Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Baffled by heat pump size/ choice!
Posted by: @tomhartleyI’m in a new build with a Vaillant 7Kw. Rads up stairs and ufh downstairs. When up stairs wants demand downstairs struggles, but back to the hot water. We came home the other night and basically had a shower one after each other but by fluke, nearly 50 mins apart. So I used then son, etc etc. but after I used it, the heating stops to heat just hot water. So my heating was off for hours.
Given the very slow response of UFH, I'm surprised that it's noticeable if the heating goes off or an hour or so. And a new build, if insulated to current standards (perhaps a big "if"), shouldn't cool down noticeably in an hour.
Posted by: @jamespaDepending on your system you can also schedule multiple, shorter, DHW reheats during the day/night
This can be easily done using the Vaillant app. At the moment I've got my 7kW Arotherm+ to top up the DHW in the afternoon afternoon and before 5am when the house heating gets turned up slightly. If the DHW cools down between those periods then it waits until the next scheduled top-up period.
Returnng to the original problem. I've thought of two more work-arounds which wouldn't need heating the DHW to a very high temperature:
i) Persuade some occupants to shower in the evening and just do a quick hand wash in the mornings.
ii) Run the cold supply to the shower(s) via a tank which is at room temperature or warmed by the main heating system - you'll get much more water at 40C is the cold supply is warmer.
iii) Use a bath tub and take it in turns to take a dip in the same water (as was commonplace in an earlier era).
Posted by: @johnrPosted by: @tomhartleyI’m in a new build with a Vaillant 7Kw. Rads up stairs and ufh downstairs. When up stairs wants demand downstairs struggles, but back to the hot water. We came home the other night and basically had a shower one after each other but by fluke, nearly 50 mins apart. So I used then son, etc etc. but after I used it, the heating stops to heat just hot water. So my heating was off for hours.
Given the very slow response of UFH, I'm surprised that it's noticeable if the heating goes off or an hour or so. And a new build, if insulated to current standards (perhaps a big "if"), shouldn't cool down noticeably in an hour.
Posted by: @jamespaDepending on your system you can also schedule multiple, shorter, DHW reheats during the day/night
This can be easily done using the Vaillant app. At the moment I've got my 7kW Arotherm+ to top up the DHW in the afternoon afternoon and before 5am when the house heating gets turned up slightly. If the DHW cools down between those periods then it waits until the next scheduled top-up period.
Returnng to the original problem. I've thought of two more work-arounds which wouldn't need heating the DHW to a very high temperature:
i) Persuade some occupants to shower in the evening and just do a quick hand wash in the mornings.
ii) Run the cold supply to the shower(s) via a tank which is at room temperature or warmed by the main heating system - you'll get much more water at 40C is the cold supply is warmer.
iii) Use a bath tub and take it in turns to take a dip in the same water (as was commonplace in an earlier era).
another is to fit waste water heat recovery
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa hi, in the above where you state from 10 to 40 takes 30 mins, do you mean, 10degrees in the tank to get it up to 40c. My system is on 110 mins max with a 30 minute break. From one of your earlier comments where you state, you have the dhw doing things at different times etc. my system has the hysteresis on 5, so once it drops, it starts to kick in straight away. Do you have this turned off? Thanks for the input.
Posted by: @tomhartley@jamespa hi, in the above where you state from 10 to 40 takes 30 mins, do you mean, 10degrees in the tank to get it up to 40c.
Yes, sorry for any confusion. 10C is sometimes quoted as the temp of incoming mains (being, I presume, roughly the temp underground at the level the mains is typically buried)
Posted by: @tomhartleyMy system has the hysteresis on 5, so once it drops, it starts to kick in straight away.
Depending on where the sensor is in the tank, leaving this feature on might well start the reheat 'automatically' sufficiently early in the 'run' of showers. Its probably necessary to experiment to find out, although you could get a bit of an idea by estimating how far up the tank the temp sensor is. The reheat should start when the cold water reaches this level. Mine is about one third of the way up the (Vaillant) tank, so the reheat would start after a bit less than 2 showers.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I have the Vaillant tank also. Is this why sometimes I can have a shower after a recharge and the temp doesn’t drop when I check the senso comfort. Next person gets in, then it reads like 35 when they get out. Sorry for side tracking the thread, the original topic at the start… why for what reason are we not just fitting 10kw or 12kw units, so the dhw heats as we’re using the shower at a higher speed and keep the same size cylinders?
Posted by: @tomhartleywhy for what reason are we not just fitting 10kw or 12kw units, so the dhw heats as we’re using the shower at a higher speed and keep the same size cylinders?
More expensive, larger, louder and won't modulate down so low and are thus less efficient for space heating if the house doesn't need it. If you really need six showers in close succession there are other solutions. You are of course also at liberty to decide your own trade offs.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi.
Any chance that one of your bathrooms can have an electric shower installed.
Gives you a little more flexibility with hot water reheat times.
Posted by: @tomhartleyI have the Vaillant tank also. Is this why sometimes I can have a shower after a recharge and the temp doesn’t drop when I check the senso comfort. Next person gets in, then it reads like 35 when they get out. Sorry for side tracking the thread, the original topic at the start… why for what reason are we not just fitting 10kw or 12kw units, so the dhw heats as we’re using the shower at a higher speed and keep the same size cylinders?
Try reducing the DHW hysteresis setting and schedule the DHW to come on just before and during periods when the hot water is likely to be used. The hysteresis setting is there to stop excessive switching on the heat pump to top up the DHW (there's also the one hour default DHW anti-cycling setting which may need to be reduced). Each DHW heating cycle has a significant energy overhead in the summer months when the general heating is off and the primary circuit has to warm up from cold. This is less of a concern in the winter when the system is already warm.
One of the data files which can be downloaded using the Vaillant app contains hourly DHW temperature readings. You can scan through this to see how the system is behaving which provides useful guidance for setting the control paramenters.
- 26 Forums
- 2,610 Topics
- 60.8 K Posts
- 825 Online
- 6,966 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Anyone concerned about GivEnergy?
An incredibly enlightening piece on the subject by @maj...
By Mars , 2 hours ago
-
Home automation and the cloud; is there a better way?
You’ve just had a brand new system installed (heat pump...
By Majordennisbloodnok , 2 hours ago
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
We've started to document everything, and part 2 of the...
By Mars , 2 hours ago
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
So the red bars are 'DHW' and the yellow bars 'heating'...
By JamesPa , 3 hours ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 7 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 7 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 7 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 17 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 18 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 20 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 21 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 23 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 1 day ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 3 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago