Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen here. Uninsulated buried primaries!, uninsulated pipework around the cylinder, system separation, oversized heat pump, undersized radiators and doubtless some things we don't know about because they are masked.
The plumber who 'installed' this should be struck off! It's almost like they designed it not to work, but I doubt they were that competent. The lack of insulation would be equally bad if this were a boiler installation (worse in the case if the dhw tank, because it would be heated to a higher temperature), how were they ever let near this job. It makes one wonder about the rest of the plumbing.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Mitsubishi Ecodan not good enough ?
3 months ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
4 months ago
-
Mitsubishi Ecodan circulation pump running.
4 months ago
-
Ecodan Auto Adapt Options
4 months ago
-
Ecodan heat pump leak
4 months ago
Currently viewing this topic 4 guests.
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,477 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 1 hour ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 15 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago