Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Samsung Air Source Heat Pump suddenly started drawing large amounts of current

7 Posts
4 Users
1 Reactions
2,002 Views
(@iainched)
New Member Member
Joined: 2 years ago
Posts: 4
Topic starter   [#1403]

I have a Samsung AE160RXYDEG Air to Water Heat Pump that has operated happily for 3.5 years, including being serviced each year, that has suddenly drawing lot more current than normal. This is apparent because wiring at the pump's MCB in the house has started to melt without tripping the circuit breaker! Has anyone experienced this or can suggest where to look next bearing in mind that reconnecting the pump to the mains does not seem sensible?



   
Quote
(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

I would suggest that you get an Electrician to check the wiring for bad connections and to measure the actual current with a clamp meter.

 



   
ReplyQuote
(@iainched)
New Member Member
Joined: 2 years ago
Posts: 4
Topic starter  

Thank you. The connections are fine, reinforced by knowing that they have not been touched in 3 years. The challenge is putting a clamp meter on a circuit that might well starting melting if turned on. I can see from a power meter in the circuit that the average current draw in cold weather was 5 Kw but this went up to a peak of 8 Kw.

PowerDraw

 



   
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 4476
 

@iainched what size is your heat pump?


Get a copy of The Ultimate Guide to Heat Pumps

Subscribe and follow our YouTube channel!


   
ReplyQuote
(@iainched)
New Member Member
Joined: 2 years ago
Posts: 4
Topic starter  

16 kW.



   
ReplyQuote
(@saenergy)
Trusted Member Member Professional Installer
Joined: 4 years ago
Posts: 21
 

Posted by: @iainched

I have a Samsung AE160RXYDEG Air to Water Heat Pump that has operated happily for 3.5 years, including being serviced each year, that has suddenly drawing lot more current than normal. This is apparent because wiring at the pump's MCB in the house has started to melt without tripping the circuit breaker! Has anyone experienced this or can suggest where to look next bearing in mind that reconnecting the pump to the mains does not seem sensible?

 

from that description it would seem to be badly terminated or failing connection at the MCB.  It’s relatively simple to sort out, replace MCB, trim cable to good copper and determinate being careful of tightening torque etc.  essentially an easy job for a standard sparkle. 

I would suggest that you check the service schedule includes an inspection of ALL electrical terminations relating to the ASHP.  This would be the same for checks in solar, battery an EV chargers which should also be tested in a regular schedule. 

 


Internationally recognised award winning installer of heat pumps and stuff


   
👍
1
ReplyQuote



(@iainched)
New Member Member
Joined: 2 years ago
Posts: 4
Topic starter  

Thank you. The advice to "replace MCB, trim cable to good copper and determinate being careful of tightening torque etc" has be actioned and all looks OK so far.



   
ReplyQuote