Ecodan high pressure at 3 bar
We have a Mitsubishi Ecodan with UFH downstairs and radiators upstairs. The pressure at the water tank is 3 bar.
I have lowered this by bleeding water from the radiators to 2 bar as indicated by the fixed red marker on the pressure gauge.
This has gone back up to 3 bar and there is water coming from all the radiator bleed valves when opened so no air in them it seems.
We have had 2 new towel rails replacing cheap old ones. Not sure if this has anything to do with it.
Any advice on how I can resolve this issue and what might be causing it?
Andy
Something similar happened to me once with a gas system boiler. The filling loop hadn't been closed properly and it was pushing up the pressure over time. You might want to check that.
Posted by: @dorkyparkThe filling loop hadn't been closed properly and it was pushing up the pressure over time. You might want to check that.
That's a good reason to disconnect the filling loop when not in use, in the way that it is designed for!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi thanks for that, I'm not sure if I'm correct but I seem to remember having to open a valve to add pressure to the system. Would this be the valve that you mean? It was fully open and I've now closed it.
Yes, you would need to reduce the pressure to the correct value for your system (usually 1 to 1.5 bar when cold).
And as @jamespa says, disconnecting the filling loop when not used is the correct thing to do.
@sand I far as I am aware, all systems have two of these valves (one on each side of the mains feed to the red tank; these should both be shut off after any adjustment to pressure. (I may be wrong but all systems I have come across have the two valves and plumbers have told me they should both be shut after adjustments are complete.) Nervously, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodles@sand I far as I am aware, all systems have two of these valves (one on each side of the mains feed to the red tank; these should both be shut off after any adjustment to pressure. (I may be wrong but all systems I have come across have the two valves and plumbers have told me they should both be shut after adjustments are complete.) Nervously, Toodles.
You are correct, but they also come with thumb-turn fittings so they can be disconnected easily. On mine at least its necessary to do this to be sure that the shut off valve is truly shut off.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,418 Topics
- 54.8 K Posts
- 280 Online
- 6,098 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Say hello and introduce yourself
@mrfield, welcome to the forums. Please go here and ...
By Mars , 17 minutes ago
-
RE: Daikin Wireless Thermostat
Our Daikin is due to be installed next week. Today i...
By Bash , 58 minutes ago
-
RE: Reliable, easy to use home battery options
Clearly aware we are talking about safety here. But a s...
By Batpred , 59 minutes ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
@ashp-bobba Thanks for the reply. Would it not work ...
By Patch321 , 1 hour ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
I did not hear back from the tech team. (Assume they ar...
By swwils , 2 hours ago
-
RE: How to use my Hanchu battery storage for home without it feeding back into the grid?
Hi. My Hanchu battery system is controlled by the (Lux...
By SKD , 4 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa thank you again. Apologies I missed you pointi...
By MairiA , 4 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In the Home Assistant firmware the data points...
By F1p , 15 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@johnbroome if it is not the pressure in the expansion ...
By ASHP-BOBBA , 15 hours ago
-
So I hear the export MPAN that UKPN assigned should be ...
By Batpred , 18 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
From what I read, the Solis has a very long list of err...
By Batpred , 18 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Roughly this should cost you £250-£300 per peak month a...
By ASHP-BOBBA , 19 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@toodles Thank you for your input. As the days have got...
By Synthbuilder , 23 hours ago
-
RE: Fan unit Making terrible noise HELP!!
@gutoffowc Oh no, sorry to hear that, are you in the Ke...
By ASHP-BOBBA , 1 day ago
-
RE: Sunsynk Whole House Backup Issue
@sheriff-fatman - could you please re-post that in the ...
By Transparent , 1 day ago
-
RE: Running my new Nibe ASHP efficiently
I didn't. I spent a while manually messing around with ...
By jamieheatpumpnew , 1 day ago
-
RE: I’m glad the cold spell is over!
I comparison with the 65kWh used above yesterday was on...
By Judith , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
I should think so, I thought that pretty much universal...
By JamesPa , 1 day ago
-
RE: Setback savings - fact or fiction?
I'm also inclined to look into how a defrost is actuall...
By cathodeRay , 1 day ago