Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @alec-morrowinternet failures are rarely excessively long. [...] Im always amazed by how people in the U.k. would rather find fault with what’s on offer rather than try and understand how things actually work.
Asking "what happens if ..." is part of trying to understand how these things actually work!
Also, I'm amazed by how some people still don't seem to accept how bad internet connectivity is in some UK villages. Call it rare if you like, but it's not exactly unknown for an underground section to flood or a cabinet to get taken out by a road vehicle and internet connectivity to be missing for days until the drainage/wiring is repaired and/or equipment replaced. If I'm home, I could reroute internet over the mobile networks but that is often heavily restricted.
So, I think it's vital that any UK-deployed "smart" controller's on/off decisions can be overridden and it doesn't only "runs to the transmitted parameters", but that still risks it getting cold before someone reaches the interface. It's desirable and better for it to fail safe if it loses connection to its mothership. It would be nice if reviews would test and mention this important feature.
You are perfectly correct, which is why I asked the question.
Industrial control systems are designed to 'fail-safe' for obvious reasons, and having the failure of one sensor (even a very important one) out of possibly several thousand, would have to be extremely dire for it to cause a major problem or a shutdown. This would normally have been engineered out by the use of a 2 out of 3 voting system.
Whilst many control systems may now be controllable via the internet, it is normally only the adjustment of settings that is allowed, actual control is still kept within the actual control system hardware.
It is therefore important that any home heating controller, retains and operates to the last acceptable input from any external source, be it over the internet or otherwise.
I've literally just changed my 2 grant Aerona to default weather compensation to see if it makes a difference to consumption, thanks for advice given by some helpful people on this site.
However what I am trying to get my head around is:
1. Hive thermostat set up on installation. Do I leave this at my current 19 degrees?
2. The hot water is programmed overnight by a separate timer connected to the cylinder while I'm on overnight cheaper tariff, and then programmed by the hive to top up a couple more times through the day for an hour.
My question is when the pumps heat the water, the radiators lose some of their heat and then have to spike again. Is my set up wrong? Or is it because it's programmed through 3rd party thermostat?
3. Both the grant controllers set up for pump 1 and 2 show different outdoor and indoor temperatures only marginally between .5 and 1 degree. Does this matter?
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
Posted by: @bretixI've literally just changed my 2 grant Aerona to default weather compensation to see if it makes a difference to consumption, thanks for advice given by some helpful people on this site.
However what I am trying to get my head around is:
1. Hive thermostat set up on installation. Do I leave this at my current 19 degrees?
No. Turn it up to 25 or so. The idea is to see how how the WC curve makes the house then change it if it gets too hot
2. The hot water is programmed overnight by a separate timer connected to the cylinder while I'm on overnight cheaper tariff, and then programmed by the hive to top up a couple more times through the day for an hour.
My question is when the pumps heat the water, the radiators lose some of their heat and then have to spike again. Is my set up wrong? Or is it because it's programmed through 3rd party thermostat?
That's normal and how I'd do it if I were on a cheap rate. Heating stops when HW runs. If you're not using much, HW will only be actually heating for less than an hour.
3. Both the grant controllers set up for pump 1 and 2 show different outdoor and indoor temperatures only marginally between .5 and 1 degree. Does this matter?
I don't know for sure but I wouldn't think that variation matters in the scale of things.
Let us know how you get on.
@kev-m it has made a difference to my electricity use. I've probably tightened up too much on hot water requirements so will be looking at those settings more. Just discovered hughf has posted the instructions for the chofu pump which has way more detail so will be exploring those for the hot water side of things.
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
This is a fascinating topic for any Heat Pump owner who is even slightly curious in getting the maximum efficiency from their device. Thank you to those knowledgeable posters who have provided the information.
I have a Mitsubishi Ecodan 14kW with a FTC5 and PAR-WR51R-E wireless controller heating radiators. Since installation the system is set to Auto Adaption mode and has worked flawlessly in heating my 180m2 1992 built timber framed house through periods of serious cold wet and windy weather in North East Scotland.
The installer said that Fixed Flow was only used for commissioning, Weather Comp Curve was too slow to react in our exposed location and that Auto Adaptive setting would give me the best of all worlds in that it auto-magically tweaked the curve on the fly to maintain a comfortable house. In terms of costs is has been more successful than I had ever hoped in reducing the energy bills by around 60% from LPG, electrical heaters and solid fuel used previously. According to the FTC5 my flow temps seem not to vary greatly from between 33C and 36C, even in the depths of winter. My 2022 stats show I consumed 6400kWhs for whole house heating and hot water use which I do not consider bad (perhaps naively) with an overall COP of 4.2
My reading here suggests that weather compensation is the way to go but is there really going to be much difference and savings over my current setup?
Posted by: @abernyteThis is a fascinating topic for any Heat Pump owner who is even slightly curious in getting the maximum efficiency from their device. Thank you to those knowledgeable posters who have provided the information.
I have a Mitsubishi Ecodan 14kW with a FTC5 and PAR-WR51R-E wireless controller heating radiators. Since installation the system is set to Auto Adaption mode and has worked flawlessly in heating my 180m2 1992 built timber framed house through periods of serious cold wet and windy weather in North East Scotland.
The installer said that Fixed Flow was only used for commissioning, Weather Comp Curve was too slow to react in our exposed location and that Auto Adaptive setting would give me the best of all worlds in that it auto-magically tweaked the curve on the fly to maintain a comfortable house. In terms of costs is has been more successful than I had ever hoped in reducing the energy bills by around 60% from LPG, electrical heaters and solid fuel used previously. According to the FTC5 my flow temps seem not to vary greatly from between 33C and 36C, even in the depths of winter. My 2022 stats show I consumed 6400kWhs for whole house heating and hot water use which I do not consider bad (perhaps naively) with an overall COP of 4.2
My reading here suggests that weather compensation is the way to go but is there really going to be much difference and savings over my current setup?
Hello @abernyte and welcome. I'm very interested in your setup as it's similar to mine (I have FTC 6 but I don't think there is a lot of difference). I haven't tried auto adaptation properly yet but will soon. I have heard it takes a week or two to 'learn'. That's quite a low flow temp for radiators btw. What sort of indoor temps do you have?
We have set it to 18C in morning rising to 19C lunchtime and 20C in the evening with a 15C set back overnight. I have set various slight tweaks to this depending on the season but broadly the same.
Posted by: @abernyteThis is a fascinating topic for any Heat Pump owner who is even slightly curious in getting the maximum efficiency from their device. Thank you to those knowledgeable posters who have provided the information.
I have a Mitsubishi Ecodan 14kW with a FTC5 and PAR-WR51R-E wireless controller heating radiators. Since installation the system is set to Auto Adaption mode and has worked flawlessly in heating my 180m2 1992 built timber framed house through periods of serious cold wet and windy weather in North East Scotland.
The installer said that Fixed Flow was only used for commissioning, Weather Comp Curve was too slow to react in our exposed location and that Auto Adaptive setting would give me the best of all worlds in that it auto-magically tweaked the curve on the fly to maintain a comfortable house. In terms of costs is has been more successful than I had ever hoped in reducing the energy bills by around 60% from LPG, electrical heaters and solid fuel used previously. According to the FTC5 my flow temps seem not to vary greatly from between 33C and 36C, even in the depths of winter. My 2022 stats show I consumed 6400kWhs for whole house heating and hot water use which I do not consider bad (perhaps naively) with an overall COP of 4.2
My reading here suggests that weather compensation is the way to go but is there really going to be much difference and savings over my current setup?
I suspect that your installer is one of the few with the relevant knowledge of how to commission a heat pump correctly.
I think that your system is using a combination of weather compensation and auto adaptation, which should provide the best overall accuracy and efficiency. If you are achieving an overall COP of 4.2, you should be very pleased. I would not suggest changing anything.
Thank you, that is good to know and matches what my "gut" instinct was telling me but you know what "fear of missing out" is like! Yes, the radiators are rarely anything other than tepidly warm to cold and the installer spent some time matching the rather larger radiators to each room compared to the old microbore ones they replaced. During commissioning we drew his attention to the lack of heat to touch in the rads and yet the house was uniformly warm. He just smiled and said "white mans magic".
sounds like it is working in weather compensation already..
it indeed fascinating how much heat there us in luke warm water in rads
I rather suspect you remembered something different from what he said!
Professional installer
but it's not exactly unknown for an underground section to flood or a cabinet to get taken out by a road vehicle and internet connectivity to be missing for days until the drainage/wiring is repaired and/or equipment replaced. If I'm home, I could reroute internet over the mobile networks but that is often heavily restricted.Posted by: @mjr
We've been offline since just before noon. Cable break, affecting several villages. No forecast repair time yet. Glad our heating is set to run OK without internet.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,110 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 5 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 10 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 16 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago