Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New GSHP idea / concept
Hello from (Eastern) Canada,
I'm no HVAC professional, but have been very interested in GSHP systems since the early 2000's.
A concept my mind has been playing with (mainly to reduce installation expenses, and maybe increase efficiency is to use underground liquid tanks instead of ground or water loops.
My specific idea is (for a 3 Ton pump) to have two ±20,000 liter underground tanks, at a good distance from each other. Instead of using one source for all temperatures, have one designated hot liquid tank, and one cold / ice tank.
To further mitigate the risk of everything freezing up, I'm thinking to connect a set of evacuated solar tubes to heat the hot liquid, and connect the hot and cold tank with mixing valves so temp can be kept at ideal temperature.
The benefit of this would be that you can freeze the cold tank at the end of winter, and use this energy for cooling in early spring, while hot tanks should be warm enough by then to provide a bit of heat if needed. In the fall the reversed process will be used. I figure you may be able to completely turn the heat pump off for a month or so in the spring and fall ...
As said I am no pro, but this idea is stuck in my mind for over a year now ... Am I onto something, or are some of my ideas not realistic? I'm looking forward to your professional opinions, for which big thanks in advance!
Hi, @ronv, and welcome to the forum. Good to have a new International member as well.
I'm certainly no professional but at a first glance I think you may have an issue with scale. In effect, by using an underwater tank, you are designing a water source heat pump rather than a ground source one, and in the UK the recommendation for a water source for a typical domestic installation is a body of water that's at least 1.5 - 2 metres deep and 0.5 to 1 acre in size to ensure the heat pump doesn't start freezing up the pond/lake. Doing the maths, that means a realistic minimum of 3 million litres so even if the minimum recommendation is wildly cautious a 20,000 litre tank is still orders of magnitude too small.
I'd also be interested to know what kind of costs would be involved to excavate a hole large enough to accommodate a 20,000 litre tank compared with the costs to sink a vertical coil for a typical ground source heat pump. In the UK, garden space is at a real premium and access is often restricted so I suspect the costs here would be far higher than in many sites in Canada, so perhaps what would be financially unlikely here might be perfectly feasible for you.
As I said, I'm purely an interested layman and so I could well be wrong. However, it's hard for me to look past the disparity in liquid volumes.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @ronvMy specific idea is (for a 3 Ton pump) to have two ±20,000 liter underground tanks, at a good distance from each other. Instead of using one source for all temperatures, have one designated hot liquid tank, and one cold / ice tank.
Worth a back of an envelope calculation.
The specific heat capacity of water is 4.2 kJ/kgK.
So if I heat at 20000 l tank by say 20C it takes 4.2*20000*20 kJ=1.7 GJ. 1 kWh is 3.6MJ so 1.7GJ is about 500kWh.
The typical UK house consumes 11MWh of gas annually, almost all for space heating.
So (unless I made a decimal point error) a 20000 l tank is nothing like big enough without drawing in heat from the surrounding soil.
That said regenerative heating/cooling does exist as a concept, using the ground as a big store. Cool it in winter, heat it in summer, both made more efficient by the previous seasons escapades.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
20,000 litres of glycol laced water will have the environment agency on your back pretty damned fast.
There are systems that do this in production today. It's used for greenhouses where many of them otherwise swing wildly between overheating and freezing cold over a 24 hour cycle.
Posted by: @etchedpixels20,000 litres of glycol laced water will have the environment agency on your back pretty damned fast.
...
Although regulations may well vary from country to country. Canada's equivalent to the Environment Agency may be more lax than the UK or, indeed, stricter.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Tanks / blatters are to be buried in the ground, they're about $5k each. I know how to play with excavator, so it will cost me a weekends rent at about $2k. Boreholes for wells are pretty expensive at $20 - $30k each (seems to be the going rate here) and you don't get the advantage of storing the heat and cold energy underground, which is kind of the idea behind the use of the two separate designated storage/water tanks.
I figured by adding the evacuated solar tubes, and mixing valves, there should be enough heat energy to prevent the water in the cold tank from freezing, and keep it in an optimal efficiency temperature range. (heat from solar tubes, flow rates, needed tank size etc. to be calculated by someone with much more specific knowledge of applicable formulas) I figure that if my tank needs an x amount of energy additional to the ground exchange, it's just a matter of finding the balance between tank size, and amount of solar tubes.
I thought about that too, and between the cost of the glycol, and potential regulatory problems, I'm actually thinking of having pure water in the tanks, and run an x amount of glycol filled coils in the tank. This will also make it easier to freeze the cold tank into a solid clump of ice at the end of the winter, so this cold energy can be used for airco in spring and early summer. At the end of the summer you dump excess heat into the cold tank, so it takes a long time when the system starts using it for heating before it gets to freezing point.
So there would be one glycol loop through cold tank, one glycol loop through hot tank, and one glycol loop from evacuated solar tubes..... Thinking that loop should heat a hot water storage tank (domestic water & floor heating), and then loop through to the hot tank. When the system is in heating mode all stored hot energy can be used (with mixing pump / valves) to keep the water in the cold tank at optimal temp during winter use. From what I read evacuated solar tubes still produce a large amount of heat, even on the coldest winter days.
If you freeze water it expands. That's been a big problem people have hit trying to do this on a smaller scale freezing 1m cubes of ice in their basement (which is a colossal amount of energy). The other one being getting it back out at a sensible rate.
It's a great concept and ice melting takes insane amounts of energy per cubic metre.
To use ice as a storage medium, consider the latent heat of fusion (334 kJ/kg) which is about the same as 80°C worth of thermal capacity.
A "3 ton" AC (cooling capacity 10kW) has daily energy transfer equivalent to freezing 3 tons of ice, so in 2 months it cools by an equivalent of melting 180 tons of ice. So you need a lot of ice. It would be doable if you own a floodable cavern or something of the sort.
It is possible to store cold in the winter and heat in the summer, but this requires an enormous mass, which must be free, so it's usually earth with pipes running through it. In other words geothermal.
I recommend comparing the return on investment of any project against: photovoltaics + standard AC for cooling, and insulation for heating.
Thank you for your response. I am trying to get away from the large area needed for ground loops, putting them in a vessel instead which will extract or dump energy into soil around it. The heat generated in the summer will "preheat" the cold tank surroundings, so it should be quite a while until all that heat has been extracted, and the water gets to the freezing point. The other "help" are the evacuated solar tubes which provide "free heat" even in winter to stop the tank from freezing. (idea is a water to water floor heating system, where heat generated by solar tubes get first used for heating, and when this not sufficient have the heat pump kick in. According to AI:
One rack of ten standard (58mm x 1800mm) evacuated solar tubes in Eastern Canada will generate approximately 400 to 550 kWh (1.36 to 1.88 million BTUs) of usable heat energy per year. See below message for more info.
Keeping this in mind, and let's say both the hot and cold tanks (and surrounding soils) are heated to 30* C. Do you still think that if the heat pump gets to work around the middle of December, the tanks will all be frozen solid by the end of March? If so, hypothetically, how many racks of tubes would I need to install to balance the demand?
- The Collection Area: A single 58mm x 1800mm evacuated tube has an actual aperture (sunlight collection) area of roughly 0.06 to 0.08 m² per tube. Therefore, a 10-tube rack provides a tight collection area of about 0.6 to 0.8 m². [1]
- Efficiency Factor: Evacuated tube systems operate with an annual thermal efficiency of roughly 50% to 65%. They are uniquely insulated by a vacuum layer, meaning they lose very little heat back to the environment, even during freezing Canadian winters. [1, 2]
\(\text{Annual\ Heat\ Output}\approx 1,300\text{\ kWh/m²}\times 0.7\text{\ m²}\times 0.55\approx \mathbf{500}\text{\ kWh/year}\)
- Temperature Independence: Unlike standard flat-plate solar collectors or solar PV panels—whose outputs can plummet in sub-zero weather—evacuated tubes will easily heat fluid up to 60°C to 80°C on a clear day in January. [1, 2]
- Snow Shedding: To maximize heat capture across the entire year (and particularly to boost poor winter production), the rack should be installed at a steep tilt angle—ideally latitude plus 15° (around 60° to 65° in Eastern Canada). This steep inclination forces snow to slide off the slick glass tubes effortlessly. [1, 2]
- Heat roughly 11,000 liters of water from a chilly tap temperature (10°C) up to a hot shower temperature (50°C).
- Offset about 15% to 20% of the domestic hot water needs for a single person over the course of a year.
- Act as a modest supplemental "offset" loop for a hydronic radiant floor heating or greenhouse system. [1, 2]
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 1,929 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 3 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 4 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 4 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 4 hours ago
-
RE: Why don't people choose heat pumps?
With a heatpump tariff, it should be cheaper to operate...
By Batpred , 5 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 5 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 8 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 12 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 3 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago