@netdonkey Primary pump should run as follows:

Heating demand on 

DHW demand on 

Defrost demand on 

Secondary pump should run as follows:

Heating demand on 

Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)

 

Primary pump runs as described above. Secondary pump is constantly on until DHW is activated

 


   
ReplyQuote
(@ashp-bobba)
Estimable Member Member
343 kWhs
Expert
Joined: 3 months ago
Posts: 67
 

@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.


   
ReplyQuote
(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  

Posted by: @ashp-bobba

@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.

 

Just heard back from Samsung and there is a software upgrade that will fix this logic so the secondary pump isnt always running.

 

 

 

This post was modified 3 months ago by NetDonkey

   
ReplyQuote



(@ashp-bobba)
Estimable Member Member
343 kWhs
Expert
Joined: 3 months ago
Posts: 67
 

@netdonkey excellent, that will help then 🙂

 

 


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
13044 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2292
 

Posted by: @netdonkey

there is a software upgrade that will fix this logic so the secondary pump isnt always running

Is that upgrade applied automatically over-the-air to all Samsung units?

Or does it require the householder or installer to do something?

Save energy... recycle electrons!


   
ReplyQuote
(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  

@transparent Samsung service rep coming out on 3/1


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
13044 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2292
 

Sheesh! Ash him/her how many sites they have to visit to implement the firmware change.
... and why they couldn't devise a system to do this remotely.

Yes, it might need the homeowner to authorise the upgrade within the App,

and it might need to be undertaken within a time-window in order to prevent hackers attempting such a route in future.

But we already have such functionality on the UK Smart Meter system, and that was designed a decade ago.

Save energy... recycle electrons!


   
👍
1
ReplyQuote
(@ashp-bobba)
Estimable Member Member
343 kWhs
Expert
Joined: 3 months ago
Posts: 67
 

@netdonkey thats great service 

 

 


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26449 kWhs
Veteran
Joined: 4 years ago
Posts: 3009
 

Posted by: @netdonkey

@transparent Samsung service rep coming out on 3/1

Did you have to pay for the visit?

 

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote



(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  

@editor as it’s a software upgrade they are recommending, I’m not needing to pay.  Going to pick their brains on all the questions I have when they get here too!!


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26449 kWhs
Veteran
Joined: 4 years ago
Posts: 3009
 

@netdonkey could this be a first for Samsung? 😂 They do have a habit of charging for visits. I’m curious to see whether it’s an actual Samsung engineer or one of their many agents handling the call-out.

But fully agree in you maximising the visit and getting as much as info as you can out them. Looking forward to the update.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@netdonkey)
Estimable Member Member
313 kWhs
Joined: 6 months ago
Posts: 56
Topic starter  

@editor it’s one of their agents.  They did say the name of the company but can’t remember it!


   
👍
1
ReplyQuote
Page 9 / 10



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security