Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Grundfos Secondary Pump Flow Rate
I've 2 x 12kW Samsung heat pumps operating as master/slave each pumping a constant rate of 26l/min into a buffer tank, ie input flow is either 26 or 52l/min depending if one or both units are operating.
I've not really looked at what the heating circuit pump is doing tbh, the installer never mentioned anything about it and I just left it as it was. It's a Grundfos UPS 2 15-50/60 (pic and characteristic curve attached) that was set at position I.
I've no idea what the system head is (static lift around 2.7m with 14 rads, not sure of pipework) but leaving the pump on the lowest setting intuitively doesn't seem right, especially as flow into the buffer tank can vary by a factor of 2. Anyone any idea what I should expect to see here.....?
Thanks
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
static head isn't relevant, the water goes round in a circle, what goes up must come down. What matters is the resistance to dynamic flow. Given that you have up to 24kw of heat input at 56l/min, into your buffer, you need to move that much heat out of the buffer through the rads: flow needs to try to match the input side.
I can pretty confidently say, that circulating pump is nowhere near enough.To hit 56l/min (2.8m3/h) your dynamic head would have to be less than 2m with that pump, which is highly unlikely for a 14 radiator sized house (unless possibly the radiator side pipework has already been highly optimised / rebuilt.)
suggest you think about:
- what is the pipework layout and sizing on the secondary side? draw it.
- get a heat metering setup installed on the secondary side to actually measure what you are getting through
- as a "can't make it worse, could make it better" - with zero plumbing changes: buy the most powerful circulating pump that you can find (And afford) that fits into the same space (thus making the swap trivial). it looks like a 130mm. then see what you get.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Thanks @iancalderbank, that's helpful and good shout re the bigger pump. I'll look into that. I might need to start lifting a few floorboards as well!
Whilst I might have 24kW of installed capacity, the reality I've seen is nowhere near that. I've been keeping records of heat generated lately and, even in this recent really cold spell, it's only been managing 10-11kW (and that's with master/slave operation). Frequent defrost cycles mean LWT never reaches it's set point but gets stuck around 43°C ish, and that ends up a few degrees lower by the time it's been through the buffer as well.
It's been able to keep the house comfortable and stable at around 18°C so in that sense it's working and has given me a good indication of my heat loss with OAT well below zero. I still feel there's a way to go on my efficiency journey though......
Simon
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn FWIW, I was running at about 9kw also on saturday (-2C here all day), flow rate of 28l/min , that kept us at 21C inside . pretty sure that is my circulating pump going flat out. I use a UPMM 25-95 130, 8.5m head at 28l/min.
you could also look at a UPML 25-95 130 which doesn't drop below the 9.5M head until about 40l/min.
surveying the pipes / valves is important too, if there are thin ones, it'll be harder to get the flow rate up just by adding more push.
it does sounds like having read your other posts, your 2x12 setup makes for hard work.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Thanks @iancalderbank. You're not wrong about the hard work. We clearly don't need 24kW but have made some improvements to the house since the system went in so the heating calcs (which I presume exist but have never seen) may have been right once.
The way the master/slave set up works on the Samsung doesn't seem helpful to me. I wanted the slave to come in to support at OAT below 2°C (which I can set) but the trouble is when the master goes into defrost (or into DHW mode) the slave switches off too! So, at the very time when the extra help is needed it switches off, which means the value of the second unit is diminished. Anyway, that's a whole other story. In hindsight a 16kW unit and no buffer tank may well have been a better bet but we are where we are!
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn would it be feasible to individually control your two units rather than rely on samsung's master slave behaviour?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Yep, they both have separate controllers (currently linked) but can be reconfigured to run individually, controlled from a single run signal from the thermostat, a Hive in this case. I was going to get my installer to sort this when they come for the annual service in Feb but may bring forward. I don't want tandem running all the while though, really I just need to switch the second one on at end Nov and switch off again in Feb - one unit is more than capable the rest of the time.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn I was just pondering a possible idea for you: you could take control of each heat pump individually via modbus, run them as 2 separate rather than a linked pair. By control I mean setting the value of run / don't run, setting target temp (either IAT or LWT depending on mode). Modbus will tell you when its in defrost mode, along with the temps and flow rate. It might then be possible based on that data as input, to write your own control loop that keeps them in antiphase. (I'm assuming you've done to death with samsung why they stay in phase with the controllers linked and it can't be resolved).
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Joule Samsung have just told me it's not possible to alter the 'slave' to remain on whilst the master goes into defrost. I thought though, if set up in tandem operation, it's perfectly possible for the second pump (heat only) to continue running, while the first pump (heat and DHW) is in a defrost or in DHW mode as they both separately feed a buffer tank.
I don't have the modbus modules fitted so that's £400 for a pair for starters, plus fitting, so I was going to try and get the simple conversion to tandem running done first and see where that gets me. I'm not into coding so may well end up going down the Homely route to get this working better without my endless fettling.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn yeah it should be perfectly possible to treat them just as independent heat sources, decouple the master-slave, if send them both a call for heat, they'll of course both run. you'd be relying on an element of luck that they don't go into defrost mode at the same time. I was trying to find a way for you to make it "better than relying on luck" but as you say if you don't have the modbus modules there is an outlay there.
one very simple idea that might work (after you've decoupled them and they are running as seperate heat sources) that requires no coding:
- connect the output 230v of your thermostat to the input "run" terminal of HP1 controller.
- also connect it to an on/off switch (this is the master for HP2 use / no use).
- then connect from the output of the on/off to a push button timer - has to be one that breaks rather than makes the connection - timed for X minutes. where X is at least the length of a defrost. output of the push timer to run terminal of HP2.
- If you detect by observation they are in phase : go press the button. delays run signal to HP2 for X minutes. should hopefully get them out of phase.
homely will require modbus by the way and you'd need to ask them if they can control two heat pumps.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks, that's really helpful!
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
Posted by: @iancalderbankI can pretty confidently say, that circulating pump is nowhere near enough.To hit 56l/min (2.8m3/h) your dynamic head would have to be less than 2m with that pump, which is highly unlikely for a 14 radiator sized house
Hi @iancalderbank. I've done some (crude) monitoring today with the system stable, looking at heat being generated and measuring secondary side flow and return. This yields flow rates between 17-21lpm for my Grundfos, depending on which setting it's on. So, less than even with a single heat pump running (26lpm) but when both are pumping into the buffer this means most inflow is effectively just mixing and being recirculated back! I'm sure this must be acting to throttle performance so the 'benefit' of the second pump is severely limited. Happily, the house has remained comfortable, just, but I'd like a bit more headroom!
The Grundfos pump curve says delivery head is around 4.5m at 21lpm so getting to 56lpm would mean a massive, and impractical, increase in head, without upsizing a load of pipe. Getting to 30lpm would probably need about 9m of head so may be a sensible aim and should allow a comfortable margin of kW transfer.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 286 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago