Hot water heating in parallel with space heating
One of the downsides of most ASHP installations (compared to a boiler) is that they cannot provide hot water heating and space heating at the same time, the ASHP output is either routed through to the DHW cylinder coil, or the space heating loop, but not both simultaneously. So with an ASHP, reading user experiences, this then requires users to block out times when the space heating can be shut-off to prioritise water heating, which isn't ideal. Or when the DHW heating kicks in automatically, the space heating is interrupted.
The different operating temperatures of the ASHP when heating DHW and space heating would make parallel operation, as used with a boiler and regular cylinder impossible because the lower space heating flow temperatures would suck heat out of the DHW cylinder, or using higher DHW temperatures flowing to the space heating would hit the CoP for the space heating.
But that got me thinking, if a DHW cylinder had two coils, a smaller, lower power coil at the very bottom of the tank, and the regular, high surface area/power main coil above it, higher up. With such a configuration, the bottom coil could then be used with the lower flow temperatures used for space heating, to warm/pre-heat the DHW to the lower temperature, with the stratification of the water in the tank preventing it pulling down the temperature of the rest of the tank, while ensuring a steady supply of warm water.
If the bottom coil was plumbed into the ASHP loop before the 3-port valve, so that it was always in the circuit (or possibly with a basic 2 port valve to switch it in on based on tank bottom temperature being below the ASHP output temp) it would provide some continuous heat into the cylinder whenever the ASHP was running, keeping the DHW at a minimum temperature in parallel with the space heating. When the ASHP switched to DHW heating, it would heat both the main coil and the bottom coil to the higher temperature, lifting the whole cylinder to the higher DHW temp.
Is there anything which would stop this from working as intended?
That sounds like an interesting idea. Coil sizes would be a potential issue, perhaps an external heat exchanger could be used instead.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @temperature_gradientOne of the downsides of most ASHP installations (compared to a boiler)...
Its not really a downside of ASHPs, its a downside of using weather compensation. Boilers with WC have exactly the same limitation.
Posted by: @temperature_gradientIs there anything which would stop this from working as intended?
Other than total load I dont think so
Posted by: @bontwoodyThat sounds like an interesting idea. Coil sizes would be a potential issue, perhaps an external heat exchanger could be used instead.
An external heat exchanger would need a pump which would be likely to disturb stratification. Cylinders with multiple coils (eg ones with a solar coill for solar thermal installations) are available!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @temperature_gradient
An external heat exchanger would need a pump which would be likely to disturb stratification. Cylinders with multiple coils (eg ones with a solar coill for solar thermal installations) are available!
Thats true, in fact my old thermal store had a solar coil at the bottom and a splarge pipe in the middle/top. Might be ideal for this sort of use if I still had the house and was running the heat pump without antifreeze as I do now!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 177 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 22 minutes ago
-
RE: Running from backup generaor in powercut?
Definitely and professionals sometimes miss it. I had...
By Batpred , 27 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
@batpred Well, I'm running the eBus interface and integ...
By dr_dongle , 2 hours ago
-
RE: Setback savings - fact or fiction?
That´s an interesting point. The combi that we have is ...
By Batpred , 2 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Hi @green_fox As a we have a PUZ-WM80VAA with FTC7 (...
By RobS , 3 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 5 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
@jamespa Thanks very much for this, and for mentioning ...
By anotherdaveuk , 5 hours ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 5 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
The Regulations specify the export limits in Amps. If...
By Transparent , 5 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hope your issues are sorted out soon. We have ...
By ChandyKris , 5 hours ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 9 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 9 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 10 hours ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 10 hours ago
-
RE: Heat pump not reaching flow temperature
is the house warm enough?
By davidnolan22 , 15 hours ago
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 16 hours ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 16 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 1 day ago
-
RE: Air source heat pump circuit not operational
Welcome to the forums. If the thermostat shows it’s c...
By Mars , 1 day ago