Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New kitchen with no walls – will fan coil units work?
looking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
I have one Mitsubishi wall mounted fan coil in my otherwise all radiator ASHP system, installed because a passive radiator wouldn't fit. It's in the room we spend most time in, which is part kitchen, part living room. It was sized so that, at the design OAT, it runs at low fan speed (it auto adjusts fan speed based on its measurement of room temperature). Im really pleased with it and so is my wife.
The fan is just audible from 2m away when operating but is easily drowned out by any other noise including talking, the TC etc. Maybe I wouldn't want it in a bedroom (although it is white noise so fairly soothing) but in a living room totally acceptable.
The only potential problem is that it shuts down if the flow temperature is <30C, a figure which you cant adjust. As it happens thats OK for me because, when that occurs, the other radiator in the room plus solar gain is sufficient to keep the room warm. But I could imagine situations where this could be a limitation and if it is then there are other models where the low FT limit is adjustable.
I hope that helps.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
Silly questions, perhaps, but is it a large room and whereabouts is it in relation to the rest of the house?
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokPosted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
Silly questions, perhaps, but is it a large room and whereabouts is it in relation to the rest of the house?
about 3.1mx5m south facing so with the new patio doors will likely have massive solar gain.
Posted by: @jamespaPosted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
I have one mitsubishi wall mounted fan coil in my otherwise all radiator ASHP system, installed because a passive radiator wouldnt fit. Its in the room we spend most time in, which is part kitchen, part living room. It was sized so that, at the design OAT, it runs at low fan speed (it auto adjusts fan speed based on its measurement of room temperature). Im really pleased with it and so is my wife.
The fan is just audible from 2m away when operating but is easily drowned out by any other noise including talking, the TC etc. Maybe I wouldn't want it in a bedroom (although it is white noise so fairly soothing) but in a living room totally acceptable.
The only potential problem is that it shuts down if the flow temperature is <30C, a figure which you cant adjust. As it happens thats OK for me because, when that occurs, the other radiator in the room plus solar gain is sufficient to keep the room warm. But I could imagine situations where this could be a limitation and if it is then there are other models where the low FT limit is adjustable.
I hope that helps.
have you got a link or model number please.
@adamk https://www.saturnsales.co.uk/I-Life2-Slim-DLMV-170-ATS2-Fan-Assisted-Radiator.html is the one I have, there is a smaller one but the size difference is quite small and obviously the fan will have to work harder on the smaller one for any given output
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @adamkPosted by: @majordennisbloodnokPosted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
Silly questions, perhaps, but is it a large room and whereabouts is it in relation to the rest of the house?
about 3.1mx5m south facing so with the new patio doors will likely have massive solar gain.
And just for the absence of doubt...
When you say "new kitchen" you mean that it's not just a new room but also that the room has already had the units, cupboards, worksurfaces and stuff installed (i.e. far too late to get underfloor heating installed).
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
its half gutted at the moment. missus not keen on underfloor if it ever leaks its potentially a whole floor up job.
looking at that rad id struggle to fit it. longest bit of wall ive got is about 800mm.
What power do you need at what FT?
will thio one do https://www.saturnsales.co.uk/I-Life2-Slim-DLMV-80-ATS2-Fan-Assisted-Radiator.html
otherwise it looks like a kickspace heater is what you need
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The fan-assisted jobbie @jamespa has linked to looks great. If not, I must admit the hydronic plinth heaters look like a really good option as well although whilst they'll obviously plumb into a central heating circuit fine I've no idea how well they'd work with the "run it low and slow" setup that is ideal for a heat pump - I'm no plumbing expert.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
seen these but not sure they will output much unless i have several, due to the rated output being at 55c. but they do turn on at 30c.
https://kitchenheaters.co.uk/product/thermix-kph-1-3-wireless-plinth-heater-heat-pump/
@majordennisbloodnok we have an under plinth heater (a Myson) and it was set up for occasional heating with the gas boiler. The only change for use on the heat pump and much lower flow temperatures was to switch to summer mode. That makes the thermal switch off inactive but the fan still pushes out the heat.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 3,078 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 20 minutes ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 1 hour ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 1 hour ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 1 hour ago
-
RE: Why don't people choose heat pumps?
With a heatpump tariff, it should be cheaper to operate...
By Batpred , 2 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 2 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 5 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 9 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 3 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 3 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago