Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Compensation Curve Minimum Temp 25 Degrees
My Ecodan doesn't seem to allow me to set a compensation curve that will drop flow temp below 25 degrees celcius. In essence at 10 degrees outside I want all heating turned off with normal DHW function. Is my only option to turn off heating completely? I Assume I'm missing something; I can only find oblique reference to the 25 degree lower limit on the Web.
Any advice would be very much appreciated.
Well, generally a heating system is controlled by demand rather than another parameter. Even if you could lower the compensation curve further it would still be running – but I suspect it would become less efficient trying to put so little heat in.
However, in the controller settings you can find Service Menu > Operation Settings > Summer Mode, which is set to Off by default. But you have the options to set Heating On (4—19°, default 10°) and Heating Off (5—20°, default 15°) temperatures for ambient temps, and Heating On and Heating Off Judgement Times (both 1-48 hrs, default 6). These aren't explained anywhere, so perhaps a call to the Ecodan support line is in order, but I would presume that the temps are just setting on below/off above values with a hysteresis to allow it to run for a while and the judgments perhaps set a minimum time it has to be below temp before the heating is actually run, and a maximimum run time for while it is operating below the off ambient temp, after which it turns the heating off again until ambient drops below the on temp. Perhaps.
My summer mode is completely off via a schedule. Keep us informed if you try this option out!
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Thanks Harri. Interesting idea. I'll give it a go and let you know what happens.
-
Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
2 months ago
-
Mitsubishi Ecodan not good enough ?
5 months ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
6 months ago
-
Mitsubishi Ecodan circulation pump running.
6 months ago
-
Ecodan Auto Adapt Options
7 months ago
- 27 Forums
- 2,792 Topics
- 66 K Posts
- 1,891 Online
- 7,196 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Before changing pump settings, check the filter, flow d...
By EnergyStorageTech , 8 minutes ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
To me an excessiveness of emojis screams AI written tex...
By Prunus , 15 minutes ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
I think that's the key question. After all inverter uni...
By Prunus , 23 minutes ago
-
RE: battery storage without solar
With battery-only storage, the tariff spread is only pa...
By EnergyStorageTech , 31 minutes ago
-
RE: tepeo ZEB UK Support & Info Thread
The comparison should separate storage-heater behavior ...
By EnergyStorageTech , 51 minutes ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
A unit which uses water to transfer the heat/chill from...
By Temperature_Gradient , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
With regards to the BUS grant raid, I gave it more thou...
By ASHP-BOBBA , 2 hours ago
-
RE: Why are ASHP installs so expensive?
The whole system seems to work on the basis of...
By ian33a , 2 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Good plan. If you can get half hourly meter readings a...
By JamesPa , 7 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@editor Most certainly. The heat pump was an ideal s...
By Abernyte , 7 hours ago
-
Although regulations may well vary from country to coun...
By Majordennisbloodnok , 8 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yep I caught our slow leak from a £100 bill rise 8)
By EtchedPixels , 8 hours ago
-
RE: Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
@jamespa in some cases, failing the Turing test might b...
By GrahamF , 11 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@energystoragetech The heat capacity of some...
By JamesPa , 13 hours ago