycol generally used in the heating system. They are different and should not be mixed. Without knowing exactly what is in the system, it is good practice to remove, flush and re-fill. I personally do not use glycol as there can be a significant reduction in performance with it incorporated within the system. I generally use water with inhibitor and, if the manufacturer insists, an antifreeze valve installed.
@johnmo
This is not really an adequate response. Maybe you don't have any issues, but this presumably means the heating system is on most of the time? There's no one size fits all to this dilemma.
Posted by: @ecodan-efficiency@johnmo
This is not really an adequate response. Maybe you don't have any issues, but this presumably means the heating system is on most of the time? There's no one size fits all to this dilemma.
If you don't like my response you are free to ignore it.
So for your education. Read the article on here about heat pump and freezing time and take issue with that. Also read response from @brendon uys above, he also does like to use antifreeze, only adding antifreeze valves if manufacturer insists. Plus how many external oil boilers have anti freeze or anti freeze valves - none.
Which bit isn't adequate, that Ethylene glycol has zero place in a domestic heating system. It is poisonous! So why would any sane person install it.
Or use of VDI 2035, this is what you get with a heat geek install and almost every install in Germany which is way colder than here.
Or do you not like suggesting to do a reaction test?
If you going to say my response isn't adequate, at least be polite enough, to clarify what you have issue with.
Posted by: @ecodan-efficiencybut this presumably means the heating system is on most of the time?
I can either do full weather compensation or batch charging the floor. So heat pump may or may not be on. But circulation pump runs 24/7 to distribute heat and solar gains.
@johnmo
I never mentioned Ethylene glycol and I'm not suggesting using it.
As I've already said, not everybody operates their system in the same way as you. There are long periods where my circulation pump does not run, for example. I suspect you'll now tell me that's wrong without trying to understand the situation.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 284 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 4 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 4 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 4 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 5 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 6 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 7 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 8 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 9 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 11 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 14 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 17 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago