Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@webcmg Silly question, but this happened to my system. Are you sure the ASHP is not trying to heat the water and the house at the same time? During the cold spell last year I was pushing 95kWh per day. Having fixed that problem (not the only one we have) the usage during the current sub-zero temperatures is now around 55kWh per day.
I don't know if it is true of all installations but ASHP's are often specified with a capacity to do one or the other but not both. If you call for both space and hot water heating at the same time they just demand ever more power in a fruitless effort to meet the demand.
If that is the issue then it's one of the easier ones to address.
Mike
Grant Aerona HPID10 10kWh ASHP
Hi @webcmg
I have a 5KW arotherm plus unit installed as a part of a hybrid system in my old and fairly leaky property (163m2, D rated semi detached sandstone house ~ 1900). No upsized rads etc. The way my system is setup, it currently defaults to running off Gas almost 100% of the time as this is the most cost effective fuel source, however, being nosey and wanting to see how the system would manage on only the ASHP over the Christmas period, I decided to deactivate the gas boiler and have it run solely from the ASHP for a couple of days. Granted, outside temperature was mild for this time of year, but to heat the house to 21°C for the 2 days, using what would likely be considered an undersized pump for the house used 22kwh one day and 28kwh the following, so substantially less than your usage. I must admit I was very pleasantly surprise how well it performed, the house was a lovely temperature! 🙂
Obviously this is a different setup than yours, and I don't have the controller settings to hand (it is the Vaillant sensocomfort we are using), but if they would be useful, I will dig them out tonight and post. In a new build like yours I would have thought you would be able to achieve better than you are getting for sure.
Edit: Just saw Mike Patricks reply, I should have added my system relies on the gas for DHW, so that will also be reflected in my lower elec usage. not sure by how much though!
Posted by: @webcmgPosted by: @derek-mHi @webcmg
Look at pages 15 and 16 in the manual kindly provided by SPDTDL. Try setting the weather compensation curve at 0.6 or 0.8.
Done, assume this is the same as heat curve? Changed to 0.6 for now.
Have you noticed any difference in energy consumption? Are you certain that your system is set for weather compensation control and not fixed water flow temperature?
You ask:
“Is it correct for the weather compensated system control to be in the insulated area of the garage?”
the answer is, it depends (!).
in Germany since 1985 the requirement on a boiler is that it has an out door sensor. This is relevant because heat genrtator controls have become sophisticated around this. (There are other reasons why this is the case, but that’s a bit if a rabbit hole)
in this case this controller will work well with no indoor reference, just on the outside temperature.
so if it’s commissioned correctly it will be fine…
Professional installer
Posted by: @mike-patrick@webcmg Silly question, but this happened to my system. Are you sure the ASHP is not trying to heat the water and the house at the same time? During the cold spell last year I was pushing 95kWh per day. Having fixed that problem (not the only one we have) the usage during the current sub-zero temperatures is now around 55kWh per day.
I don't know if it is true of all installations but ASHP's are often specified with a capacity to do one or the other but not both. If you call for both space and hot water heating at the same time they just demand ever more power in a fruitless effort to meet the demand.
If that is the issue then it's one of the easier ones to address.
Mike
@mike-patrick thanks for the message - how might I check if this is the case?
Posted by: @derek-mPosted by: @webcmgPosted by: @derek-mHi @webcmg
Look at pages 15 and 16 in the manual kindly provided by SPDTDL. Try setting the weather compensation curve at 0.6 or 0.8.
Done, assume this is the same as heat curve? Changed to 0.6 for now.
Have you noticed any difference in energy consumption? Are you certain that your system is set for weather compensation control and not fixed water flow temperature?
Hi @derek-m, I made the school boy error of not noting down the Kwh usage before changing the settings. I took an energy consumption reading earlier today so will check tomorrow. We've also had work people in the house so had windows open due to covid so hopefully we can get back up to temperature and monitor properly now having turned off the zones they were working in. One thing that doesn't make sense to me is the use of UFH downstairs and radiators upstairs. My target flow temp is around 32 degrees, which maintains a 20c temp downstairs, but this doesn't seem sufficient to provide enough heat for the radiators upstairs. Is the combined use of UFH and Radiators common? If so, how is this differential heat requirement efficiently overcome?
@webcmg in the first best world you would have an electronic mixer controlled by a vaillant wiring centre for the floor and two heat curves..
Professional installer
@webcmg I was afraid you would ask that!
The way this is achieved varies from one make to another. I have a time switch like you find on conventional heating systems that controls the times when the hot water is on and separately the space heating. You just set those times so that the space heating is off when the water heating is on.
But I know others on this site, who are much more technically informed than me, will offer other suggestions.
I'll be interested to learn what you find.
Mike
Grant Aerona HPID10 10kWh ASHP
@mike-patrick it might seem to you there are choices of approach, but for for optimum performance of the heat pump and vrc700 you really should select and install the components as they indicate in vaillants schematics.
I don’t know why installers and specifiers think they know better that vaillant design engineers!
Professional installer
Posted by: @alec-morrow@webcmg in the first best world you would have an electronic mixer controlled by a vaillant wiring centre for the floor and two heat
@alex-morrow our UFH zones have a manually set mixer (currently set to 50c - so largely redundant), if these were set to 22c or somewhere in that region would that help? Based on the suggested settings today's target flow temp is 33c, so assume the efficiency would be lost due to having to significantly increase flow temp. I assume this is why an electronic mixer and two heat curves would be best so it can fluctuate the heat flow as required? Does anyone run a similar setup with upstairs radiators and UFH downstairs without the electronic mixer?
I spoke to the plumber who setup the pipework today, he didn't really know anything about about ashp- but just said the 33c flow temp won't be enough to heat the upstairs radiators. I worry that the design of the ufh and radiators is not optimal for a heat pump.
Hi @webcmg
Check to see if any of the valves are partially closed on any of the radiators.
Check that your water pump is producing adequate pressure and flow to get the water up to the radiators. Try measuring the temperature of your radiators and then shutdown your UFH so that all the flow is going to the radiators. If the temperature of the radiators starts to increase then you have a pressure or flow problem. Try increasing the pump speed.
Posted by: @webcmgPosted by: @alec-morrow@webcmg in the first best world you would have an electronic mixer controlled by a vaillant wiring centre for the floor and two heat
@alex-morrow our UFH zones have a manually set mixer (currently set to 50c - so largely redundant), if these were set to 22c or somewhere in that region would that help? Based on the suggested settings today's target flow temp is 33c, so assume the efficiency would be lost due to having to significantly increase flow temp. I assume this is why an electronic mixer and two heat curves would be best so it can fluctuate the heat flow as required? Does anyone run a similar setup with upstairs radiators and UFH downstairs without the electronic mixer?
I spoke to the plumber who setup the pipework today, he didn't really know anything about about ashp- but just said the 33c flow temp won't be enough to heat the upstairs radiators. I worry that the design of the ufh and radiators is not optimal for a heat pump.
Hi,
If after checking the pump operation you still cannot get the correct temperatures upstairs, then change the weather compensation curve from 0.6 to 0.8.
-
How Accurate Is My DIY Heat Loss Calculation?
1 week ago
-
Surface mount or bury primaries for heat pump installation?
1 week ago
-
Issue with Samsung Cascade System
1 month ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
2 months ago
-
Design Of Cascade System Replacing Undersized ASHP
2 months ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,767 Topics
- 65.1 K Posts
- 842 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Next steps on my ASHP journey: Radiators and Pipework
If you are considering phasing the project, then I woul...
By GrahamF , 4 hours ago
-
RE: Siting of the external sensor on a heatpump
Of course had the heat source been a heat pump it would...
By JamesPa , 6 hours ago
-
Never assume, it makes an ass of u and me! OK, tha...
By JamesPa , 6 hours ago
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
In fairness all heating has cost a lot to run in recent...
By JamesPa , 8 hours ago
-
RE: Is it the house or the equipment?
@springswood We have two Daikin single split A2A syst...
By Rob of York , 9 hours ago
-
RE: Navigating the World of Refrigerants In Heat Pumps: A Guide for Homeowners
Indeed we are invvestigating AC at present and are havi...
By Toodles , 1 day ago
-
No, but the heat pump must be capable of delivering a S...
By JamesPa , 2 days ago
-
RE: Daikin ESPAltherma and Home Assistant installation
It's laziness lol The PV system is very chatty, meter...
By bobflux , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 2 days ago
-
RE: Vaillant Arotherm Plus 7KW need a service on it
booked it with Vaillant. will use them until i can find...
By AdamK , 2 days ago
-
RE: Adventures in heat loss calculations
I have seen it stated that the declared calorific value...
By JamesPa , 3 days ago
-
RE: Two heating zones to one zone
@transparent Many thanks. The garage is fairly well ...
By Profzarkov , 3 days ago
-
RE: Vaillant Aurotherm - Heater Wire Position
Ah, good point. I need to check if this was installed i...
By Batpred , 4 days ago
-
@batpred thanks for getting a copy. Appreciate the supp...
By Mars , 4 days ago
Members Online
No online members at the moment