Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Compensation Curve Minimum Temp 25 Degrees
My Ecodan doesn't seem to allow me to set a compensation curve that will drop flow temp below 25 degrees celcius. In essence at 10 degrees outside I want all heating turned off with normal DHW function. Is my only option to turn off heating completely? I Assume I'm missing something; I can only find oblique reference to the 25 degree lower limit on the Web.
Any advice would be very much appreciated.
Well, generally a heating system is controlled by demand rather than another parameter. Even if you could lower the compensation curve further it would still be running – but I suspect it would become less efficient trying to put so little heat in.
However, in the controller settings you can find Service Menu > Operation Settings > Summer Mode, which is set to Off by default. But you have the options to set Heating On (4—19°, default 10°) and Heating Off (5—20°, default 15°) temperatures for ambient temps, and Heating On and Heating Off Judgement Times (both 1-48 hrs, default 6). These aren't explained anywhere, so perhaps a call to the Ecodan support line is in order, but I would presume that the temps are just setting on below/off above values with a hysteresis to allow it to run for a while and the judgments perhaps set a minimum time it has to be below temp before the heating is actually run, and a maximimum run time for while it is operating below the off ambient temp, after which it turns the heating off again until ambient drops below the on temp. Perhaps.
My summer mode is completely off via a schedule. Keep us informed if you try this option out!
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Thanks Harri. Interesting idea. I'll give it a go and let you know what happens.
-
Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
3 months ago
-
Mitsubishi Ecodan not good enough ?
6 months ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
7 months ago
-
Mitsubishi Ecodan circulation pump running.
7 months ago
-
Ecodan Auto Adapt Options
7 months ago
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 2,947 Online
- 7,218 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
Sorry that was a mistype. I meant 2A2A ie a2a with 2 o...
By JamesPa , 9 minutes ago
-
RE: Electricity price predictions
@rob-of-york sounds like a term that Heidegger would...
By Papahuhu , 35 minutes ago
-
RE: Why don't people choose heat pumps?
An excellent concise exposition of loss aversion: a 4% ...
By cathodeRay , 1 hour ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Agree but remember to retain your isp router as they wi...
By JamesPa , 2 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 10 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 11 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 14 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 18 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 4 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 6 days ago