Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Dedicated heat meter and HP heat meter discrepency
Hi all,
I have a Daikin Altherma 3 split, 16kW (EPGA16DV) which was installed back in 2020. Since then, I've been periodically keeping track of the energy usage, that it and the external heat / electricity meters report. I'm seeing a significant discrepancy in the results from the heat meter, and I'm wondering if anyone has seen anything similar or has any suggestions.
The original heat meter was showing around about half the heat produced compared to what the Daikin unit reports. I reported this issue to the installers and after a lot of back and forth, last year they installed a different heat meter. It is closer, but still there is a significant disparity. For example, over the last month the heat meter reports 1458kWh while the Daikin reports 2065kWh (diff compared to last month's readings). The electricity meters are much closer showing 839kWh (EM1) to 805kWh (Daikin). Which reading is used, significantly impacts SCoP: 1.74 if using the external meters and 2.57 if using the Daikin readings.
An SCoP of 2.57 seems low, but it was cold at the start of the month. 1.74 however seems terrible.
I don't know what to do now. I've asked the installers many times, but they just say that the flow calculations show it operating at 400%. That is not reflected in the SCoP at all.
Any ideas, thoughts, suggestions welcome!
Allan
Posted by: @theallanHi all,
I have a Daikin Altherma 3 split, 16kW (EPGA16DV) which was installed back in 2020. Since then, I've been periodically keeping track of the energy usage, that it and the external heat / electricity meters report. I'm seeing a significant discrepancy in the results from the heat meter, and I'm wondering if anyone has seen anything similar or has any suggestions.
The original heat meter was showing around about half the heat produced compared to what the Daikin unit reports. I reported this issue to the installers and after a lot of back and forth, last year they installed a different heat meter. It is closer, but still there is a significant disparity. For example, over the last month the heat meter reports 1458kWh while the Daikin reports 2065kWh (diff compared to last month's readings). The electricity meters are much closer showing 839kWh (EM1) to 805kWh (Daikin). Which reading is used, significantly impacts SCoP: 1.74 if using the external meters and 2.57 if using the Daikin readings.
An SCoP of 2.57 seems low, but it was cold at the start of the month. 1.74 however seems terrible.
I don't know what to do now. I've asked the installers many times, but they just say that the flow calculations show it operating at 400%. That is not reflected in the SCoP at all.
Any ideas, thoughts, suggestions welcome!
Allan
If correctly installed, I would expect the external heat meter to be the more accurate. Please provide photo's, both distance and closeup, of your installation.
Absolutely! One shot of the internal part of the split HP + buffer tank, close up of the heat meter, and one of the DHW tank.
I don't have a schematic of the piping, but I can draw one up if it would be useful.
I'd expect the external meters to be more accurate as well, which is what really bothers me about the SCoP.
Thanks,
Allan
Where are the temperature sensors associated with the heat meter, are they in pockets or clipped to the pipework? Are the temperature sensors making good thermal contact and are they and the pipework adequately insulated?
Where are the temperature sensors measuring the LWT and RWT, and flow meter connected to the heat pump controller?
Low COP can be caused by flow and return water mixing within the buffer tank. What are the temperatures on the pipes going in and out of the buffer?
Hi,
Thanks so much for your help and insight with this! Attached are photos showing the layout of the heat meter and close ups of its two temperature sensors in the pipes. They both appear to be firmly embedded and secure.
This morning I took some readings from the heat meter and the equivalent from the Daikin:
- Heat meter:
- Delta temp: 2.56C (leaving water: 40.6C, inlet 38.1C)
- Flow rate: 1.364 m^3/h
- Daikin:
- Delta temp: 3.9C (leaving water: 40.9C, inlet 37.0C) - the Daikin also has a Leaving water PHE which was 41.5C - I think that's the water temp on the heat exchanger plate?
- Flow rate: 1.332 (on screen as 22.2l/min)
- Analogue meters on manifold:
- Delta temp: 3C (flow: 36C, return 33C)
One thing I did find interesting is that while looking at the numbers on the heat meter over night, the delta went negative a number of times. Only about -0.5C, but I hadn't expected that. The largest delta I saw was +4.6C.
Allan
@theallan I'd definitely suggest you draw a schematic to help us understand, the overall layout and where the metering points are. that may start to give some clues why the meter readings are different.
negative DT will happen hen the circulation pump is running but the heat pump is not heating. RWT can be higher than LWT in that situation. that will happen during defrost, or at any point when the heatpump's compressor has shutdown, but its still keeping the circulation pump running, as part of its normal cycle of control.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@Dandee - No I hadn't thought of that - the readings above were while calling for space heating. Do you mean to just disable the call for heat and DHW production?
@iancalderbank - Thanks for the negative number explanation. I'll draw a schematic this weekend and upload it.
As the saying goes "a picture is worth a thousand words".
The heat meter temperature sensors are indeed in pockets, and if correctly installed will hopefully be making good thermal contact. Measuring temperature accurately is not as easy as many may think, since the type of sensor used will have a specified accuracy, then the electronics required to convert the sensor output into an actual reading will also have a specified accuracy. Accurate flow measurement is even more difficult to achieve.
If you were to install two identical heat meters on the same system, I am quite confident that they would not give the same reading, but the readings should be within the specified tolerance.
If you look at the data sheet for your heat meter it should give details of the specified accuracy, you could also ask Daikin what the expected accuracy of their measurements should be. If both heat energy output measuring systems are providing reasonably consistent measurements, the percentage difference between the two readings should be reasonably consistent over a period of time.
As I think has already been pointed out, the LWT and RWT readings can reverse when the heat pump performs a defrost cycle.
I suspect that the low SCOP is probably due to the way your system has been configured and is being operated. Do you have any thermostats or TRV's within your system? Are you operating the system in Weather Compensation (WC) mode or fixed LWT? If in WC mode what are the settings?
another thing to check is whether the heat meter is configured for glycol. A glycol mix has less heat energy than pure H20. My heat meter (which is similar to yours) is set to reduce output by (I think) 20% for this. Make sure you're comparing like with like. In fact my ASHP (Mitsubishi but others may be the same) has several sorts of manual adjustments and fudges you can make so it's worth checking this on yours.
-
Daikin 6kw setup with Dixell controller
2 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
6 months ago
-
Daikin Error Code 7H05
1 year ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
2 years ago
-
Daikin COP / energy used measurement from MMI
2 years ago
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 289 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago