New 5kW Samsung Gen6 heat pump owner with loads of questions

46 Posts
8 Users
5 Reactions
1,715 Views
(@johnnyb)
Trusted Member Member
306 kWhs
Joined: 3 months ago
Posts: 40
Topic starter  

Hi, I've signed up as I've just started on the heat pump journey and discovering it isn't entirely straight forward. My initial cop was about 2 where I was expecting something like 3.5-4 and being able to tweak it get above 4.

We are self building a new home, have moved in but still working on it as we lived in a static caravan on site over the summer. The heating has been on for about 2 weeks.

We have a 5kW Samsung Gen6 I would love to know if anyone has an interpretation to the manual!

We have UFH downstairs and only a towel rad in the bathroom, which is feed from the same manifold as the UFH. Bedrooms don't have heating at the moment but we have pipe work in the floor void so we can add it if we need to.

I didn't research the heating much as there are so many things to find out about when building a house, and this really is a self build as I'm doing a lot myself. I decided to leave the heating to the plumbers as I don't have the knowledge and it needs quite a bit to get a HP running well. I'm now regretting that decision, or a least my choice of plumber, even though they have a good name locally. They will come out and help but there first things is to email Samsung to ask what is wrong as as far as they are concern they have done a good install. Also it is coming up to Christmas and they are very busy, that may not help the response I'm getting.

 

I have a buffer and a secondary pump. I was told Samsung insist on it for the warranty, we used a Samsung registered installer, but after reading this forum I'm realising it probably isn't the best way to run it. I also have fixed speed pumps and they are being run on their highest speed, both at the same speed.

I started running the flow temperature low and slow using the WC, but I think it may be too low.  I can have the flow temp varying between 23 and 30, mostly around 24-26, giving a floor temperature of 20-22 keeping downstairs around 20 deg if I run it constantly but the COP was around 2. Reading around that is probably too low a flow temperature?

I have increased the flow temperature to around 33-35 and yesterday I discovered that the immersion heater was set to boost if the hot water cycle took more than 20 minutes, which it does every time.

Changing these two has increased the cop to about 3 but the heating was on for several hours last night and the house was 22.5 deg this morning then went up to 23/24 when the sun came out and is still at 23 deg now, a little too warm to be comfortable this morning.  I'm in Suffolk and it has been around 10 degs today and no extra heat was needed.

 

I'd like any thoughts on the lowest temperatures that are suitable for the flow temps. It was nice to have the constant 20 deg in the house but I think I was just wasting energy and need another strategy.  I have discovered that the plumbers we used aren't of the heat geek camp, not anti, but still a traditional plumbing background.

I'm also interested in better ways to keep the temperature constant, or to keep the floor at a constant temperature so it isn't cooling right down before being heated up again, if that is a good idea.

 

If anyone has deciphered the Samsung manual it would be useful to understand it. I tried to change it so i could use the inbuilt heating controls last night and I got the primary pump to switch on but not the secondary pump that pumps the water around the UFH. There seem so many different settings it is difficult yo understand what controls are needed, what they do, if there are other ways to run it etc.

 

I have just signed up for a Homely trial so that will probably help the HP controls and the COP, but I'd still like to know what is going on and to have ideas on what is good to change, things I really should get the installers to sort out, and maybe changes that could be made to the pipework/pumps/buffer etc. to help efficiency.  Searching for info on Homely was how I found this forum.

This topic was modified 3 months ago by Mars

   
Quote
Mars
 Mars
(@editor)
Illustrious Member Admin
26249 kWhs
Veteran
Joined: 4 years ago
Posts: 2978
 

Welcome to the forums! I hope you’ll find the answers you’re looking for here; there are plenty of Samsung users around who might be able to help.

It’s no secret that most heat pump manuals leave a lot to be desired, and Samsung has long been known for having some of the least user-friendly ones.

While I can’t assist with your specific questions and will leave that to others, I’d be very interested to hear about Samsung’s level of support as you progress. Please do keep us updated.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@broadsman)
Estimable Member Member
748 kWhs
Joined: 9 months ago
Posts: 51
 

Good luck with getting any info out of Samsung. Their customer service is known to be very poor and they rely on the brand name to get purchasers. How do I know?, well you can guess. I have a Gen 7 12Kwh and like you am still playing with temperature settings. On open circuit, ie no buffer and as far as I know only one pump. Manual almost useless. Great info and help on here though.

 

This post was modified 3 months ago by Broadsman

   
🤔
1
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4995 kWhs
Joined: 3 years ago
Posts: 737
 

Hi @johnnyb 

I have the same heat pump as you but use radiators not UFH. 

You should be able to run the UFH on a lower flow temperature than radiators and the lower the better for efficiency and running costs. 

How do your radiators fit into the scenario as the will probably need a higher flow temperature than the UFH

The buffer vessel will have a negative effect on efficiency and I have heard the manufacture warranty demands it used often. 

Are you using antifreeze or anti frost valves?

How are you measuring COP as apparently there is a quirk in the Samsung figures you have to allow for. 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
👍
1
ReplyQuote
(@johnnyb)
Trusted Member Member
306 kWhs
Joined: 3 months ago
Posts: 40
Topic starter  

Thanks for the posts, I'll find out how Samsung respond in the new year. The installers messaged today to say they have emailed Samsung to ask for assistance and hope we will get an engineers visit, but said Samsung have already closed for Christmas so it will be the new year before they hear back.  They said they normally get charged £500 for a visit but are hoping it will be free as there seems to be an issue with our set up and another customer also having a similar COP.

 

@bontwoody According to a youtube video here it is less efficient under 30 or 35 deg. He did add a note later that after an update where it could control the PWM pump this was no longer an issue. I don't have a PWM pump, it's manual adjustment of the speed.  Agile is cheap again this weekend so I am going to turn the WC temps down again and leave it on low for a couple of days and see if it is any better. I'm also going to try to watch it to see if it is cycling and measure the flow and return temperatures.

 

The rad is a towel rad in the bathroom and is feed from the UFH manifold. When I suggested having it and running it this way I thought it would be good to dry to towels. When the flow temperature was 25 or under it didn't do much, at 30-35 it feels warm and does help dry the towels. They did tell me it wouldn't be much help but it wasn't difficult or expensive to put it in. It does help warm the bathroom most of the time when it is 30+degs so has some use.

 

We have anti frost valves.

I am using the Samsung figures on the controller, that's all I have at the moment.  Once the Homely set up is here I expect to be able to see a lot more.


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4995 kWhs
Joined: 3 years ago
Posts: 737
 

@johnnyb So I think what might be happening is at the very low flow temperature you are trying to use, you cannot get the UFH to release enough energy into the house for the minimum output of the heat pump. If you can control the pump speed by PWM (I do) then it can slow the pump and the water will stay in the floor longer and increase the delta T making the situation better.

I had a similar problem and managed to improve it by moving my controller into my living room and using the inbuilt thermostat to stop the heat pump before it started to cycle (see https://thegreeningofrosecottage.weebly.com/blog/a-moving-experience)

Do you know what your flow rate is? Perhaps you can turn your pump down manually to achieve a similar effect to PWM.

Regardless of all of the above, if you can run at a flow temp in the 30s you should get good COP. Im getting 4-5 in that range. The only difference I can see between our systems is you have a buffer. Depending on your situation, you might be able to turn that into a volumiser although I would image the volume of water already in your system would be sufficient for a 5kW Samsung. If you know how much UFH pipe you used you can calculate it.

This post was modified 3 months ago by bontwoody

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



TechnoGeek
(@technogeek)
Reputable Member Member
991 kWhs
Joined: 2 years ago
Posts: 114
 

Posted by: @bontwoody

How are you measuring COP as apparently there is a quirk in the Samsung figures you have to allow for. 

@johnnyb If it is any help, I calculate the COP / SCOP using the following formula for my Samsung heat pump

 

( Energy Generated + Energy In ) / Energy In = COP

So for example, on a day where my local outside temperature was a constant 6 C all day (12th Dec 2024) my system generated 84.6Kw and consumed 26.1 Kwh

This gave me a COP of: (84.6Kw + 26.1Kwh) / 26.1Kwh = 4.24 for that day.

 

To verify the formula is correct, my calculated heat loss for an inside temperature of 21C and outside temperature of 6C is 6.7Kw per hour.

This would in theory make my system consume: Heat loss / COP = 6.7Kw / 4.24 = 1.58Kw per hour of electricity

The system ran a total of 17 hours that day so consumed electricity at a rate of:  Total Electricity Consumed / Runtime = 26.1Kwh / 17hrs = 1.53Kw per hour 

So both results of 1.58Kwh and 1.53Kwh are very similar giving me the confidence in the above COP formula

 

Hope that helps 🙂

This post was modified 3 months ago by TechnoGeek

5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat


   
ReplyQuote
(@johnnyb)
Trusted Member Member
306 kWhs
Joined: 3 months ago
Posts: 40
Topic starter  

@technogeek Thanks for posting that. It does make sense now you've pointed it out,  but I haven't realised the energy generated needed adding to the energy used, and I don't think the installer did either as I gave him figures for the second week and he said my cop was just over 2. Even more worrying that they don't know how to interpret the Samsung figures!

 

If this is correct it means the best day the cop was 4 and the other days this week it was 3.5 or better.


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4995 kWhs
Joined: 3 years ago
Posts: 737
 

@johnnyb This formula does seem a bit contenious, but the results do seem to me to be closer to what is expected (obviously not to everyone though see https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/new-samsung-12kw-heat-pump-help/paged/3#post-38938)

The Vaillant heat pump controller has exactly the same glitch when trying to calculate COP.

This post was modified 3 months ago by bontwoody

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
TechnoGeek
(@technogeek)
Reputable Member Member
991 kWhs
Joined: 2 years ago
Posts: 114
 

@johnnyb to be fair I did not know in the beginning either. I had to do my own research and experimentation to understand what was going on.

This link has a graphical representation of what the formula is based on http://labman.phys.utk.edu/phys136core/modules/m3/refrigerators.html

Q1 is the heat harvested from the cold store (outside air or in Samsung speak "heat generated"), the work done (electricity consumed) W which are both added together to create Q2, the heat store (inside of your house). This sum is divided by the work W done to give you your coefficient of performance, COP.

COP must not be confused with efficiency (Output / Input) because that would imply you are creating energy from nothing (to get 400% efficiency) and the laws of physics states you cannot create or destroy energy, merely convert it from one form to another.

Kind Regards

5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat


   
ReplyQuote
(@johnnyb)
Trusted Member Member
306 kWhs
Joined: 3 months ago
Posts: 40
Topic starter  

@bontwoody Thanks for your posts, and the link to your blog. a very interesting project you have there.

I have tried different speeds on my pumps but with some the pump switched off and others the deltaT just got smaller, down to 0.5 at one point and then the pump switch off.  With a low flow temperature deltaT gets a little smaller I think, but mostly it is around 1.5-2, it is set to 5 in the settings and that is what it gets to with a DHW cycle.

Interesting about how to read the Samsung figures. At the moment my installer is reading it as a very low COP and it has got their attention so I will let them continue to question it.  Once I am on the Homely trial I should have more data and be able to see how much energy is actually being used and produced.

I have several more questions after reading your blog, it looks like you set your up yourself?  There are several settings I would like to try adjusting but I don't want to cause any issues or lose track of what I have changed and what affects they are having.

The field setting value (FSV) 4051 on my system is set to Use(100%).  You said you had to change yours to off for your pump to stop running continuously on the original pump.  My pump doesn't run continuously but I wonder if that is affecting my set up. Did you change both the positions of the wires and the setting at the same time? I would assume you did and don't know if the setting made the difference or the cable positions

Did the PWM pump make much difference to your COP and help things run better, was it worth changing?

When you had the cycling with the low flow temperatures was it affecting the COP? I don't think mine cycles, the primary pump is always on and I think the outdoor unit is always running when the pump is but haven't sat beside the outdoor unit to watch it as it is wet and windy today.  I also think that with FVS 2091 set to Use (signal on/off) it stops the unit cycling, but I'm not sure if I have understood that correctly or not, it might just be the primary pump.

It looks like you had the flow at low 30's in your graphs, but said you'd set the water law temperatures at 38 to 45.  Do you find the flow temperature is several degrees lower than you have it set in the waterlaw temperatures, mine seems to be.

 

DO you know what the settings need to be for the Samsung display unit to acts as the thermostat and control the heating?  I have an external thermostat fitted but want to try using the Samsung controls as you have done to see if it works, the thermostat I have seems to have a mind of it's own.  I found settings somewhere online but when I tried changing them a couple of days ago the secondary pump didn't switch on.

 

I love your EV. We looked at the i3 several years ago, and loved it, but bought an e-Golf as VW had a great deal on back in 2017 and the price was about £10k cheaper. We still have it, but look at i3's and still think they look a great little car.

 


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4995 kWhs
Joined: 3 years ago
Posts: 737
 

@johnnyb Thanks :-). I’m off out on a Xmas do tonight but will sit down and try to answer as many of your questions as I can tomorrow.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



Page 1 / 4



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security