Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New kitchen with no walls – will fan coil units work?
looking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
I have one Mitsubishi wall mounted fan coil in my otherwise all radiator ASHP system, installed because a passive radiator wouldn't fit. It's in the room we spend most time in, which is part kitchen, part living room. It was sized so that, at the design OAT, it runs at low fan speed (it auto adjusts fan speed based on its measurement of room temperature). Im really pleased with it and so is my wife.
The fan is just audible from 2m away when operating but is easily drowned out by any other noise including talking, the TC etc. Maybe I wouldn't want it in a bedroom (although it is white noise so fairly soothing) but in a living room totally acceptable.
The only potential problem is that it shuts down if the flow temperature is <30C, a figure which you cant adjust. As it happens thats OK for me because, when that occurs, the other radiator in the room plus solar gain is sufficient to keep the room warm. But I could imagine situations where this could be a limitation and if it is then there are other models where the low FT limit is adjustable.
I hope that helps.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
Silly questions, perhaps, but is it a large room and whereabouts is it in relation to the rest of the house?
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokPosted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
Silly questions, perhaps, but is it a large room and whereabouts is it in relation to the rest of the house?
about 3.1mx5m south facing so with the new patio doors will likely have massive solar gain.
Posted by: @jamespaPosted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
I have one mitsubishi wall mounted fan coil in my otherwise all radiator ASHP system, installed because a passive radiator wouldnt fit. Its in the room we spend most time in, which is part kitchen, part living room. It was sized so that, at the design OAT, it runs at low fan speed (it auto adjusts fan speed based on its measurement of room temperature). Im really pleased with it and so is my wife.
The fan is just audible from 2m away when operating but is easily drowned out by any other noise including talking, the TC etc. Maybe I wouldn't want it in a bedroom (although it is white noise so fairly soothing) but in a living room totally acceptable.
The only potential problem is that it shuts down if the flow temperature is <30C, a figure which you cant adjust. As it happens thats OK for me because, when that occurs, the other radiator in the room plus solar gain is sufficient to keep the room warm. But I could imagine situations where this could be a limitation and if it is then there are other models where the low FT limit is adjustable.
I hope that helps.
have you got a link or model number please.
@adamk https://www.saturnsales.co.uk/I-Life2-Slim-DLMV-170-ATS2-Fan-Assisted-Radiator.html is the one I have, there is a smaller one but the size difference is quite small and obviously the fan will have to work harder on the smaller one for any given output
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @adamkPosted by: @majordennisbloodnokPosted by: @adamklooking at what i can use in my new kitchen if i get a heat pump fitted. due to so many doors and units using the rest i need to look at plinth heaters.
ive seen some that say they work with heat pumps, though surely if im running my system 24/7 the fans on them would also be running 24/7?
only other option is some sort of heating from the ceiling, as the heating pipe work is accessible at the moment?
Silly questions, perhaps, but is it a large room and whereabouts is it in relation to the rest of the house?
about 3.1mx5m south facing so with the new patio doors will likely have massive solar gain.
And just for the absence of doubt...
When you say "new kitchen" you mean that it's not just a new room but also that the room has already had the units, cupboards, worksurfaces and stuff installed (i.e. far too late to get underfloor heating installed).
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
its half gutted at the moment. missus not keen on underfloor if it ever leaks its potentially a whole floor up job.
looking at that rad id struggle to fit it. longest bit of wall ive got is about 800mm.
What power do you need at what FT?
will thio one do https://www.saturnsales.co.uk/I-Life2-Slim-DLMV-80-ATS2-Fan-Assisted-Radiator.html
otherwise it looks like a kickspace heater is what you need
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The fan-assisted jobbie @jamespa has linked to looks great. If not, I must admit the hydronic plinth heaters look like a really good option as well although whilst they'll obviously plumb into a central heating circuit fine I've no idea how well they'd work with the "run it low and slow" setup that is ideal for a heat pump - I'm no plumbing expert.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
seen these but not sure they will output much unless i have several, due to the rated output being at 55c. but they do turn on at 30c.
https://kitchenheaters.co.uk/product/thermix-kph-1-3-wireless-plinth-heater-heat-pump/
@majordennisbloodnok we have an under plinth heater (a Myson) and it was set up for occasional heating with the gas boiler. The only change for use on the heat pump and much lower flow temperatures was to switch to summer mode. That makes the thermal switch off inactive but the fan still pushes out the heat.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 2,013 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
@cathoderay Very valid points and I agree with your sta...
By ian33a , 56 minutes ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
The hot water heating looks normal. The heat transfer ...
By GrahamF , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay - thats great. Is there any possibility ...
By JamesPa , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 3 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 12 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 15 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 19 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 22 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 24 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 1 day ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 1 day ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago