Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
No spare parts for Vaillant Ground Source Heat Pumps in the UK & major corrosion issue is another problem for GSHP
@phowardstutterheim, now that this thread has been reawakened, what happened with your system?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
The corrosion problem was never resolved. I filed a lawsuit against the maintenance company for failure to prevent corrosion and compensation for damages, but my legal firm and I could find no expert witnesses, likely partly due to self-protection within the industry, and partly due to the difficulty of proving internal damage, likely reduction in efficiency and in useful life of the heat pump and ancillary equipment, without dismantling and virtually destroying the pump in the process. Corrosion is a topic that no one in the industry is willing to acknowledge or address. The case was ongoing for nearly three years and finally had to be abandoned. After replacing various corroded parts as well as a Sorbox filter, the system continued to function. Vaillant Germany apologised, as did Vaillant UK, and promised in writing that parts would always be readily available in the UK, but I have no way of knowing if this is the case or not.
The corrosion problem was never resolved.Posted by: @phowardstutterheim
Here's an excellent explanation.
I filed a lawsuit against the maintenance company for failure to prevent corrosion and compensation for damages
If you have non barrier PEX underfloor heating, it is the most likely culprit as it is permeable to oxygen.
The maintenance company can't do anything about it.
Whoever decided to install non barrier PEX in a heating circuit bears responsibility, but it's probably too late to sue them.
A little bit of oxygen (ie, the amount in the initial filling water) is OK. It'll react and form oxides, and if you add inhibitor these also contain oxygen scavengers. Then you get no corrosion unless you have oxygen ingress via non barrier PEX, refilling after leaks, or other stuff like local low pressure sucking in air through the vents.
I also have a non barrier PEX underfloor heating system which was installed in the 1980's, so I looked into it in great detail. It seems like corrosion is a neglected and relatively not well understood subject (by installers) but all the info you need is actually available, for example in DIN VDI 2035.
Dirt separators like the "sorbox filter" will remove some sludge but this treats the symptom, not the cause.
When water contains a lot of oxygen, the only way to avoid corrosion is to 1) not have any steel component in the installation and 2) the heat exchanger should be stainless steel welded, or stainless steel with EPDM seals, not stainless brazed with copper (see above link for why) and 3) monitor pH and adjust if necessary.
...which is why I'm on a quest for a non cast iron body circulator that does not cost an arm and a kidney 🤣
The UFH system was installed at the same time as the GSHP, and it was supplied by Nu-Heat. Nu-Heat utilized its signature Fastflo® PE-RT tube for its hydronic systems. This tubing is a 5-layer high-density polyethylene pipe designed specifically for durability and flexibility in water-based floor heating. The Fastflo® tube used in these systems included an oxygen diffusion barrier to protect the heating system's metal components from corrosion. So no, it was not the UFH, it was maintenance, and I have lab results to prove it.
No corrosion inhibitors detected in system fluid. No frost protection detected. Low pH.
Yeah if you have acidic pH it's going to be bad.
I'm baffled at the size of these metal flakes, they're huge! This doesn't look like the usual sludge from oxidized iron at all! What the hell happened? Where does this stuff even come from? What kind of metal is ut? You have a lot of aluminium radiators?
We have no radiators. The sludge comes from inside the Heat Pump and ancillary equipment. We would have had to pay a lot to have these particles analysed but a corrosion expert said that they are clearly metal as well as rubber. Identifying the precise source of internal corrosion would be impossible without opening the system and looking at all the metal parts, which means effectively tearing it apart, hence our dilemma in providing sufficient evidence.
