Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
Posted by: @cathoderayThe heat pump logic says it is warm outside, so the house needs less energy (only enough to balance the heat loss at that OAT), but in fact the house needs more.
That's exactly what my analysis above would predict. After the rise in oat the bit of the house you live in continues, for a while, to lose energy to the middle of the walls at a higher rate than would be the case in the steady state at the new oat. This continues until a new thermal gradient is established which falls continuously from inside to outside, rather than having a minimum in-between. The heat pump supplies energy corresponding to the steady state at the higher OAT and thus there is a deficit. This is a direct consequence of the fabric thermal mass (heat capacity in scientific terms). I would expect the converse to happen if there is a sudden fall in oat.
My boiler, which had a control loop based on iat, exhibited different, but no less annoying, deviations from perfect control. The problem for the designers of heating control systems is, i imagine, that they don't know the characteristics of the house (which will vary widely) and can't rely on installers or homeowners to dial them in. That's where controllers which learn about the house over a period of time have the edge!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A similar pattern happened again last night and into this morning, low overnight OAT, followed by rapid rise in OAT fooling the heat pump into thinking the house was warm, IAT must be fine when in fact it was anything but, it was actually falling:
I have now written some extra code in my auto-adapt script to detect this and if detected, then add a boost to the WCC end points. I will report back once it has had a chance to run, and can be seen to be working.
Midea 14kW (for now...) ASHP heating both building and DHW
I look forward to seeing the results of your script.
I fiddle with our WC curve increasing/decreasing between 0.55 and 0.75 according to the extent of wind chill. Strong winds and driving rain doesn’t get adequately compensated by WC alone, even on Vaillant’s active mode.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
Posted by: @judithI look forward to seeing the results of your script.
Thanks for your interest. It hasn't really been tested yet. The recent modification to the code was to deal with a rather specific circumstance, a rapid rise in OAT after a cold spell dialling down output prematurely, and that hasn't happened since adding the modification (I suppose a bit like it never rains when you take your umbrella!). What it doesn't (yet) do is deal with wind chill, which we have had rather a lot of recently. The script does do its thing, but it does it assuming no wind chill, meaning it doesn't (yet) do enough auto-adaption.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,676 Topics
- 62.6 K Posts
- 208 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Harvest Thermal - ASHP with a smart thermal battery
As its using ToU tarrifs then its totally believable so...
By JamesPa , 12 minutes ago
-
Why do you want to maintain a specific deltaT? The out...
By JamesPa , 27 minutes ago
-
RE: Heat pump installation quotations
@batpred Excellent, thank you very much!
By sttpd1917 , 57 minutes ago
-
Hopefully this will answer your question. To...
By ASHP-BOBBA , 58 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
I would be interested to find out if others do this and...
By ASHP-BOBBA , 1 hour ago
-
Don't you dare. You just carry on as you are; as @batpr...
By Majordennisbloodnok , 3 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@ragtime27 some rooms in our house only have one place ...
By Judith , 3 hours ago
-
@mkz, that's very helpful. Even if Urban Plumber are no...
By Majordennisbloodnok , 6 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 7 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 8 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 11 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@bash, something we haven't touched on already relates ...
By Majordennisbloodnok , 1 day ago