Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
What do you think of this plumbing software.
https://www.h2xengineering.com/free-trial/
Allegedly calculates Pressure drops , Temperatures , losses from a AutoCAD style front sheet.
If true, just up my street
ian
Posted by: @iantelescopeYes Derek, I agree with you .......... I should have Designed my Heat Pump myself.
External pipe Temperature Sensors?
The Only affordable sensors appear to be K type sensors which attach to the outside of the copper pipes.
This external temperature sensing can be inaccurate if not very inaccurate with the Temperature measurement being the Temperature of the copper , not the water!
Internal pipe Temperature Sensors?
These Sensors appear to be very accurate, judging by my experience with my German "Sharky".
Excellent but completely unaffordable.
How do you measure internal water Temperatures?
ian
The most accurate way to measure temperature would be to use a Resistance Temperature Detector (RTD) such as a PT100, which a fundamental resistance of 100 ohm at 0C. A RTD normally requires a transmitter to convert the resistance value to a 4-20mA or 0-10v dc output.
They are also available in different levels of accuracy.
The actual sensors come in a wide range of sizes and types, I would suggest that you have a look on this website:-
https://www.tcdirect.co.uk/Default.aspx?level=2&department_id=230
Posted by: @iantelescope
What do you think of this plumbing software.
https://www.h2xengineering.com/free-trial/
Allegedly calculates Pressure drops , Temperatures , losses from a AutoCAD style front sheet.
If true, just up my street
ian
Maybe you should suggest that your installer uses this system.
Posted by: @iantelescope
External pipe Temperature Sensors?
The Only affordable sensors appear to be K type sensors which attach to the outside of the copper pipes.
This external temperature sensing can be inaccurate if not very inaccurate with the Temperature measurement being the Temperature of the copper , not the water!
Internal pipe Temperature Sensors?
These Sensors appear to be very accurate, judging by my experience with my German "Sharky".
Excellent but completely unaffordable.
How do you measure internal water Temperatures?
there's a lot going on in this thread but just want to say something on this specifically. This point is not correct IMO.
Affordable pipe (and room) temperature sensing exists for heating systems, and has been done, by many people who are into this monitoring . there is LOADS about this on the openenergymonitor forum, there is no point duplicating the discussion here, please go read that forum or start reading their specs here https://docs.openenergymonitor.org/emontx4/other_sensors.html
I myself have a large setup of DS18B20 sensors monitoring various pipe and room temps (using the easiest install method of taped external metal-to-metal contact to the pipe) and it works well and gives a very usable response time to changes in T, and a very usable accuracy. If you can be bothered to do the plumbing / soldering you can locate it inside a pocket for even better response.
DS18B20's cost about a pound each in 10 packs.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
How would I measure internal water temperature?
I would install a thermowell, into which I would install a suitable temperature sensor, making certain that it had good thermal contact. Depending on the level of accuracy required I would probably use a PT100 RTD.
You of course can use whatever method you wish, and agree or disagree to your hearts content.
hi ian
DS18B20
I have , at the moment , several DS18B20 's attached to the Heat Pump.
These are excellent , but, no reliable pipe clamping system seems to be available.
Several DS18B20 can be used together ...................but each additional DS18B20 decreases the reliability.
DS198B20 's have been copied.
K Type Thermocouples
Clamps with K type thermocouples are readily available .
The K types are faster , but , suffer from voltage offsets at the plugs/sockets.
Data loggers are available for multiple K Type Sensors.
The Copper problem.
With my system, built , such that all the Copper pipes are physically connected to a common copper mass, low frequencies , and DC Temperatures are often identical, with Higher frequencies, however, accurate.
ian
@iantelescope like I said, ds18b20's work for me and hundreds of other people, there is umpteen pages on this in energy monitoring forums. I'm just objecting to your statement within this forum, that "there isn't a usable inexpensive solution to pipe temperature monitoring". There IS. if you don't consider it good enough for your needs, that's a different statement.
clamping wise I use a bit of thermal paste for contact, and then tape it tight. ideally I believe one should use a minimally-stretchy metallic type tape, but a load of winds of bog standard electrical tape does the job for me. there's people out there who've soldered copper pockets to the outside that you can find howto video's of.
I do not understand what you are saying about copper mass , low frequencies and DC temperatures (what is a DC temperature?).
With the DS18B20 sensors in the right place and a device that polls the sensor sufficiently frequently and reliably, you can see the response to a change in flow temperature as the HP comes on, very quickly and clearly, in the primary and the distribution circuits and in individual radiators.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm just objecting to your statement within this forum, that "there isn't a usable inexpensive solution to pipe temperature monitoring".
a £500-700 monitoring system is cheaper than years of paying £500-1000/year extra bills, on thousands of badly installed systems.
Ultimately one can buy it, set their system over 12 months the sell it on the forum, and so on.
Posted by: @derek-mThe most accurate way to measure temperature would be to use a Resistance Temperature Detector (RTD) such as a PT100
I have been looking at these, but they are not easily integrated, so far as I can see, into a (and my) USB connected modbus wired system, because the USB port can only provide 5V, and PT100 analog to digital to modbus converters typically need 6V and more often than not more (eg 12V).
I've also tried to find some data on how well (or not...) an externally measured copper pipe temp correlates with the internal fluid temp (which itself perhaps isn't at a uniform temp, though possibly near enough so to be 'good enough'), but haven't found anything useful yet.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @iancalderbank@iantelescope like I said, ds18b20's work for me and hundreds of other people, there is umpteen pages on this in energy monitoring forums. I'm just objecting to your statement within this forum, that "there isn't a usable inexpensive solution to pipe temperature monitoring". There IS. if you don't consider it good enough for your needs, that's a different statement.
clamping wise I use a bit of thermal paste for contact, and then tape it tight. ideally I believe one should use a minimally-stretchy metallic type tape, but a load of winds of bog standard electrical tape does the job for me. there's people out there who've soldered copper pockets to the outside that you can find howto video's of.
I do not understand what you are saying about copper mass , low frequencies and DC temperatures (what is a DC temperature?).
With the DS18B20 sensors in the right place and a device that polls the sensor sufficiently frequently and reliably, you can see the response to a change in flow temperature as the HP comes on, very quickly and clearly, in the primary and the distribution circuits and in individual radiators.
I have no doubt that DS18B20's work fine as you have described.
I suppose much depends upon what temperatures you wish to measure and what you intend to do with the data collected.
According to the specification, a DS18B20 has an accuracy of +/- 0.5C, so if the objective is to measure the DT between LWT and RWT on a heat pump, the measurement obtained could be between 4C and 6C for a normal 5C DT. If this obtained value is used in the thermal energy output calculation then the end result could be quite different from the truth.
Obviously these are the possible extremes, so it would be hoped that the end result would be closer to the truth.
To help minimise errors, both sensors should be tested together in water, preferably against a known standard, at approximately the temperature of final use. Any differences between the two readings should be noted, and allowances made when reading and possibly offset when used within calculations.
As you have already noted, when mounted externally any sensors should have good thermal contact and be well secured and insulated to minimise errors.
Posted by: @iancalderbankI myself have a large setup of DS18B20 sensors monitoring various pipe and room temps
We may have covered this before, if so apologies: how do you get the DS18B20 data into your monitoring system? I rather suspect the answer is going to involve ESP (electronic not ethereal variety) and HA which as you know I do not have the former, I want to keep things simple, and am not a fan of the latter.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,635 Topics
- 61.5 K Posts
- 232 Online
- 7,032 Members
Join Us!
Latest Posts
-
RE: Debugging my legionella immersion heater
I notice this (66 is rather hot) with my legionella cyc...
By JamesPa , 10 minutes ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
@transparent I thought you would spot that wind turbine...
By Batpred , 40 minutes ago
-
UK warm homes plan - how can it be delivered?
@editor Sobering thoughts on your article on the workfo...
By Batpred , 2 hours ago
-
RE: Setback savings - fact or fiction?
You are right to be intrigued by it IMHO. SOFAIK it is...
By JamesPa , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils there is no logic to oversizing a heat pump. It...
By AgentGeorge , 11 hours ago
-
RE: Vaillant Sensocomfort Time
Thank youy for the pointer. I think I have managed to ...
By ispookie666 , 1 day ago
-
RE: Forum updates, announcements & issues
I have been doing a lot of work on the site lately and ...
By Mars , 1 day ago
-
@majordennisbloodnok good advice, thanks for that.
By David999 , 1 day ago
-
RE: My Grant R290 9kW Heat Pump Installation
I am following this thread with great interest and than...
By TaffontheTaff , 1 day ago
-
RE: Sizing an ASHP; Heat loss and kW
You can't measure heat loss with a website. But you ca...
By JamesPa , 2 days ago
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a — I have a sort of residual interest in this pr...
By cathodeRay , 2 days ago
-
Hi, Thank you. So its a Daikin Altherma 3M...
By Lbart68 , 2 days ago
-
I have a Contactum CU. Would the below RCBO (descriptio...
By Batpred , 2 days ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
@chainreaction Agree with @broadsman , it seems many ...
By Batpred , 2 days ago