Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@agentgeorge Fortunately the one thing that you *won't* need to worry about is the wiring because there is hardly any! The eBus board has a socket on it and comes with a detachable plug that takes two wires (+/-) - you attach that to your eBus, plug in the board and you're good to go. + and - should be marked and the documentation claims that getting it wrong won't fry anything but I've not put that to the test. The board then broadcasts its own little WiFi network (SSID), you attach to that and a Web page should come up (if not then the IP address is in the documentation) and you can set parameters, the main one of which is to give it an IP address on your home network (static or DHCP). The firmware should be perfectly good enough to kick off with and once you have done that then once rebooted it'll be broadcasting eBus packets to your network till you unplug it.
What follows assumes that you are running HomeAssistant (HA). Unless you bought a pre-installed and configured HA box then, again, you'll have at least passing familiarity with Linux.
At this point you can telnet to the eBus card on its IP and port and all being well you'll see a load of digital junk coming back at you.
You next need to download and install an eBus daemon (software that runs permanently listening for stuff) called ebusd within the HA machine and tell it the IP address of the eBus card. This then catches the eBus traffic from the board, tidies it up a bit and looks for somewhere to send it within HA. A common way of handling that is to install an MQTT daemon in HA, another piece of software that runs permanently and is part of the MQTT integration for HA and handles messages from other software. Here, MQTT knows how to deal with ebus packets (I'd need to check where it got told this, possibly when the ebusd daemon was installed) but a collection of ebus devices and entities should then appear in HA which can be built into cards and histories.
Most integrations are installed in HA simply by selecting them from a table. The more experimental and niche ones are made available in collections like GitHub and appear in a separate HA collection called HACS.
I think my main problem with the documentation was that it gave you lots of detail but omitted the one thing that was so blindingly obvious to the writers and readers that they didn't mention it and without which nothing else made any sense. A lot of the time after extensive research I would come back to the original documentation and think. "Oh, so *that's* what they meant".
I am *not* going to claim to be an expert in this august company 🙂 and anything I have said may have been overtaken by newer and easier ways of doing it but I can help avoid some blind alleys.
There is or was a separate way into the Vaillant data via an integration called MyVaillant or MyPyllant. This, though interrogates the Vaillant servers and needs to be used with caution since it can flood them at which point you'll be suspended for an hour or two before it replies to further data requests.
Hope this helps and is mostly accurate!
Posted by: @agentgeorge@simonf no sensor is accurate unless calibrated, I ran the calibration cell in the test laboratory at Gaydon Proving Grounds for a few years; everything had to be +\- 0.1C at 20C stabilised for 1h with the test engineer in the cell, as entering the cell affects the calibration as the human acts as a heat source.
It makes me smile when I read posts on here with stats of room temperatures as 21.5C, without a tolerance and calibration certificate its meaningless and is just a random number.
I agree and that’s why I don’t believe a lot of the high COPs that get reported on Vaillant units.
It’s a shame Vaillant don’t calibrate the sensors. When I had them out to replace mine the Vaillant engineer had to go through 3 different sensors to try and get a pair which matched. They had no process for testing or calibration.
@adamk I'm observing my own system at low temperatures and it was useful to compare it with your history and some "Should my system be doing this?" posts. I have a 10kW Vaillant AroTherm Plus running as a hybrid with a buffer tank and a small backup oil boiler. Switch-over is at a bivalent point currently set at -2 C. Temperatures here since 1 January have been varying between +4 and -6 C and mostly below 0. Significantly, relative humidity was in the low 90s between Christmas and New Year, dropped to the mid 70s until a couple of days ago and is currently around 96% (Central Scotland isn't known for crisp snowy days). The correlation with defrost cycles is striking and I'm seeing one about hourly just now. When ambient temperature was below -2, the boiler cut in. Its thermostat is set to minimum (50-55C), applied in short bursts so held the buffer tank at pretty much the usual temperature of about 44 C. Once the temperature rose above -2 the boiler shut off and the buffer tank temperature can be seen to sag to 41 C between defrost cycles. It has now gone a bit high but probably temporarily. The difference between ASHP flow and return (and that to/from the radiators) is about 5 C. None of the temperature values are calibrated 🙂 but are a mean of multiple sources where possible (I'm reading eBus - see post and I installed other pipe sensors and temp/humidity gauges). I interpret this to mean that the system is beginning to feel the squeeze and trying to maintain the temperature between high demand and frequent defrost cycles but that the oil boiler is doing what it was put there to do. This house was practically designed to radiate heat despite my best efforts. I calculated a SCOP from the Vaillant app figures and for 12 months from 1 June 2024 I'm getting about 4.75 +/- 0.25. Right now it is telling me 3.2 for the last week.
ive got the installer coming Monday to fix an isolation valve the previous engineer damaged by not installing the strainer retaining ring in the right position. ive also got an issue where the hp pees over the path when doing a defrost even though it has a soak away, hopefully just some rubbish in the drain pipe blocking it. ive also asked them to sort the sensors as i have a 0.5c+ discrepancy between flow and return, though they said if Vaillant come out they might charge £98.
@agentgeorge if it is i need to somehow tweak it to match as its confusing the heat pump. 0.5c apparently skews the cop by about 25% up or down depending on the pipe the sensor is on.
So it seems probably most of the issues I’ve had are down to bad flow and return sensors. With them swapped around I’m now getting what I can only assume is an over inflated cop. What it has done as well though is to now show a clear separation between hot water and heating cop with heating now beating hot water.
what I don’t get though is in one position the gap is about 0.6c but when swapped it’s more like 0.9c. I wondered if one sensor was reading cooler and the other hotter so when swapped the gap is greater, or maybe some issue with the wiring. I’m now waiting for the installer to sort out how I get get 2 matching sensors that are at least close to a calibrated one.
@adamk In my experience the gap widens when the outside temperate increases, so could be that. Or maybe just down to the way the swapped sensors have been installed. With them being clip on sensors, the exact placement and way they are installed makes a difference. i.e. if thermal grease was used on the probe, if the any of the pipe insulation is in contact with the sensor. Hopefully your installer will get lucky and find some matching sensors.
@simonf I did try swapping them twice and in both cases the gap increased by 0.2 to 0.3 compared to the shipped position error of 0.5/6.
ive tried cleaning the pipe and sensor tip and it didn’t seem to make any difference.
what I could do with is a calibrated sensor and then a pile of these to find a good pair.
Posted by: @adamk@simonf I did try swapping them twice and in both cases the gap increased by 0.2 to 0.3 compared to the shipped position error of 0.5/6.
ive tried cleaning the pipe and sensor tip and it didn’t seem to make any difference.
what I could do with is a calibrated sensor and then a pile of these to find a good pair.
Its almost surprising that ASHPs don't feature a 'sensor calibration' mode. Absolute accuracy isn't that important, but relative accuracy affects measured COP so is. It wouldnt be beyond the wit of man to have an offset somewhere, which could be calibrated by swapping the sensors or just switching off the compressor so that flow and return are (more or less) at the same temperature
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 1,034 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 36 minutes ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 3 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 4 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 6 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 7 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 7 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 10 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 10 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 12 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 12 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 12 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 13 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago