Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@jamespa I was told by the octopus engineer to set the target temp to 21c, and it's not getting to 21. It's been "warming up" since midday and still not up to 21c.
I can live with 21c tbh, but it's more my mum who seems to prefer something close to 22c. She spends most of her day in the living room, where it lags a few degrees behind. Hopefully won't when I do the adjustment tomorrow.
I'm pretty sure my system was designed to reach more than 18c, as per my radiator schedule. IIRC, its supposed to be able to reach 21c in the living room.
Posted by: @editorPosted by: @razzI was told by the Octopus people that the primary pod should be in the part of the house with the most consistent temps.
Does your hallway really have most consistent temperature or was it just easiest for Octopus to install your pod there?
This is nothing more than guidance, but our main thermostat (pod) lives in a place that is most ‘neutral’. Our main living areas are the warmest and get a lot of solar gain. Our TV room is the coldest as is the rest of the north facing part of the house. So ours lives in the hallway because it’s the ‘middle’ temperature of the house and that works for us to deliver and call for heat most uniformly.
Like @andrewj says, it’s about figuring out which room in your house that is.
The rear extension (living room/diner/kitchen) has a lot of glass, plus a 'roof lantern', so it gets cold in the winter, and VERY hot in the summer. Same with the loft extension.
IIRC, the installer said one of the reasons they put it in the hall to avoid the heat spikes from cooking. The installers were worried about the cosy hub wifi signal reaching the pod, so didn't want to put it to too far from the cosy hub. Also, the old thermostat was in the hall, so they figured it would be a good spot.
I think putting it in the first floor hall might be more 'neutral', it's relatively sheltered from solar gain, away from any particular radiator etc.
Posted by: @jamespaI just want to repeat and emphasise that, in simple terms, you have to choose between radiator balancing, in which the householder must currently play a part in some cases, or maximum comfort. This choice is independent of whether the heat source is a heat pump or a boiler, because its about the behaviour of the radiators and the house not the heat source.
Stay the course and you will very probably achieve much higher level of comfort than you ever will with a boiler based system (at least one set up as we almost invariably do set it up).
Up until the introduction of heat pumps more or less the only people in the UK* who experienced the significant comfort benefits of low temperature operation (which you aren't yet seeing) were those with underfloor heating. Heat pumps are spreading those benefits to the majority with radiators, but it takes some adjustment, both in terms of how we think about and operate the systems and of the systems themselves. Stay the course and take the time to develop a bit of understanding and you should see the benefits.
This is the vision I bought into when I signed the contract for the heat pump.
Instead it's the exact opposite, and I'm paying a premium to be colder, and once again sleeping in my front living room, with ache/pain in one ear, in a strangely noisy house.
Posted by: @razzI was told by the octopus engineer to set the target temp to 21c, and it's not getting to 21. It's been "warming up" since midday and still not up to 21c
In an earlier post you’d stated: “Also, it looks like the radiator balancing is way off. Right now, my bathroom is 22.5c, hallway is 20.8c (target of 21c), and living room is 18.2c.”
The hallway at 20.8C is just about there. Does it not maintain and hold the temperature? What about the bedrooms and other areas (apart from the living room), are they at or close to 21?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editorPosted by: @razzI was told by the octopus engineer to set the target temp to 21c, and it's not getting to 21. It's been "warming up" since midday and still not up to 21c
In an earlier post you’d stated: “Also, it looks like the radiator balancing is way off. Right now, my bathroom is 22.5c, hallway is 20.8c (target of 21c), and living room is 18.2c.”
The hallway at 20.8C is just about there. Does it not maintain and hold the temperature? What about the bedrooms and other areas (apart from the living room), are they at or close to 21?
Yeah, the 20.8C holds in the hall. Currently, the hall is at 20.8C, the bathroom is 24C (but probs cos people have been using it, and its a small room). Living room is 18.4c, and that's with cooking breakfast there (20 mins ago it was 17c).
I don't have sensors in the bedrooms, but they're noticably colder so probably about 18c.
Posted by: @razzThis is the vision I bought into when I signed the contract for the heat pump.
Instead it's the exact opposite, and I'm paying a premium to be colder, and once again sleeping in my front living room, with ache/pain in one ear, in a strangely noisy house.
Well its achievable almost for certain. BUT you have to go back to basics and operate 24x7 with the weather compensation correctly adjusted, the main sensor (if there is one) in a sensible place and preferably disabled (not sure how the Octopus heat pump responds if you just turn the target to max, thats the normal way to disable sensors), radiators balanced with TRVs (if fitted) set well above the desired temperature. If you have problem areas of the house such as the area with the roof lantern then you have to recognise them and give some thought to how you will deal with them because no boiler or heat pump can, on its own, fix such extremes.
Its unfortunate, but we currently do not have the technology to do this automatically, it needs systematic manual tweaking until its right. This does take time but is well worthwhile. In many houses this can be done at install time but unfortunately some, such as yours it appears, have quirks that no installer can realistically find.
We can help here if you answer the questions, but ultimately only you can do the adjustments! Let us know how tweaking the LSV in the living room affects things.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Me again just to keep you all informed.
still an on going saga, had engineers out, moved hot water sensor to bottom of tank as 300l was only enough for 2 showers before the water got cold. So now the max temperature i can get hot water too is around 47 and takes around 2 hours but then never seems to go hotter in the app. Ie I haven’t got to 50 degrees yet. Shall see 47 probably hot enough. Not sure legionnaire cycle will ever work?
Noise at least the 2 engineers yesterday agreed it’s still too noisy listening to it themselves, not sure what happened but the heat pump has got noisy again not as bad as it initially was, but still too loud. They have gone off to see if new firmware was load over the previous good version.
i’m back to heating water during the day and setting overnight temperature low so pump doesn’t start. Wife was nagging as no sleep but at least Octopus are trying to sort.
oh the internal vibrating noise they have tried lagging internal pipes! Can’t test yet as letting family have a good nights sleep.
must admit when it was working it was pretty comfortable and costing around £7 a day,
when i run it like now its around £12 a day as it empties my house batteries early on during the day so i’m using peak price most if the time.
still these are new units fingers crossed they will sort soon.
ps its all wind noise, one if the engineers covered part of the fan when it was idling and the noise was similar to the sound i am getting during a heat or water schedule. To me sounds like the grill is causing most of the noise as aur rushes through ?
Good to hear that progress is being made! From what you and others say Octopus seem to recognise that there are issues with the Cosy 12 and working on fixes, so very likely a bit of patience, even if its annoying, will pay off.
Posted by: @l2jadstill an on going saga, had engineers out, moved hot water sensor to bottom of tank as 300l was only enough for 2 showers before the water got cold. So now the max temperature i can get hot water too is around 47 and takes around 2 hours but then never seems to go hotter in the app. Ie I haven’t got to 50 degrees yet. Shall see 47 probably hot enough. Not sure legionnaire cycle will ever work?
The legionella cycle may run on the immersion, at least in part. It depends on the heat pump, my Vaillant does it natively but many heat pumps engage the immersion.
Posted by: @l2jadps its all wind noise, one if the engineers covered part of the fan when it was idling and the noise was similar to the sound i am getting during a heat or water schedule. To me sounds like the grill is causing most of the noise as aur rushes through ?
Very plausible, grill design is pretty important to noise and of course the fan is probably running faster than with a Cosy 9.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@l2jad Re the noise of heatpump - mine has been noisier again over last few days. It seems to be the colder outside temperatures. It had been running a lot quieter but as soon as the temp dips below 5 degrees it ramps up again, not as loud as before but still too loud! This is definitely something Octopus need to fix or we'll be suffering again next Winter
@harriworld yes temperature does affect it have noticed that, last weekend was zero and i was asked to report back to octopus, which i have. i had experimental firmware on it, which was like running on tick over, very quiet, after their previous visit with the developer leads i believed it was being released.
The installers yesterday are trying to find out if i was updated again because thats when it went noisy again!!! Hopefully I should hear what i now have and is it the same i had been tested with ??
if you try covering half the fan when its quiet it sounds really noisy thats why i think its the grill causing the problem.
at least they know they have an issue as the installers have heard the noise it makes!!!
its definitely improved on my original problems but still not acceptable, as said i have basically had to set it off overnight and ramp up in the morning not on my cheap tariff period. But wife can’t sleep with it, i suffer tinnitus so not do bad for me
Currently viewing this topic 10 guests.
Recently viewed by users: Sheriff Fatman 26 minutes ago.
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 2,120 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 7 minutes ago
-
In June 2025 this academic group at Oxford modelled the...
By Judith , 1 hour ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
@majordennisbloodnok Thanks I hope it helps someone. St...
By antonical , 12 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 13 hours ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 19 hours ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 20 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 20 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 24 hours ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 1 day ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 1 day ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 2 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 2 days ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 2 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 2 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 3 days ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 3 days ago