Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
50 Hz heat pump on a 60 Hz grid
My understanding is inverters modulate .. so heat pumps designed for a 50 Hz grid can run on a 60 Hz grid as well. Is this correct? I see HPs from China rated for both .. labelled 50/60 Hz .. is this true of all models? I am in Canada (60 Hz grid) .. so we don’t have as many options, and I’d love to import the better tech you guys have in Europe.
Single phase heat pump inverter drive consists of boost power factor correction, HV DC bus caps, then three phase full bridge inverter driving the motor. There is no hardware specific reason why a single phase 50Hz model would not run fine on single phase 60Hz as long as voltage is correct. For US-style 240V ie split phase with Neutral in the middle, maybe problems could occur with the noise filter if it is not designed with this in mind. The software may also detect 60Hz, or detect split phase as L/N inversion, decide it is abnormal, and refuse to run. Better ask the manufacturer.
- 27 Forums
- 2,783 Topics
- 65.6 K Posts
- 2,466 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
To be honest, I was not sure about the status. I see th...
By Batpred , 23 minutes ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
Ah, that makes sense when a combi is in place. The boil...
By Batpred , 2 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
@bobflux Thanks, that gives me something to check the i...
By Paul1098 , 3 hours ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
Without doing some research I can't immediately answer ...
By JamesPa , 4 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
For Powerwall calibration, avoid forcing repeated deep ...
By EnergyStorageTech , 11 hours ago
-
Over the years, due to the non barrier PEX underfloor h...
By bobflux , 23 hours ago
-
RE: Getting closer to a finished Haier system
All the 45° elbows required for getting the primaries i...
By Singlespeed , 24 hours ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 3 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 3 days ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 3 days ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 4 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 4 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 5 days ago