Replacing oil heati...
Replacing oil heating in a 1600s cottage. Is a 12 kW heat pump enough and what should it cost?
7 Users
5 Reactions
(@eccentric-sushi)
Considering a heat pump
New Member Member
Your energy: 29 kWh
@jamespa Thank you. Do you know anyone who might do this around Buckinghamshire?
(@eccentric-sushi)
New Member Member
Your energy: 29 kWh
@jamespa Thanks for the input.
Valliant aroTHERM plus 12kw is being proposed, along with Grant HP R290 155 if we want the 15.5kw.
Floor loss calculations - I've used 0.30 W/m²K (retrofitted floor insulation). Do you think this is too much?
Did the window area definitely get subtracted from the wall area? Yep.
(@eccentric-sushi)
New Member Member
Your energy: 29 kWh
@rob-of-york  Thank you for the input.
0.5 would be significantly lower than modern homes historically. Not sure I agree with that approach. What would you be putting in to your heat loss calcs? I might go down the route of a pressure test if deemed valuable, but the outcome will not significantly change the cost of the heat pump (difference between 12kw and 15kw seems to be under £1k, which is marginally higher than the cost of the pressure test), so is it worth doing?
Thermal bridging - did think about this but decided this was tinkering at the margins and so left it. There should be sufficient margin in the calculations hopefully to compensate for this.
(@eccentric-sushi)
New Member Member
Your energy: 29 kWh
@old_scientist Can I ask what insulation exercise you carried out? We definitely wouldn't be able to get uPVC! Wooden windows (£££) are the only option for us unfortunately.
Really useful to know your over-spec isn't costing a significant amount (albeit maybe 10% higher running cost by the sound of things, with additional headroom in case things go wrong).
Your energy: 133 kWh
Posted by: @eccentric-sushi
If you mean a pressure test then no, sadly.  Sorry
Attached the detailed specs for the Vaillant (in Czech unfortunately).  I dont have the From the table on p44 it will do 14.7kW at -2/35.  However there is some fairly convincing evidence that Vaillants measurements are made for a central european climate, which because its colder and drier, is more forgiving of the effect of defrost.  In the UK which is damp, defrost really matters (a) because it happens a lot and (b) because you are designing for a temperature bang in the defrost window, not a much lower temperature.  The upshot of this is that you probably have to derate 10-20% which brings it back to 12kW.
Unfortunately I don't have the equivalent information/data for Grant and I am not sure if they even publish it.  This is one area where Mitsubishi score, they publish very comprehensive data and its in English!
I honestly dont know.  The difficulty is that the perimeter matters as much as the area, and the ground is not at OAT its typically at 10C.  Any tool that does not include both perimeter and area is suspect. Here are links to some tools (found by AI) but I havent checked them, although I have used the last of them for general U value calculations.
.  Perhaps also compare with what your installers have calculated for heat loss
Your energy: 26 kWh
@eccentric-sushi — despite having been a few years ago in the same position that you are now, changing from oil to ASHP, I have little to add to the excellent advice you have already received.
The little I would add is
(1) to underline again that fact that calculated heat losses are totally dependent on their assumptions (which is why I call them whatiffery - they are just a bunch of 'what if' calculations). The obvious conclusion is you have to be very careful with your assumptions, and be brutally honest about when you don't know what the correct value is.
(2) one way of independently checking heat loss calculations is to use past fuel consumption. This is easy enough with gas, but very hard with oil, because of the way we buy it, and the crude ways we measure what is in the tank. However, I have in the past wondered if it might be possible to estimate oil use over short time frames by recording running times, based on the fact oil boiler nozzles deliver a fixed rate of oil over time. If you still have the oil boiler and can run it, it might be worth getting it to run at a low flow temperature, ideally low enough to mean it is on most of the time, and then estimate how long it is on for over say 24 hour intervals. You can then do an empirical heat loss, on the basis that when the house is in steady state (steady room temp), then the current heat loss is the current heat energy being delivered to the house. We can expand on the detail of how to do this if you are interested and are able to give it a try.
(@rob-of-york)
Your energy: 11 kWh
@eccentric-sushi
I used 0.5 ACH for my house, but then it is a 1970s detached with all the retrofit insulation that I could reasonably do as well as uPVC double glazed doors and windows. The overall calculated heat loss came out close to the one that I worked out empirically from a large number of individual days gas usage and average indoor and outdoor temperatures, which gave me some basic confidence that the ACH value assumed was about right. It's written up in this thread:
https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/adventures-in-heat-loss-calculations/
Based on your figures, I think thermal bridging comes out around 1600W (total area of building components x 23.5 x 0.15), which is roughly 10% of the total, so not entirely insignificant.
How the U-value for your floor is worked out depends on whether it is a solid floor, or a suspended one (e.g. floor boards).
With a solid floor, it is the perimeter that matters, and there is a fairly complicated formula for working it out in section section 5.12 of the rd10SAP specification.
For suspended floors, the depth of insulation matters. For example, my house has floorboards with 150mm of Rockwool insulation suspended under them and then an air gap of about 45cm to the ground below. The U-value is 0.22 for that. A U-value of 0.3 would be correct for 100mm of insulation, and 0.5 for 50mm. (Values from section 5.13 of the rd10SAP spec.)
(@old_scientist)
Samsung
Your energy: 34 kWh
Roof spaces were insulated to modern standards using regular loft insulation. We have some vaulted ceilings with no loft space above. Some had minimal infill fibre insulation between the rafters that had mostly slipped down, and others had none. We insulated these ceilings internally with PIR backed plasterboards, and internal wall insulation using PIR backed plasterboards was also fitted to the old stone part of the cottage (which limits the thermal mass of those walls but has made them significantly warmer). Newer parts of the property (extensions) have cavity wall insulation.
It's not possible to estimate how effective those measures were as we switched from oil to ASHP at the same time as most of the insulation upgrades were done so no comparison data for before and after.
Overall we are REALLY pleased with our ASHP. The house is so much more comfortable than when we were on oil, we don't have a smelly oil tank in the garden and trace smells of oil in the house around the boiler, it costs a fraction of the price to run and is far quieter. The only downside is the wife would like the hot water a little hotter as we only heat it to 45C in winter and 42C in summer.