Posted by: @ashp-bobba@netdonkey Primary pump should run as follows:
Heating demand on
DHW demand on
Defrost demand on
Secondary pump should run as follows:
Heating demand on
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
Primary pump runs as described above. Secondary pump is constantly on until DHW is activated
@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobba@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
Just heard back from Samsung and there is a software upgrade that will fix this logic so the secondary pump isnt always running.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkeythere is a software upgrade that will fix this logic so the secondary pump isnt always running
Is that upgrade applied automatically over-the-air to all Samsung units?
Or does it require the householder or installer to do something?
Save energy... recycle electrons!
Sheesh! Ash him/her how many sites they have to visit to implement the firmware change.
... and why they couldn't devise a system to do this remotely.
Yes, it might need the homeowner to authorise the upgrade within the App,
and it might need to be undertaken within a time-window in order to prevent hackers attempting such a route in future.
But we already have such functionality on the UK Smart Meter system, and that was designed a decade ago.
Save energy... recycle electrons!
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkey@transparent Samsung service rep coming out on 3/1
Did you have to pay for the visit?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@netdonkey could this be a first for Samsung? 😂 They do have a habit of charging for visits. I’m curious to see whether it’s an actual Samsung engineer or one of their many agents handling the call-out.
But fully agree in you maximising the visit and getting as much as info as you can out them. Looking forward to the update.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
First time wall mounting an ASHP
2 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
Samsung problems
4 months ago
-
Sudden drop in COP
5 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 272 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@editor if possible please correct my reply above. In...
By Tim441 , 2 hours ago
-
RE: Setback savings - fact or fiction?
No need to create a new thread, @sheriff-fatman. You do...
By Majordennisbloodnok , 9 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Well done to Scottish Power for doing a good job. Well ...
By Majordennisbloodnok , 10 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Fair point. The highest frequency of defrosts I'd seen...
By Sheriff Fatman , 10 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 11 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I remember reading in some inverters. They mandate a se...
By Batpred , 12 hours ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 13 hours ago
-
RE: Running from backup generaor in powercut?
@majordennisbloodnok Back in the 80’ or 90’ we had a te...
By Toodles , 13 hours ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 15 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 15 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Great to hear! I just figured this out a day or tw...
By anotherdaveuk , 17 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 22 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 2 days ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 2 days ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 3 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 3 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 3 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 3 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 3 days ago