We were told by experts, including at Vaillant, which we consulted on multiple occasions and who were very reluctant to respond to our questions, that most of the corrosion accumulates in the rubber hoses inside the heat pump because the hoses do not have an oxygen barrier and are a common place for the accumulation of corrosion. The buffer cylinder may be corroded/damaged by corrosion on the hot water side. The condenser may be damaged / full of corroded particles
We were told that, “If the condenser fills with corroded particles, then it would potentially affect efficiency due to poorer heat transfer, this could cause issues with the operation, this will only become known once the heat pump started faulting, flushing may help in some very rare cases but generally does not solve the problem, systems are always recommended to be flushed and chemically treated upon install, a suitable filter is also recommended." While, over a two-year period, we found various people within the GSHP industry who were willing to discuss these issues after a lot of repeated correspondence, what we were unable to do was find an expert witness who would testify that:
- The brine side of the heat pump may be damaged
- The efficiency of the system may be compromised (COP)
- The life expectancy of the system may be compromised (20 years+)
Further, we thoroughly investigated the training and guidance provided by the GSHPA and the MCS at the time, and there was no reference anywhere to corrosion prevention, nor were certified installers required to have certification or training in basic heating and plumbing which, of course, covers corrosion prevention as an ABC. This may no longer be the case as we drew a lot of attention to this problem when we were investigating the causes and consequences of corrosion in heat pumps and attempting to take action against the maintenance company. At the end of the day, the maintenance company was trained according to standards of the day and was probably largely unaware of both corrosion and the means to prevent it. They are certainly aware now.
You can get an idea of what these shavings are:
They're not rusty, so not steel. You can always try with a magnet.
Crush it with some pliers to check if it's rock / mineral or metal.
Heat it with a blowtorch:
- Melts : aluminium
- Burns while melting: thermoplastic
- Burns while not melting: most likely rubber
- Does not melt: stainless steel
Honestly this looks like someone in the factory dumped a bin of metal shavings or other detritus into a pipe and you got the equipment delivered with the crap inside.
Are these shavings present on:
- Both sides of the heat pump?
- Only one side, which one?
We were told by experts, including at Vaillant, which we consulted on multiple occasions and who were very reluctant to respond to our questions, that most of the corrosion accumulates in the rubber hoses inside the heat pump because the hoses do not have an oxygen barrier and are a common place for the accumulation of corrosion.Posted by: @phowardstutterheim
Bullshit.
Rubber hoses do let in some oxygen, but that oxygen will travel in the circuit to corrode iron somewhere else. Just because some O2 enters in the hose doesn't mean it will "attract" sludge or particles into the hoses.
When I took out the 40 year old rubber hoses from my installation, they were absolutely okay. I mean, the rubber had gotten a little bit stiffer than new, and the inside was painted by brown sludge, but there wasn't a single particle in there. All the corrosion flakes were at places where flow slows down so they can settle (bottom of the buffer tank, radiators, etc) and of course in the heat pump exchanger since this has small cross section and acts as a filter.
FYI I drew a sample from my heating water
This is the kind of particles you'd expect from cast iron or steel corroded by oxygen. Scale in cm and mm. Unfortunately the cell phone camera can't tell the difference between rust (brown flakes) and magnetite (black particles) but it is clearly visible.
Completely different from yours. I bet it's not corrosion and this stuff was probably already inside when you got the equipment.
In your comment, you are both confident and rude, which translates into arrogant. Your knowledge appears to be based on a single sample of a 40-year-old system, which is hardly an apt comparison. Thus, in my opinion, your comment is both arrogant and ignorant.
- 26 Forums
- 2,591 Topics
- 60.3 K Posts
- 269 Online
- 6,924 Members
Join Us!
Worth Watching
Latest Posts
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@papahuhu As much as anything, it was bad timing that s...
By Toodles , 3 minutes ago
-
I intend to replace the Plex pipework in the area of my...
By DavidAlgarve , 6 minutes ago
-
RE: Electricity price predictions
Mention on the news about Octopus and one or two other ...
By Toodles , 2 hours ago
-
RE: Rate the quality of your heat pump design and installation
@josejo Reports of such lack of commissioning and downr...
By Toodles , 3 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Looks like you're not subscribed to any topics... pleas...
By Mars , 3 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 11 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 23 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 1 day ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 1 day ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 1 day ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago