Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
MIM-B19M + Homely ?
An excellent summary of my Thermostat options, James.
I will , initially, wait until I have removed the Heat Exchanger ......................now tomorrow !!
My current inclination, for the Thermostat problem, is to initially keep the current Physical Thermostat.
I will then experiment with increasing the Thermostat Temperature by +3 C on my current settings.
I will then adjust , by whatever means, (Field bits 201/202/203 or Water law display 2091 options 2,3 or 4) the Water Law graph hoping to get a stable house Temperature during the day.
But I will Wait until the outcome Tomorrows upgrade before deciding!
Mod-bus
If the removal of my Heat Exchanger , now tomorrow , works .....................I will initially, try and install the MIM-B19N Mod-bus interface as intended some two years ago.
Homely :
I would, if affordable , then install Homely on the MIM-B19N Mod-bus Analyzer .
MIM-B19N fitting ?
My original problem with the MIM-B19N was that it did not physically seem to fit inside my Samsung Heat Pump cabinet in my Garden.
Everything appears to be odd on my Samsung!
Mod-bus RS485 ?
Once installed the MIM-B19?N would transmit on a RS485 Mod-Bus cable.
I would install a RS485 cable from my garden Samsung cabinet to my house.
Homely attaching to the RS485 Mod-bus cable.
Original Mod-Bus Control cables:
The Czech Electrical engineer, employed by my "installer" fitted standard electrical cables between my Samsung Heat Pump in my Garden and the Control box within my kitchen.
When asked "why he did not install the correct RS485 cabling " he replied that "it would make little difference, standard electrical cables would work without a protective Earth Sleeve ".
Three days later the , Czech Engineer announced that he would be returning to the Czech republic because of the "appalling standard of my "installer".
Do I need to replace the standard electrical cable with earth screened rs485 cable?
Ok.
Not sure what the point in the modbus interface is unless you definitely intend to get homely.
You will need to reconnect the thermostat to the demand for heat terminals on the Samsung and check first that it's actually electrically compatible. Traditional thermostats in the UK are 230V whereas most heat pumps need zero volt contacts. I have no idea about the Honeywell, you may need a relay. You could also not bother reconnecting it, all you would lose is the temperature limit function which has relatively little value anyway!
You will need to set 2091,2092. I would suggest to 4 which allows the heat pump to sniff the lwt form time to time to decide whether to switch on or not according to the WC temp setting ( the manual is a bit obscure on this, but I think that is what option 4 is for). Several other of the parameters in the annotated manual I posted will also need to change.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespa...
Not sure what the point in the modbus interface is unless you definitely intend to get homely.
...
...or another third party monitoring and/or controlling device. Home Assistant or OpenHAB spring to mind, but even home-grown python scripts would be able to make good use of the ability to control locally rather than through a manufacturer's portal.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokPosted by: @jamespa...
Not sure what the point in the modbus interface is unless you definitely intend to get homely.
...
...or another third party monitoring and/or controlling device. Home Assistant or OpenHAB spring to mind, but even home-grown python scripts would be able to make good use of the ability to control locally rather than through a manufacturer's portal.
Fair enough, I have the impression that @iantelescope doesn't have that in mind but as you say it's another option. First task is to get the heat pump running as it's maker intended!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
MIM-B19N ?
My original reason for using a MIM-B19N was :
1) to run the internal Diagnostics within the Garden cabinet of the Heat Pump.
The large Clouds of water vapour produced by my Heat Pump raised alarm with my neighbours and , with one neighbour in particular , a large Care home.
I ran both Diagnostics within the Heat Pump itself, with the Heat Pump displaying it's results on a HEX format LCD character display. This in the intense cold of a December morning following a large cloud incident!
2) to determine the status of the de-iceing routines after a cloud producing incident within the Heat Pump itself.
How much power was consumed during de-iceing ?
At What Temperature was de-icing triggered.?
Both of these questions could only be answered with the MIM-B19N interface.
Homely and the MIM-B19N?
Homely is Now advertised as the Solution to Samsung Thermostat problems.
Homely uses the preferred Samsung MIM-B19N interface.
https://midsummerwholesale.co.uk/buy/samsung-heat-pumps/Samsung-modbus-MIM-B19
Many thanks for your Homely recommendation!
Posted by: @iantelescopeHomely is Now advertised as the Solution to Samsung Thermostat problems.
I don't see that in the advert and am not sure what 'Samsung Thermostat problems' you refer to. Homely is really a more sophisticated controller.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Without MIM-B19N How?
Many thanks for your intervention.
How could I interrogate the status of my Samsung and run the Samsung internal diagnostics without a Mod-Bus , RS 485 interface?
The Official interface , the MIM-B19N is £140 ...........
I , usually , have no programming problems.
many thanks
Sorry, @jamespa , Midsummer are advertising the MIM-B19N as THE interface from SAMSUNG to Homely.
https://midsummerwholesale.co.uk/buy/samsung-heat-pumps/Samsung-modbus-MIM-B19
As you, yourself , said , @jamespa
" Homely are reputed to be an excellent Thermostat "
With the addition of a MIM-B19N Mod-bus interface I can examine the performance of both the thermostat and the Heat Pump itself.
as @toodles said , highly recommended.
I was disputing your characterisation of it as 'the solution to Samsung's thermostat problems.' Sofaik there are no problems with Samsungs temperature sensor/thermostat to 'solve'.
Homely isn't a thermostat, it's a sophisticated flow temperature controller, more sophisticated than the Samsung one. That doesn't mean that there is anything wrong with the Samsung one, just that if you pay more you can do better.
Likewise a Rolls Royce is 'better' than a mini (in many circumstances) but that doesn't mean that there is anything wrong with a mini.
Noted that you want to use the modbus interface to interrogate the Samsung, and wasn't aware of that. Perhaps you could also write your own homely. The objective is simple, min flow temp (or cost of you have tou tariffs) to achieve desired comfort level. The challenge is to define 'desired comfort level' and to integrate into the control a forward looking view of the oat (and possibly solar gain).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @iantelescopeWithout MIM-B19N How?
Many thanks for your intervention.
How could I interrogate the status of my Samsung and run the Samsung internal diagnostics without a Mod-Bus , RS 485 interface?
The Official interface , the MIM-B19N is £140 ...........
I , usually , have no programming problems.
many thanks
A bit of miscommunication I think, @iantelescope. @jamespa was questioning what use the modbus interface would be if you weren't sure you'd get a Homely box. I was pointing out that the modbus interface's value would not just be limited to Homely, but also to one of several alternative third party controlling/monitoring systems such as Home Assistant.
Nonetheless, whether you choose Homely or a different home automation system, modbus is the ideal and perhaps only way to interrogate and control your heat pump locally.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Do I REALLY need to remove the HEX ?
To my consternation I have discovered that the Homely installation instructions contain :
Notice the Heat Exchanger in the installation instructions!
Notice the pair of motors etc etc !
My system would appear to be one of many !!
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 135 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 7 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 7 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 7 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 9 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 10 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 12 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 12 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 14 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 17 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago