Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@sliderule no worries at all. One black segment is quietest/min power. Three black segments is normal/full power (see photo)👍
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
that's on mine which is a 2021/22 FTC6 btwPosted by: @skd@sliderule no worries at all. One black triangle is quietest/min power. Three black triangles is normal/full power 👍
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
Posted by: @sunandair...it’s flow rate recommendation is around 11 LPM...I have found it’s important to keep Farley close to the recommended flow rate for your model of HP.
To pick up on this (flow rate) comment... I've a Grundfos primary pump which the FTC6 reports as producing 8lpm on constant speed 1, and 12 or 13 (it flip-flops every few seconds) on constant speed 2 - a) I assume the FTC pump speed setting has no effect whether it's 1 or 5, and b) with UFH and rads, what's the guidance on whether I should be at 8 or 12/13; is it just 'nearest the book flow' (e.g. nearest to 10.8lpm) or, with the UFH likely using/being on more, the nearest slower setting?
Unlikely, but c) is there any known way I adjust the Grundfos to get near half way in-between, e.g. ~10.5lpm?!
Posted by: @skdOne black segment is quietest/min power. Three black segments is normal/full power (see photo)
Can I just check this is correct - having read the FTC6 installation manual, the three bar settings are described as Normal / Level1 / Level2; does anyone know what Level1 and Level2 mean, precisely? (I can't find anything on google) Do we not think that 'Normal' is 'Normal quiet mode' (i.e. reduced noise) and not 'normal noise mode', given it's under the Quiet mode settings/schedule?
Posted by: @rhh2348Posted by: @skdOne black segment is quietest/min power. Three black segments is normal/full power (see photo)
Can I just check this is correct - having read the FTC6 installation manual, the three bar settings are described as Normal / Level1 / Level2; does anyone know what Level1 and Level2 mean, precisely? (I can't find anything on google) Do we not think that 'Normal' is 'Normal quiet mode' (i.e. reduced noise) and not 'normal noise mode', given it's under the Quiet mode settings/schedule?
This is what I worked out after speaking to Mitsubishi Tech Support, and experimenting myself. You're right, it's poorly described in their literature.
3 black bars is Normal mode, and refers to standard power / loudest compressor setting.
2 black bars is slightly reduced power, and a bit quieter than Normal. This is Level 1 Quiet Mode.
1 black bar is the greatest available reduction in compressor power. Level 2 Quiet Mode.
Hope this is some help.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
Posted by: @skdYou're right, it's poorly described in their literature.
3 black bars is Normal mode, and refers to standard power / loudest compressor setting.
2 black bars is slightly reduced power, and a bit quieter than Normal. This is Level 1 Quiet Mode.
1 black bar is the greatest available reduction in compressor power. Level 2 Quiet Mode.
Hope this is some help.
That's an understatement - the manual states the three levels as text (e.g. 'Normal / Level1 / Level2') rather than the number of 'bars'/squares the FTC6 actually displays, and then reverses the order (e.g. rather than 1 bar = Normal, 2 bars = Level1, 3 bars = Level3)! Extremely odd, thus:
However, further down it also states that if quiet mode is enabled, the heat pump icon changes to one with a crescent moon bottom-right, thus:
It'd be nice to know exactly what the two alternative levels adjust, if anyone's got/can find that info?
Will test with quiet mode settings once the W/C is roughly there. Thanks again for now, though.
@rhh2348 yes, the compressor symbol on the main screen will include a moon icon whenever either of the Quiet Mode settings is selected.
I know what you mean - I wish Mitsubishi would provide a written description on the workings of this mode.
Mitsubishi Tech Support verbally told me that each Quiet Mode setting simply places an electronic restruction on maximum compressor speed, nothing more than that.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
Posted by: @rhh2348Posted by: @sunandair...it’s flow rate recommendation is around 11 LPM...I have found it’s important to keep Farley close to the recommended flow rate for your model of HP.
To pick up on this (flow rate) comment... I've a Grundfos primary pump which the FTC6 reports as producing 8lpm on constant speed 1, and 12 or 13 (it flip-flops every few seconds) on constant speed 2 - a) I assume the FTC pump speed setting has no effect whether it's 1 or 5, and b) with UFH and rads, what's the guidance on whether I should be at 8 or 12/13; is it just 'nearest the book flow' (e.g. nearest to 10.8lpm) or, with the UFH likely using/being on more, the nearest slower setting?
Unlikely, but c) is there any known way I adjust the Grundfos to get near half way in-between, e.g. ~10.5lpm?!
Where is your circulator pump located in the circuit? Is it positioned on the Primary Flow or the Primary Return? Do you have a Mitsubishi pre plumbed cylinder with a plate heat exchanger? And do you know where your flow sensor I see located- as it should be on the return pipework going back to the heat pump? Do you have a Low Loss Header fitted? Regarding c) there is a device called a flow setter valve which simply restricts flow but might not be necessary. One litre faster than optimum shouldn’t be a problem.
dont understand a) what are you assuming. What isn’t happening?
A bit of a late response to this reply, however thank you for doing so, @sunandair.
I've done some more reading around this since my previous post, and thought it'd be useful to cover off some of the points:
- it's not a Mitsubishi (pre-plumbed) cylinder / the flow sensor is on the return pipework, yes / there is a LLH.
- question (a) was to understand if this [the FTC pump speed setting] affected anything other than purely what speed a Mitsubishi pump [for their pre-plumbed cylinder] runs at - e.g. if set to 1 or 5 does that affect something else, like compressor speed, or is otherwise included in any of their algorithms?
- Previously, I'd mangled primary flow rate with UFH zone flow rate, the latter of which is handled by an additional pump on my system - plus, I believe my assumption (that UFH pumps should run slower to provide an optimal reduced flow rate) is incorrect, and that typically one aims for UFH pumps to provide three times the flow of a rad zone! 😳
Posted by: @rhh2348A bit of a late response to this reply, however thank you for doing so, @sunandair.
I've done some more reading around this since my previous post, and thought it'd be useful to cover off some of the points:
- it's not a Mitsubishi (pre-plumbed) cylinder / the flow sensor is on the return pipework, yes / there is a LLH.
- question (a) was to understand if this [the FTC pump speed setting] affected anything other than purely what speed a Mitsubishi pump [for their pre-plumbed cylinder] runs at - e.g. if set to 1 or 5 does that affect something else, like compressor speed, or is otherwise included in any of their algorithms?
- Previously, I'd mangled primary flow rate with UFH zone flow rate, the latter of which is handled by an additional pump on my system - plus, I believe my assumption (that UFH pumps should run slower to provide an optimal reduced flow rate) is incorrect, and that typically one aims for UFH pumps to provide three times the flow of a rad zone! 😳
I believe that the FTC controller can only vary the water pump speed if the actual water pump is capable of having its speed varied. An easy way to check is change the speed setting from 1 to 5 and listen for a change in pump speed.
The actual water pump speed, and subsequent variation in flow rate, is one of the factors which determines how much thermal energy is being transported from the heat pump to the heat emitters.
If the flow rate is say 10 lpm and the DT is 5C, then a certain quantity of thermal energy will be transported. If the flow rate is now increased to 20 lpm then to transport the same quantity of thermal energy the DT must reduce to 2.5C.
As the heating demand increases, the options from a control point of view is to run the water pump at constant speed and allow the DT at the heat pump to vary, or vary the water pump speed to maintain a reasonably constant DT.
If you can vary the water pump speed between 1 and 5 by means of the FTC, then it may be possible to identify the setting that produces a DT of approximately 5C when the heating demand is at a maximum.
With regard to the required flow rate through UFH as against radiators, I suspect it will depend upon the heating capacity of the UFH and radiators. If you pass 3kW of thermal energy into both radiators and UFH, and both are capable of emitting 3kW of thermal energy, then the required flow rate and subsequent DT should be approximately the same.
-
Mitsubishi Ecodan not good enough ?
1 month ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
2 months ago
-
Mitsubishi Ecodan circulation pump running.
2 months ago
-
Ecodan Auto Adapt Options
2 months ago
-
Ecodan heat pump leak
3 months ago
- 26 Forums
- 2,676 Topics
- 62.6 K Posts
- 219 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Harvest Thermal - ASHP with a smart thermal battery
I thought people here might find this interesting, even...
By springswood , 5 minutes ago
-
RE: Heat pump installation quotations
@batpred The only draughty place is in the living ro...
By sttpd1917 , 24 minutes ago
-
Don't you dare. You just carry on as you are; as @batpr...
By Majordennisbloodnok , 40 minutes ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@ragtime27 some rooms in our house only have one place ...
By Judith , 45 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
I didn't know about those, they look like good pieces o...
By JamesPa , 4 hours ago
-
@mkz, that's very helpful. Even if Urban Plumber are no...
By Majordennisbloodnok , 4 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 5 hours ago
-
My first question is why bother with the auto balancin...
By JamesPa , 5 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 5 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 5 hours ago
-
I share the same experience as @majordennisbloodnok hav...
By Old_Scientist , 6 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 9 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@bash, something we haven't touched on already relates ...
By Majordennisbloodnok , 1 day ago