Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

vaillant arotherm plus - Failure - DHW

24 Posts
6 Users
3 Reactions
134 Views
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 178
Topic starter  

Vaillant engineer arrived today.  He change the control board and harness for the compressor.  This did not fix the problem.  So next step is for the inverter to be changed. However, there is a problem!

The Vailliant engineer found 20 volts being inducted into the EBUS cable.  This is a result of the EBUS cable being in the same outside wall trunking as the mains feed (about 2.5m).  The manufacturers specs states that the 2 cables have to be separated by at least 120mm. 

Vaillaint will not come back until this is fixed.


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5107
 

Posted by: @trebor12345

The Vailliant engineer found 20 volts being inducted into the EBUS cable.  This is a result of the EBUS cable being in the same outside wall trunking as the mains feed (about 2.5m).  The manufacturers specs states that the 2 cables have to be separated by at least 120mm. 

Ooh interesting.  Installer is going to have to fix that I presume.  Is there any suggestion that this could be the only problem (in which case Vaillant may want to charge the installer for nugatory work!).  


This post was modified 2 days ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 178
Topic starter  

Posted by: @jamespa

Posted by: @trebor12345

The Vailliant engineer found 20 volts being inducted into the EBUS cable.  This is a result of the EBUS cable being in the same outside wall trunking as the mains feed (about 2.5m).  The manufacturers specs states that the 2 cables have to be separated by at least 120mm. 

Ooh interesting.  Installer is going to have to fix that I presume.  Is there any suggestion that this could be the only problem (in which case Vaillant may want to charge the installer for nugatory work!).  

Myself I don't believe that it's an induced voltage in the EBUS.  The installer is coming Thursday to reroute the cable.

 


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5107
 

Posted by: @trebor12345

Myself I don't believe that it's an induced voltage in the EBUS.  The installer is coming Thursday to reroute the cable.

I'm inclined to agree.  Poor bus design that can't survive this.  I know you are supposed to separate mains and signal cables, but I bet a lot don't.   I guess that they also say any old 2core cable doesn't help, if it were screened or twisted pair it would be more resilient

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 178
Topic starter  

Posted by: @jamespa

Posted by: @trebor12345

Myself I don't believe that it's an induced voltage in the EBUS.  The installer is coming Thursday to reroute the cable.

I'm inclined to agree.  Poor bus design that can't survive this.  I know you are supposed to separate mains and signal cables, but I bet a lot don't.   I guess that they also say any old 2core cable doesn't help, if it were screened or twisted pair it would be more resilient

 

The manufacturer should specify a screened EBUS cable (IMHO).

 


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
bobflux
(@bobflux)
Estimable Member Member
Joined: 4 months ago
Posts: 113
 

Posted by: @trebor12345
The Vailliant engineer found 20 volts being inducted into the EBUS cable.

Without information about where and how it was measured, this is useless. Don't even know if DC or AC.

EBUS has 20VDC between the two wires when idle, so if it the measurement is "20V DC between the two wires" then yeah it means the device at the other end of the cable is powered and the cable is connected, good news, everything works fine... 🤣 

EBUS does not use differential signaling, it's plain old single ended 2400bps serial, so twisted pair is not likely to bring any benefit (no drawback either). Best protection against interference would be coax. You could also use a 2 conductor shielded cable but shield needs to be connected at both ends to "-" terminal. Strange they didn't go with cutting edge technology from 1983 like RS485 or CAN like everyone else. RS485 works fine on dirt cheap SYT telephone cable ziptied to three phase AC cables... 

 

 

 



   
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 178
Topic starter  

Posted by: @bobflux

Posted by: @trebor12345
The Vailliant engineer found 20 volts being inducted into the EBUS cable.

Without information about where and how it was measured, this is useless. Don't even know if DC or AC.

EBUS has 20VDC between the two wires when idle, so if it the measurement is "20V DC between the two wires" then yeah it means the device at the other end of the cable is powered and the cable is connected, good news, everything works fine... 🤣 

Not my area of expertise, but it was measured between the plus and minus of the EBUS cable to Earth. Cant remember if it was AC or DC, but I think AC.

 


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 178
Topic starter  

Installer called this morning and has move the 2 cables 120mm apart.  System has been started and switched off 3 times and its working.  So now in monitor mode.


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
Batpred
(@batpred)
Noble Member Member
Joined: 1 year ago
Posts: 1066
 

Posted by: @trebor12345

Posted by: @editor

If it were my system I’d be straight on to the installer and Vaillant support. A three-week-old heat pump really shouldn’t be throwing faults like that.

The installer has just called and noted an error code of F.753, which means there is fault with the outside unit (communication has been lost between the main heat pump control board and the inverter/frequency converter board).  Vaillant have been contacted and will attend site on Wednesday.

Just curious, is your installer a small local one or a major one?

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
Batpred
(@batpred)
Noble Member Member
Joined: 1 year ago
Posts: 1066
 

Posted by: @trebor12345

Posted by: @jamespa

I'm inclined to agree.  Poor bus design that can't survive this.  I know you are supposed to separate mains and signal cables, but I bet a lot don't.   I guess that they also say any old 2core cable doesn't help, if it were screened or twisted pair it would be more resilient

The manufacturer should specify a screened EBUS cable (IMHO).

the new vaillant models pro and the new plus use modbus for this communication to the odu, so it seems this will make it more robust to installers trying to cut corners.

I am also pretty sure vaillant also do a “pipe with signal cable” combined option to stop ac induced currents - as not even a rookie installer would want to be found running power cables next to hot water ones… 😉 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 178
Topic starter  

Posted by: @batpred

Posted by: @trebor12345

Posted by: @editor

If it were my system I’d be straight on to the installer and Vaillant support. A three-week-old heat pump really shouldn’t be throwing faults like that.

The installer has just called and noted an error code of F.753, which means there is fault with the outside unit (communication has been lost between the main heat pump control board and the inverter/frequency converter board).  Vaillant have been contacted and will attend site on Wednesday.

Just curious, is your installer a small local one or a major one?

 

I would say a medium company of around 20/30 employees.

 


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 178
Topic starter  

As expected it failed to run late yesterday with the same fault codes.  So inverter to be changed on monday.


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote