Samsung E911 intermittent issue
Hi all,
Been having a trawl through the forums for the E911 and have a few other queries.
I have a AE080CXYDEK which was installed back in June and has been working well. Recently, however, we have had a couple of E911 errors which has led me to dig into our install a bit more.
Using our MIM i can see the flow is around 7.2-7.4lpm which is almost at the HP's minimum in which the E911 error starts. I have queried our installer (electrician who installed the solar and battery and subsequently subbed the ASHP install out) and it's taking a while to get anywhere. So my queries are as follows:
We have a Evosta 3 set to fixed curve regulation mode level3. Is this correct?
It looks like the Evosta has been installed upside down but I assume it was done this way due to the flow direct?
I can stop it from erroring by only running the heating and within 15 mins of powering on the DHW it trips (subsequently in the last 12hrs I have had both running and it hasn't tripped). Does this narrow down what the issue could be?
In another thread, Mars mentioned checking the Y strainer. Is this easy to do as a novice or should I be pushing to get the plumber to come out and check. If it's easy where is it usually located and what does it look like?
How happy are other plumbers to come out and diagnose a system they havent put it and is it worth doing this?
Thanks!
@netdonkey The model number for your Samsung indicates it is an 8kW system? The flow rates you are indicating only provide around 2.5kW and the code E911 is related to lack of flow, airlocks, restrictions on flow or other flow sensor issues.
Samsung send an inline strainer with their systems, if this was fitted it will collect debris from the system and block (this is its job) this will need checking 1st, also its worth confirming the length of the primary pipework from the condenser to the plant room (from the condenser to the manifold or plant room, buffer or 1st secondary distribution pipework valves). It worth making sure this pipework is the correct size for the flow rate and distance it serving. 8Kw will need a minimum of 28mm on a short run.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Thanks. The pipework run from the ASHP to main plant is around 13m. Would the strainer be near the pump or the main plant? I assume the strain would be on the return to protect the pump?
@netdonkey The strainer can be anywhere on the rerun line from the airing cupboard / plant room to the ASHP condenser, so this could be in that room or at the condenser, they look like a Y shape: linked here for you to see.
Please clarify 2 things if you can?
13m from the condenser to the plant room as the main ASHP pipes
What size is the pipework from the condenser (most manufacturers need you to limit the run to a max 10M or calculate an upsize in pipework and pump to cope with the length of run).
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkeyWould the strainer be near the pump or the main plant?
On our system, originally, it was inside the heat pump unit (we don’t have a Samsung). It was a bloody stupid location because we had to remove heat pump side panels to access it, so we had the installers move it into our plant room. See photo.
I asked installers specifically about Y strainers on a recent podcast and they should be fitted on every installation, so you should have one somewhere.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@netdonkey Should be shut of valves either side. the nut can be a bit tight on some of them, be sure to support the pipe when you try.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@netdonkey do exactly what @ashp-bobba says above.
Cleaning it is really easy once you've popped the nut off. It's got a little gauze filter/mesh inside. Give that a rinse under a tap, but before you do, check to see how many corrosive bits are in there as a reference.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Can't see anything that resembles a Y filter. There does seem to be a big black fillter (pic attached) which might be a filter?
Before and after the Evosta3 circulation pump there are valves. Is it worth making sure those are fully open?
The heat pump has just came on, the pipes near the water tank start to get a bit warmer and then the HP goes off again so sounds like it might be cycling?
@netdonkey The filter in the first photo looks saucespiciously like a ‘MagnaClean’ type filter; as the flow passes through this, the larger volume of the chamber reduces speed of flow and allows a magnet to attract and retain any particles of ferrous material that passes through the pipework. This chamber is normally cleaned out during any servicing work. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
-
Samsung problems
3 days ago
-
Sudden drop in COP
1 month ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
10 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
2 years ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 27 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 17 minutes ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 5 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
Hello, unfortunately i did not take any photos, but you...
By ThunderMink , 6 hours ago
-
RE: Solar Thermal DHW and ASHP
Since you already have the ashp it makes little financi...
By Judith , 14 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
I think you’ll find it depends on the room heat loss. A...
By Judith , 14 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 15 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil Fwiw I have the 7kW model with which I'm, ver...
By JamesPa , 16 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@grahamf you appear to value your recirculating loop de...
By Judith , 16 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 16 hours ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 19 hours ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 20 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 2 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 3 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 3 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 3 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 3 days ago