Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Compressor attempts start but fails - Nibe Fighter 2005 8kW
Hoping someone may have seen this problem before. I have a Nibe Fighter 2005 8kw single phase heat pump which heats a swimming pool. From yesterday it is failing with the following behaviour. Starting from a full power off reset, the system waits 20 mins before attempting to start the compressor; after 20 mins I hear the compressor motor startup noise for about half a second, after which it stops; the fan continues to rotate; the system stays on, but evaporator temp, hotgas temp, etc are not right; after about 5 mins the compressor motor attempts to start again with a short pulse of noise, then stops; after the second attempt the system alarms and stops with "fan alarm" (but don't focus on "fan" because I have learnt that the alarm descriptions are pretty random).
The system had been working fine all winter (for background heating and frost protection, not pool heating) and has been heating pool fine for a few weeks this summer.
I'm on the Isle of Skye, with nearest heat pump engineers 2 hrs away, so I have looked after this heat pump myself for years: so far, 3 replaced temperature sensors and a new soft start unit (2yrs ago).
Unluckily for me this latest fault happened at 5.30 on a Friday, and the only guy who has ever helped me by phone finishes work at 5!
Any insights or advice would be gratefully received. It's been pouring with rain here for a few days so I haven't opened the heat pump lid to start poking around, see if anything looks amiss, etc.
The system is pretty old, maybe 15-18yrs, and we've had it from new.
Thanks
I had a very similar problem with my valiant and it turned out to be a blocked filter. Unbeknown to me I have a very fine filter in addition to the mag filter. Heat pump engineer told me this accounts for 90 percent of call outs so definitely worth checking.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thank you! As soon as it stops raining I will check that out. Looking at manual now.
It might not be in the manual, mine was a rather innocuous third party 40mmx80mm brass fitting between the heat pump isolation valve and the heat pump itself, on the return.
It may of course be something completely different. Any fault codes?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaI had a very similar problem with my valiant and it turned out to be a blocked filter. Unbeknown to me I have a very fine filter in addition to the mag filter. Heat pump engineer told me this accounts for 90 percent of call outs so definitely worth checking.
That's a very good suggestion. I'd forgotten that we had a similar issue a couple of years ago, but ours was accompanied with an error on the screen that I translated into a flow error. Given the age of @skyefarmer's system, I'm not sure the control panel throws up error codes. @skyefarmer do you have any errors?
In closing, that is probably the best name for a heat pump to date. "What heat pump do you have?" The "Fighter". Terrific name!
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Update: It finally stopped raining and I opened up the heat pump. The attached picture tells the story. Quite surprised that can happen!
So I'm currently searching for an appropriate replacement capacitor for the Ducati energia 16.33.5660
I usually use RS Components, but not looking good. Does anyone know what the modern equivalent is? Thanks. Will let you know if I find it.
Update 2: I've ordered a Ducati Energia 4.16.33.56.60 from TME Electronic Components. Fingers crossed for the new one fitting and me being able to salvage the wiring.
@skyefarmer pleased you found it!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@skyefarmer great you located the source of the issue and that you have the skills to replace the capacitor. Fingers crossed!
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @skyefarmerThe attached picture tells the story.
"To tell you the truth, I don't know if HAL is homicidal, suicidal, neurotic, psychotic, or just plain broken."
I think we know which category yours falls into @skyefarmer
Good luck getting it fixed.
Update: All fixed. Replacement Ducati capacitor is in. The only delay was getting hold of some stranded copper wire of suitable diameter to handle the start up current (approx 16A).
@skyefarmer amazing. Well done!
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@skyefarmer I see you have had a good bit to do with the same GSHP I have, just had my Fighter 1140 make a loud noise and so dirty it make house light flicker with electical noise and after a shutdown and restart it will not start the compressor, the Emerson ESC-255 has a Fault Mode LED error. Not sure if I should swap soft start...I can't find any info on what triggers the fault mode on the ESC-255.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 924 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 6 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 10 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 12 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 12 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 15 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 21 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 21 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago