Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Auto adapt and the Ecodan curve
Iv read often on here that while your on auto adapt the ecodan system will still to a good degree use the set curve you’ve set.
But…Recently iv had the it set at 38 high end @ -3.
The MELCloud app shows on cold mornings though the flow temperature reaching as high as 45c.
At the weekend just to see what happens I lowered my high end to 30c.
This morning MELCloud showed my flow rate at one point reaching 50c.
Is this going to show that while on auto adapt that actual set flow rate has no real affect??
Was this chart taken when the house was cold?
I think it would help others to interpret this if you can give OAT outside ambient temperature and inside thermostat temperature. And third piece of info is what was the target room temperature at this point. Also how long the HP has been on.
Problem is the chart shows a steep cool-down during the off time of 4 or 5 minutes. Not only that it’s cooling is accelerating towards the end of the off period.
As much info as you know is always handy but appreciate you may not know what’s needed. EG rads or UFH. Size of HP, how big is the load (size of total emitter capacity at T50 rating)
in principle if your room temp is close to your target room temp Auto Adapt will reduce its output but only as it gets close to room temp. But I have often seen Auto Adapt rising above my weather curve so I often stop using it.
So I’m not entirely sure if it uses my weather curve at all or if it has its own notional weather curve built in. That’s not to say it doesn’t use your curve I’m just not 100% convinced.
but regarding the curve you’ve posted it shows it wants to heat at a high output because the heat loss at that point in time is very high.
here is a chart of ours when the room temp is almost reached and you can see the drop in return temp is not steep.
I’ve also just noticed your curve might be doing a defrost???
Below are charts showing the hour before and hour after. Also a chart showing set temp/ room temp/ outside temperatures.
iv no underfloor heating.
size of pump is 8.5kw
no understanding tbh of t rating.
3 bed semi approximately
100sq meters
I have to state I’m not at all unhappy with performance as my house is well able to heat to a nice comfortable temperature seemingly quite easy. All rads fully open other than one in bedroom turned down to 2 tvr.
At 38c top end yes but as I said atm it’s down to 30c.
how do you know when it’s defrosting??
@westkent it’s defrosting when the flow temp line (in blue) drops below the return temp line. (In black)
The flow temp rapidly drops because the defrost system works in reverse so the flow water is chilled as its relative heat is used to warm up the refrigerant to melt the frosting.
depending on how many radiators you have your HP may struggle to operate as low as 30c without shutting down a lot. That’s why I asked about the T50 rating. That’s a measure of a radiator output at a given room temperature.
as an example my 8.5 ecodan works well at 35c and cannot go below 32c without rapid cycling.
we have 15 radiators
So as I have glycol in the system am I able to some way or other deter the H/P from defrosting???
@westkent The glycol is there to stop the water from freezing and causing damage to any of the pipework (in or outside the heatpump). The defrosting will still be a necessary stage in the heat pump’s cycle - when the fins ice up due to moisture freezing on them, they need to be defrosted or cleared with some heat. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Thanks for the replies. Very helpful in understanding how things to a degree work.
Im going to keep the upper temp at 30c at -3 and see if it continues to heat the house comfortably.
My heating went back on near on a couple of hrs ago at 3pm and the flow atm is at 34c with an OAT of 9c.
My wireless remote thermostat is set to 20c and showing a room temperature of 20.5c and still heating.
@westkent A thermostat has a ‘Hysteresis’; this may well be ~1 degree or possibly a little more - thus preventing a system from being turned on and then off at short intervals. Some controllers allow adjustment of this ‘tolerance’, others are fixed by the manufacturer. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
What does the front display of your main controller show you can offset the weather comp curve from there.
No one other than Mitsubishi really knows what auto adapt is allowed to do but all the info says it starts with the weather curve but then learns how you house heats up and adjusts from there.
if you have been running it for a while maybe it’s now doing it own thing
- 26 Forums
- 2,661 Topics
- 62.2 K Posts
- 855 Online
- 7,058 Members
Join Us!
Directory
Latest Posts
-
RE: GivEnergy inverter tripping due to over-voltage?
That's useful information @tim441 I would like to be ...
By Transparent , 55 minutes ago
-
RE: Cooling with air to water heat pumps
Very sensible Unfortunately I fear that's too simple...
By JamesPa , 1 hour ago
-
Nobody will, that's the point of this thread, the heat ...
By JamesPa , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Good morning. I just came across your website. Was ho...
By iRadiate , 7 hours ago
-
RE: Failed Heat Pump Install: IWA Claim Rejected
Many of the estimates we received mention IWA and RECC....
By Batpred , 18 hours ago
-
RE: Rural burning – I've had enough
Same here in Finland. It's strictly forbidden ...
By upnorthandpersonal , 18 hours ago
-
RE: Renewables & Heat Pumps in the News
Something worth flagging... we've just published a news...
By Mars , 18 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
The Homeowners' Q&A podcast is back... I've changed...
By Mars , 19 hours ago
-
RE: Anyone concerned about GivEnergy?
I have already signed up with Axle so yes, that takes c...
By KevH , 20 hours ago
-
@batpred Would it pass the airbnb feedback test no. I...
By EtchedPixels , 1 day ago
-
A quick update... we've just launched the beta version ...
By Mars , 2 days ago
-
RE: Who Actually Owns a Heat Pump in Britain? We Asked. Here Is What We Found.
The age part doesn't surprise me - only 25% of UK home ...
By EtchedPixels , 2 days ago
-
RE: Home automation and the cloud; is there a better way?
Nothing you've said there, @etchedpixels, is something ...
By Majordennisbloodnok , 2 days ago
-
I've heard from others living in the vicinity of Derril...
By Transparent , 2 days ago