Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @bensonAnyone able to advise at all?
I' d like to see a graph of that. It doesn't make sense to me, unless he means that at low temps, the pump runs at constant speed.
Midea MHCV10WD2N7 R290, 5.8kWp energy community solar power.
Posted by: @bensonAnyone able to advise at all?
I' d like to see a graph of that. It doesn't make sense to me, unless he means that at low temps, the pump runs at constant speed.
I agree, the video lacks context and detail, and the Midea Engineering Data manual is even briefer:
"ZONE1 H-EMISSION sets the emission type for heating mode."
The radiator as opposed to UFH question appears in the comments below the video, but there is no useful answer.
Mr Graham Hendra (@grahamh), maker of the video, and late of Freedom Heat Pumps, is a member of this forum. He may be able to provide further details.
Midea 14kW (for now...) ASHP heating both building and DHW
This is a very interesting thread I am currently deep into the rabbit hole of building my own smart controller pretty similar to the svenarr but with added dry contacts for my Grant Aerona3. I started off with an esp32 module, a modbus hat for a raspberry pi and an 8 channel coil relay module but as I have iterated I have learned that the esp32 module can handle the switching itself and I sourced a much smaller modbus module. So I have ended up building two prototypes one that will plumb into my existing home assistant system to replace my Waveshare modbus converter and 8 channel relay (the two new red modules), and a RPi zero W with the modbus hat, that will be a standalone Home Assistant instance with full modbus control as well as switching. I am going to add a couple of RJ45 terminals and terminals for thermistors (tank and buffer tank if needed) so it should be a neat little unit when done. All the user (me and maybe a mate!) will need to do is run two cat5 cables out to the unit attach the wires to the PCB (I will create a wiring guide) and then plug the cables into the box and then will have either wired (PoE) connectivity of USB powered wifi connectivity to the heatpump.
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
I am also looking into the Grant R290 as it may also be a Exinda/Midea clone as I want to add this to my Home Assistant Integration. Obvs not owning one makes researching (read tinkering!) difficult lol!
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
@grantmethestrength - thanks for the contribution, very interesting. Not everyone will want to do this sort of thing, but for those that do, reading about and seeing what others have done is very useful. I do like wired connections, once wired up they are far more reliable than wireless connections (until the rodents get to the cables...).
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@grantmethestrength - thanks for the contribution, very interesting. Not everyone will want to do this sort of thing, but for those that do, reading about and seeing what others have done is very useful. I do like wired connections, once wired up they are far more reliable than wireless connections (until the rodents get to the cables...).
yeah I have opted for the PoE option as I prefer wired, but I realise others may need a wireless solution and are more likely to have power close to their ASHP rather than a couple of ethernet runs out of their house. Both versions could be located outside in an enclosure close to the ASHP with a couple of short ethernet runs into the unit. I already piped two cables out to my unit so I will put this where my current controls are. I just need to learn how to solder and we are good to go!
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
Posted by: @cathoderay@grantmethestrength - thanks for the contribution, very interesting. Not everyone will want to do this sort of thing, but for those that do, reading about and seeing what others have done is very useful. I do like wired connections, once wired up they are far more reliable than wireless connections (until the rodents get to the cables...).
I did look at your suggestion of minimal modbus but as I am deep down the Home Assistant rabbit hole I have parked that for now but it does look like a good stand alone solution.
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
@grantmethestrength that looks really good albeit must profess to not fully understanding all of what you have said! I'd love to have the knowledge to build such a device myself as you are doing, alongside learning some basic coding. Perhaps when I finish renovating our house (not too far off finishing), I'll delve into it a bit more. For now, the ready made svenar was absolutely ideal for us.
Posted by: @benson@grantmethestrength that looks really good albeit must profess to not fully understanding all of what you have said! I'd love to have the knowledge to build such a device myself as you are doing, alongside learning some basic coding. Perhaps when I finish renovating our house (not too far off finishing), I'll delve into it a bit more. For now, the ready made svenar was absolutely ideal for us.
This is actually based on the same chipset as the Svenar and if it wasn’t for my need to control dry contact switches the Svenar would have been a decent solution. Once I (read me and my AI overlords) have this working I am going to reach out to Sven and his dad and share my work as I really like their project.
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
Regarding the warm end of the WC curve, are there any particular parameters that people would recommend? I had it set as 31 degrees C at 16, which is working ok but leading to a fair bit of overshooting. With homely my minimum outlet flow temperature was set at 35 so I have it (perhaps incorrectly) set in my mind that I shouldn't be going much lower than this. I have just slightly adjusted to 31 degrees C at 14.
Furthermore I guess this is the time of year when the heating might just need to be turned on and off when a bit cold as it isn't quite 'full' heating season yet...
If it helps, my outlet is running at 25C.
It would seem to be erroneous that someone set a minimum flow temperature in the controller if you were using the homely, that is going to limit it’s low end (most efficient) range for no good reason. The high end range mayb necessary, but only if you have heat sensitive emitters, ie UFH.
Posted by: @bensonRegarding the warm end of the WC curve, are there any particular parameters that people would recommend? I had it set as 31 degrees C at 16, which is working ok but leading to a fair bit of overshooting.
This really depends on your heat loss and emitters. My installer and I seem to have been too pessimistic about the heat loss and maybe overshot on radiator upgrades, but that is a nice place to be.
At the moment it is 5.8C outside and 19.7C inside (target 20C). My system is breezing along with a flow temperature of 30.4C.
When it is 16C outside, I can’t get the flow temperature below 27-29C. The heat pump compressor won’t go slower than 15Hz. This doesn’t seem to be a problem, as in warmer weather it turns on and off maybe once every 2-3 hours.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 293 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 15 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 15 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 18 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago