Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

vaillant arotherm plus - Failure - DHW

25 Posts
6 Users
3 Reactions
173 Views
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 179
Topic starter  

Vaillant called today and have now changed the inverter.  So all 3 components changed (control board, harness and inverter). They also checked the AC voltage being induced by having the mains supply and EBUS cables separated by 120mm.  This had dropped from 20 volts to 5 volts. 

Now we wait and so what happens. 


This post was modified 1 hour ago by trebor12345

2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote