New Samsung 12KW Heat Pump Help
Posted by: @bontwoodyThe seem to think that the situation is the same as the Vaillant one
FWIW, the Vaillant app gives the energy efficiency (=COP) as (total heat generated including heat pump energy used)/ energy used. See this screenshot. However, the numbers don't quite add up.
Posted by: @bontwoodyUsing the adjusted calculation for the Samsung alters its COP to 4.76. Much closer to mine.
@bontwoody I think the fact that your Samsung displays generated energy as less than OEM generated energy whereas mine is the reverse may just demonstrate the inaccuracy of how Samsung measures flow rate and delta T. It uses external temperature probes whereas the heat meter uses pockets and paired probes.
I monitored what Samsung was displaying as delta T and flow rate through ESPHome and it correlated well with its displayed heat output of around 4kW. After an hour of stable heat output, generated energy had increased by 4kWh. So I am pretty sure that generated energy includes electrical input energy and is different to the Vaillant. It is noteworthy that the latter calls it environmental yield.
@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
My interest in the correct formula is academic really, but there seem to be people on both sides of the fence.(see @technogeek here https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/new-heat-pump-owner-questions)
I think the argument about whether its called environmental yield or something else might be a translation one from the Korean.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
@bontwoody Sorry for the lack of explanation. I was taking my comment from Glyn Hudson's recent observation on the OEM forum - "I found the onboard Samsung flow and return temperature sensors are quite inaccurate, if you do a mass flow rate calculation to calculate heat delivered it could be significantly inaccurate because of the inaccurate onboard sensors. My Samsung is 20% out. Heat meters use matched pairs of temperature sensors in wet pockets, which have maximum 2% error."
I was concerned that users with poor COPs might be falsely reassured that all was OK if they added electricity usage to generation before dividing by usage. Of course, if the Samsung consistently underestimates generation, then the poor COP might be completely false and using the G+EU/EU formula might be closer to reality. But if it overestimates it as often as it underestimates it then using the correct formula might be more important. At the end of the day, if you are happy with your electricity consumption then that is what matters.
@mike-h Yes, totally agree about false reassurance Mike. I was thinking that an error would always be in the same direction but I guess that doesnt have to be the case.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 79 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 2 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 5 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 8 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Well at least that solves the mystery of where the exce...
By JamesPa , 10 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 10 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 1 day ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 1 day ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 2 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 3 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago