Removing a Low Loss Header from Samsung Gen6 System
also its worth saying, the PWM pump is not the enabler to run at low flow temps. That comes from having big enough emitters, properly balanced, etc.
what the PWM does is control the flow rate up/down to maintain the DT , at lower output levels when running in a steady state for a long period. For a given lower output, you can have either the flow rate staying the same (Fixed speed pump) and DT reduced, or the DT can stay the same and the flow rate reduces (variable speed pump).
there is an FSV , can't remember the number of the top of my head, for Target DT. with a PWM pump in the system, the samsung will vary the flow rate to try to maintain this DT but only when its in the stable part of a heating cycle. It has no effect when doing DHW, or when in the initial startup part of a heating cycle (Which is 30-60 mins , at least on my system). This FSV for DT control method has no function if you don't have a PWM pump (this is a common misconception), and is of little use in a system with primary/secondary seperation.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks for that explanation Ian, very interesting and useful
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@iancalderbank Ah okay, thats interesting. I have to say deciphering the user manual and FSV values is one of the most difficult parts of owning a samsung heat pump.
@ecobaker You should see a Mitsubishi! 🤣
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 25 Forums
- 1,429 Topics
- 30 K Posts
- 18 Online
- 1,215 Members
Join Us!
Latest Posts
-
RE: Making best use of Agile with a battery and ASHP
Hello Jamesw, I’m in a similar situation as I have 8.1 ...
By Toodles , 41 mins ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@kenbone no need for what kenbone regarding the 100watt...
By David999 , 1 day ago
-
RE: Insulation of flow and return Heat Pump piping
@mike-h Thanks Mike. Toodles.
By Toodles , 1 day ago
-
RE: Bivalent (or even trivalent!) system design options for a new GSHP installation
For your interest @algienon this is what happens when a...
By Transparent , 1 day ago
-
RE: Rising Damp – Production Recommendation
Yet another topic I'm not an expert in. Nonetheless, th...
By Majordennisbloodnok , 1 day ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor yes, the more I read the forum posts the more I...
By sjn , 1 day ago
-
RE: Observations on my Ecodan's estimates of energy consumed and delivered
As it is possible for the FTC to be powered from a sepa...
By HarriUp , 2 days ago
-
RE: ASHP Cut-off Temperatures: What's Your Setting and is a Your Heating Still On?
My system has been running 24/7 on weather compensation...
By HughF , 2 days ago
-
RE: Heat Pump Truth or Myth#2 - Cycling uses a lot of power and ruins your COP
I cannot state that I have noticed that our A2A heat pu...
By Derek M , 2 days ago
-
RE: Maximising Savings: Navigating My First Year with Octopus Energy and Heat Pump Running Costs
@toodles I can also happily report that the Agile tarif...
By Steve D , 2 days ago
-
@editor As we all know, RHH always strive to educate, e...
By Toodles , 2 days ago
-
@bontwoody I used the website link to contact them for ...
By Toodles , 2 days ago
-
RE: Samsung ASHP power cycling
I have considered that and I would have expected to see...
By Blaine_t , 2 days ago
-
RE: 14kW Midea ASHP in an old leaky building
Hi @batalto. I see you have a Midea ASHP and I am sched...
By Kbedders , 2 days ago
-
RE: Additional ASHP kW for DHW cylinder?
We're in a similar boat to you with a hodgepodge of dif...
By Mars , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
Anyway, so far we have all missed the main protagonist ...
By Toodles , 2 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
@ivanopinion Im in the same team as Ivan. I think for a...
By bontwoody , 3 days ago
-
RE: Issues with Vaillant connectivity via the MyCONNECT gateway
@drew-pa I don't know about hard work! It is pretty cl...
By dr_dongle , 4 days ago
-
RE: Are Solar Diverters Necessary for Homes with ASHPs and Solar PV?
@editor No, I made one 😀 Loft insulation all...
By Andris , 5 days ago
-
@hughf Thanks for that. Ah so they are talking about ...
By IRMartini , 5 days ago
Latest Topics
-
Making best use of Agile with a battery and ASHP
By jamesw 3 hours ago
-
By Toodles 2 days ago
-
By Blaine_t 2 days ago
-
Insulation of flow and return Heat Pump piping
By Toodles 2 days ago
-
Rising Damp – Production Recommendation
By Mars 2 days ago
-
Additional ASHP kW for DHW cylinder?
By Project_Electrify 3 days ago
-
By IRMartini 5 days ago
-
Riello / Midea - modbus set flow temp
By stuartornum 6 days ago
-
Ecodan software update. Real or scam?
By Morgan 6 days ago